Default Gal steel Townhome

This townhome has a central water boiler providing hot water and radiant heat to all the units. It appears as the main water line(s) are galvanized steel. All the water lines in the unit are copper and a little pex. I am going to write up the gal steel. What is your opinions? Thanks
Attached Thumbnails
gal-steel-townhome-highland-069.jpg  
Reply With Quote
  #2  
Old 7/29/08, 4:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gal steel Townhome

What would you write? Does your jurisdiction prohibit the use of galvanized steel for supply lines?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/29/08, 4:58 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Gal steel Townhome

I'm with Jeff...

What's the problem with gal steel?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 7/29/08, 5:06 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gal steel Townhome

gal steel rusts from the inside out and has higher probability of water leakage and poor water quality in potable water piping. In my area it is typically uninsurable.

I havent really seen it as a primary supply line and copper through-out the unit/building.

You guys dont call out gal steel supply piping?

Thanks
Reply With Quote
  #5  
Old 7/29/08, 5:08 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Gal steel Townhome

Virtually any pipe is going to have it's problems over time. Yea, in 40 years the supply might have to be replaced. But if it's copper it might have to be replaced too. So to answer your question in a word... No.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #6  
Old 7/29/08, 5:11 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Gal steel Townhome

http://www.randpc.com/AskTheEngineer...rRe-piping.asp



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 7/29/08, 5:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gal steel Townhome

In my particular jurisdiction, galvanized steel pipes are no longer approved for re-pipes or original construction, however, California's building code still allows it.

If there are no current issues with the piping, there's no reason to "write it up" unless it's prohibited by the AHJ.

Having said that, all the galvanized piping I have ever seen has been close to, or in need of replacement. I have not seen galv in newer construction.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 7/31/08, 1:04 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Gal steel Townhome

I've look at that picture for a while now and maybe I'm wrong, but isn't that black pipe and cast iron fittings. If I'm right neither are approved for supply piping anywhere in the country (I could be wrong, but not sure cast iron fittings were ever approved for supply.
Someone with better eyes set me straight.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #9  
Old 7/31/08, 1:38 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Gal steel Townhome

Not sure where it came from, but I hope this is useful as I often refer to this .

Galvanized pipe was commonly used for water supply lines many years ago, but over time many have filled with scale, which is why some older homes suffer from low water pressure. Hard water greatly reduces the life of steel pipe.
Reply With Quote
  #10  
Old 7/31/08, 1:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gal steel Townhome

This is a common mistake. Pressure is not affected by pipe size or material. The static pressure is the same whether the inside diameter is 1/16 of an inch, or 3 inches, or 3 feet.

Quote:
Originally Posted by relliott
Galvanized pipe was commonly used for water supply lines many years ago, but over time many have filled with scale, which is why some older homes suffer from low water pressure.
Flow, or volume (GPM) is reduced by pipe diameters.

The following, however, is true.

Quote:
Originally Posted by relliot
Hard water greatly reduces the life of steel pipe.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 7/31/08, 5:22 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gal steel Townhome

Quote:
Originally Posted by jpope
Flow, or volume (GPM) is reduced by pipe diameters.
Some Chicago inspector had a blog entry titled "Is it pressure or flow" - can't recall who, though.
Reply With Quote
  #12  
Old 7/31/08, 5:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gal steel Townhome

Pressure (PSI) and flow (GPM) are two, completely separate items, and should be inspected as such.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 7/31/08, 8:01 PM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,391
Default Re: Gal steel Townhome

Jeff:
I agree with everything you've said. However, there were some dramatic failures of non-domestic galvanized pipes in our general area, Korean galvanized (I think), which were springing pin-holes leaks due to an inadequate annealing process. Also, if I remember correctly, some copper mains in Canyon Country were failing prematurely due to acidic soils and builders were substituting them for galvanized ones. This is not a recent phenomenom, and I wondered if you'd heard about it. The Korean galvanized were infamous for awhile, and would inform my clients about its history of leaks, and always deferred to a specialist.
Reply With Quote
  #14  
Old 7/31/08, 8:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gal steel Townhome

Yes Kieth, I am aware of the sub-standard Korean piping that was used. My area (Santa Clarita) was one of the areas significantly affected by this particular piping.

There was a large class-action lawsuit filed against builders in our area for using this pipe, which was settled for $41 million, affecting more than 5,000 homes.

Here is a snippet from one article published about the lawsuit.

Quote:
The galvanized steel pipes at issue in the litigation were manufactured using the electric resistance weld (ERW) process. Literature has been published for nearly three decades indicating worldwide premature corrosion problems with ERW galvanized steel pipes used for potable water delivery.
There were even allegations that water-softening systems were partially responsible for the premature failure of this piping. Several suppliers of these systems were included in the lawsuit and contributed to the settlement.


Quote:
By agreeing to the settlement, the dealerships will only have to pay homeowners a total of $1.25 million out of the total $41 million. However, it is the settlement that has some water treatment dealers nervous, saying it may open up others in the industry to similar suits.
In any event, since 1994, the use of galvanized piping has been discontinued in the Jurisdiction of Santa Clarita.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 7/31/08 at 9:04 PM..
Reply With Quote
  #15  
Old 7/31/08, 11:12 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Gal steel Townhome

Okay, I'll ask one more time, anyone else think that large black steel pipe is not Galvanized. It is actually black steel pipe. Oh and BTW there are no insulating unions in that picture.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded to building Steel Structure Frame mcyr Electrical Inspections 11 4/29/09 11:50 AM
A steel House rcooke Canadian Inspectors 4 3/20/08 11:42 AM
Lots of steel, lots of rust... mkiss1 Structural Inspections 2 2/28/08 11:12 AM
disimilar metals cbono Canadian Inspectors 12 1/15/08 7:43 AM