Default Garage Dryer Duct

Have any of you seen this before and how would you write this up? The aluminum dryer duct on my last inspection exited the laundry room directly into the garage and it had a 90 bend that ran vertical to a dryer vent monted on the roof. The Duct had (2) 90's and was approx 27' length with the bends. The vertical duct in the garage was 18" from the garage dry wall and was only "supported" were it exited the wall and roof. The duct was basic duct thickness and pieced together is ~3 foot sections. Nothing was protecting the duct from damage and it very flimsy. There was cardbord boxes pushed against it. I could easily move it from side to side with little effort. I wrote this as safety hazard and that it needed to be replaced (including no supports and exceed length standards). My main question is how should I have written this up regarding the fire hazards and what standards apply to ducting in the garage.



John Scaparo
Innovative Home Inspection, LLC
Canton, Michigan 48187
734.664.5853

john@InnovativeHomeInspection.com


Michigan Licensed Residential Builder

2101201845

InterNACHI MI #09041012, AHIT Member
Plymouth Michigan Home Inspector
Canton Michigan Home Inspector



"Helping To Secure Your Home Investment"

Looking for link exchange partners.
If interested send me your link.

Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/18/10, 1:31 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage Dryer Duct

All ducting located in the garage that penetrates the firewall should be 26 gauge sheet metal. It sounds like a relocation of the original. Any evidence of an original location elsewhere?

www.MauiHomeInspections.com
Reply With Quote
  #3  
Old 6/21/10, 10:51 PM
pnarron pnarron is offline
InterNACHI Member
 
Join Date: Jan 2010
Posts: 74
Default Re: Garage Dryer Duct

It would be a fire hazard because of the lint!
Reply With Quote
  #4  
Old 6/22/10, 12:09 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Garage Dryer Duct

The 2006 edition of the IRC states the following concerning ducts that penetrate garage walls and ceilings:
R309.1.1 Duct Penetration

Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum No. 26 gauge (0.48 mm) steel sheet or other approved material, and shall have no openings in the garage.
Read http://www.nachi.org/dryer-vent-safety.htm and http://www.nachi.org/attached-garage-fire-hazards.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
supply duct in garage. mnorthrup Inspecting HVAC Systems 2 8/27/09 9:07 PM
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 12:47 PM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 9 9/9/07 7:02 PM
Newer construction dmacy General Inspection Discussion 9 7/18/06 9:04 PM


All times are GMT -4. The time now is 1:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts