Default Galvanized natural gas pipe

At an inspection the other day, I noticed a galvanized elbow installed between 2 straight runs of black iron gas pipe. Is galvanized allowed as a general rule? Does it depend on local codes?



Jonathan Graham
HouseCalls Home Inspection Services
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/24/12, 12:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 50,934
Default Re: Galvanized natural gas pipe

The issue with gavanized pipe is the possibility of the coating flaking and then plugging valves and orifices.

If drip/dirt legs are present the risk is low but I would note the non standard use of the galvanized fitting in the gas piping system.



As a Professional Home Inspector, I support the privacy of my clients.

For more information click Trustyourinspector.ORG


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 3/24/12, 4:20 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 12,373
Default Re: Galvanized natural gas pipe

Well for once we agree Micheal. I would note it, it should be changed . It does depend on were you are the do not even ask for drip legs here .



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #4  
Old 3/24/12, 5:49 PM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,823
Default Re: Galvanized natural gas pipe

Our local utility doesn't recommend it either(for the reasons Mike gave).



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector
www.aaintegrityhomeinspection.com
Reply With Quote
  #5  
Old 3/24/12, 6:58 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,718
Default Re: Galvanized natural gas pipe

Allowed by the UPC...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 3/24/12, 7:07 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 32,283
Default Re: Galvanized natural gas pipe

I was told not allowed here however if running underground to say a garage would you rather use Black or Galv ?
Reply With Quote
  #7  
Old 3/24/12, 9:56 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,954
Send a message via Yahoo to jfunderburk
Default Re: Galvanized natural gas pipe

Quote:
Originally Posted by jpope View Post
Allowed by the UPC...
And the IRC. It's a misconception that galvanized is prohibited for natural gas.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #8  
Old 3/24/12, 10:42 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,403
Default Re: Galvanized natural gas pipe

Quote:
Originally Posted by jfunderburk View Post
And the IRC. It's a misconception that galvanized is prohibited for natural gas.
It varies at where you live.

From Ameren Illinois, my local utility provider:

Fuel Line:
Customer Requirements:

…… The customer’s fuel line is the pipe that connects
to the outlet of the gas meter set and extends
through the wall into the house. The fuel line
should enter the house or structure within three
(3) feet of the gas meter set.

…… The customer fuel line from the meter through
the house wall
must be a minimum of one (1) inch
IPS schedule 40 black iron pipe.
For Corrugated
Stainless Steel Tubing (CSST) installations, a
termination fitting mounted on the outside house
wall is acceptable for the transition from black
iron pipe.






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
  #9  
Old 3/24/12, 10:54 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,954
Send a message via Yahoo to jfunderburk
Default Re: Galvanized natural gas pipe

Quote:
Originally Posted by ccurrins View Post
It varies at where you live.

From Ameren Illinois, my local utility provider:

Fuel Line:
Customer Requirements:

…… The customer’s fuel line is the pipe that connects
to the outlet of the gas meter set and extends
through the wall into the house. The fuel line
should enter the house or structure within three
(3) feet of the gas meter set.

…… The customer fuel line from the meter through
the house wall
must be a minimum of one (1) inch
IPS schedule 40 black iron pipe.
For Corrugated
Stainless Steel Tubing (CSST) installations, a
termination fitting mounted on the outside house
wall is acceptable for the transition from black
iron pipe.
I said IRC. Local codes vary.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #10  
Old 3/24/12, 10:56 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,954
Send a message via Yahoo to jfunderburk
Default Re: Galvanized natural gas pipe

2009 IRC G2414.4.2 (403.4.2) Steel. Steel and wrought-iron pipe shall
be at least of standard weight (Schedule 40) and shall comply
with one of the following:
1. ASME B 36.10, 10M;
2. ASTM A 53/A 53M; or
3. ASTM A 106.
Commentary: Steel pipe must be Schedule 40 or heavier, must comply
with one of the listed standards and can be black
iron or galvanized. Contrary to popular belief, natural
gas does not adversely react with the zinc coating on
galvanized pipe."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #11  
Old 3/24/12, 10:57 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,403
Default Re: Galvanized natural gas pipe

Quote:
Originally Posted by jfunderburk View Post
I said IRC. Local codes vary.
You also said this

"It's a misconception that galvanized is prohibited for natural gas."






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
  #12  
Old 3/24/12, 11:00 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,954
Send a message via Yahoo to jfunderburk
Default Re: Galvanized natural gas pipe

Quote:
Originally Posted by ccurrins View Post
It varies at where you live.

From Ameren Illinois, my local utility provider:

Fuel Line:
Customer Requirements:

…… The customer’s fuel line is the pipe that connects
to the outlet of the gas meter set and extends
through the wall into the house. The fuel line
should enter the house or structure within three
(3) feet of the gas meter set.

…… The customer fuel line from the meter through
the house wall
must be a minimum of one (1) inch
IPS schedule 40 black iron pipe.
For Corrugated
Stainless Steel Tubing (CSST) installations, a
termination fitting mounted on the outside house
wall is acceptable for the transition from black
iron pipe.
Is galvanized prohibited anywhere else by your utility? Or just the fuel line?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #13  
Old 3/24/12, 11:08 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,403
Default Re: Galvanized natural gas pipe

Quote:
Originally Posted by jfunderburk View Post
Is galvanized prohibited anywhere else by your utility? Or just the fuel line?
It's not prohibited with water lines, if that's what you mean.

Not sure if it still is with All of the fuel line. It used to be, at least by local AHJ.

But I believe the fuel mixture has changed, so maybe have the restrictions.

I rarely see galvanized on fuel lines, unless it's a nipple, elbow, etc.






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/24/12, 11:13 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,403
Default Re: Galvanized natural gas pipe

Here's an example from a few days ago.
Attached Thumbnails
galvanized-natural-gas-pipe-hpim6100.jpg  






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
  #15  
Old 9/8/14, 2:24 PM
paul dimaggio paul dimaggio is offline
New User
 
Join Date: Sep 2014
Posts: 1
Please Note: paul dimaggio is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Galvanized natural gas pipe

As Joe Funderburk mentioned (which is the same requirement as 2013 California Plumbing Code, Fuel Gas Piping 1208.5.2.2), galvanized pipe may be used for natural gas piping.

2009 IRC G2414.4.2 (403.4.2) Steel. Steel and wrought-iron pipe shall
be at least of standard weight (Schedule 40) and shall comply
with one of the following
:
1. ASME B 36.10, 10M;
2. ASTM A 53/A 53M; or
3. ASTM A 106.
ASTM A53 specification. "Standard Specification for
Pipe, Steel, Black and Hot-Dipped, Zinc-Coated, Welded and
Seamless", section 17, discusses Galvanized Pipe requirements:

17. Galvanized Pipe
17.1 Galvanized pipe ordered under this specification shall
be coated with zinc inside and outside by the hot-dip process.
The zinc used for the coating shall be any grade of zinc
conforming to Specification B6. ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 42 11/3/13 6:47 PM
Help - Polybutylene Pipes Rick G Plumbing Inspections 45 6/26/13 4:21 PM
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Is this allowed? belliott Plumbing Inspections 4 7/15/09 6:40 PM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 6:39 PM

All times are GMT -4. The time now is 1:53 PM.
no new posts