Inspected a house today that had a flex gas line connected between two metal pipes in crawl space area. Stop valve was also present in crawl space. This was in the gas line supplying the range. Didn't seem right to me. How would you right that up?
Reply With Quote
  #2  
Old 2/16/06, 10:31 AM
pkelley's Avatar
pkelley pkelley is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: St. Charles, Il
Posts: 102
Default Re: Gas flex line in crawl space

Gas flex lines cannot pass through walls and or flooring. The Shut off valve needs to be with in reach of the appliance it is servicing.Recommending a qualified contractor repair

Was there a drip leg present?
Reply With Quote
  #3  
Old 2/16/06, 7:32 PM
Richard Seay Richard Seay is offline
New User
 
Join Date: Sep 2005
Posts: 15
Please Note: Richard Seay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas flex line in crawl space

Thanks, you asked - Was there a drip leg present? No, I very seldom see them here. The flex line is connecting two gas pipes in the crawlspace area. It does not pass through a wall or floor. Didnt look right to me.
Richard
Reply With Quote
  #4  
Old 2/16/06, 8:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas flex line in crawl space

Flex gas line? That doesn't really tell us enough to give a proper response.

CSST is allowed in any location that other gas piping is allowed. If the flex gas line you were referring to was in fact, CSST, there may be no problem with that application. Also, CSST can pass through walls floors etc.

If the flex gas line was actually an appliance connector, it was probably improper. Appliance connectors are for connecting appliances, not piping.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/16/06 at 8:23 PM..
Reply With Quote
  #5  
Old 2/16/06, 11:56 PM
Richard Seay Richard Seay is offline
New User
 
Join Date: Sep 2005
Posts: 15
Please Note: Richard Seay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas flex line in crawl space

My mistake, the flex gas line was actually an appliance connector. Thanks
Reply With Quote
  #6  
Old 2/16/06, 11:57 PM
JohnH515's Avatar
JohnH515 JohnH515 is offline
New User
 
Join Date: Feb 2006
Posts: 13
Please Note: JohnH515 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas flex line in crawl space

Jeff, is there a visable difference between CSST and appliance connector line?

John
Reply With Quote
  #7  
Old 2/17/06, 12:54 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas flex line in crawl space

Appliance connectors are typically smaller in diameter and three feet long. CSST can be quite long and sized as you would expect for building supply.

http://www.gastite.com/flash.php



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 2/19/06, 11:41 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas flex line in crawl space

Here are some pictures of a fairly common set up. The CSST is run through the wall to rigid pipe, and then to an appliance connector.

The rigid piping wasn't really necessary in this case, but there's nothing wrong with the set up.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/28/07 at 4:15 PM..
Reply With Quote
  #9  
Old 2/20/06, 3:33 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Unhappy Re: Gas flex line in crawl space

Here is a picture of how NOT to install the flex gas connector.

This was in a basement, passing up through a wall up to a kitchen range.

The valve has to be in the same room preferably next to the appliance. Here is the rub .. Most shut off valves for kitchen stoves are behind the appliance... Hmmm
Attached Thumbnails
gas-flex-line-crawl-space-100_2254.jpg  

Last edited by pbolliger; 2/20/06 at 3:36 PM..
Reply With Quote
  #10  
Old 2/20/06, 7:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas flex line in crawl space

Quote:
Originally Posted by pbolliger
The valve has to be in the same room preferably next to the appliance. Here is the rub .. Most shut off valves for kitchen stoves are behind the appliance... Hmmm
Also, appliance connectors are absolutely not allowed to pass through walls, floors, etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/21/06, 10:27 AM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas flex line in crawl space

AGA website has alot of info on csst as well as appliance connectors which are a listed assembly. Also check the Fule Gas Code or IRC fule gas section.
Reply With Quote
  #12  
Old 8/10/08, 1:27 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 708
Default Re: Gas flex line in crawl space

Quote:
Originally Posted by pbolliger
The valve has to be in the same room preferably next to the appliance. Here is the rub .. Most shut off valves for kitchen stoves are behind the appliance... Hmmm
However you can access gas range valve by removing the bottom drawer (in most cases)
Reply With Quote
  #13  
Old 8/10/08, 2:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Gas flex line in crawl space

Quote:
Originally Posted by jpope
Also, appliance connectors are absolutely not allowed to pass through walls, floors, etc.
Nor through the cabinet of the appliance. About 1/2 of every furnace I see has the appliance connector going into the cabinet itself.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #14  
Old 8/12/08, 12:32 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Gas flex line in crawl space

Jeff what happened to the pictures in #8?



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #15  
Old 8/12/08, 1:07 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas flex line in crawl space

I have no idea. Maybe they expired after two and a half years. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Return air from crawl space WHI Inspecting HVAC Systems 11 1/9/12 8:43 PM
Crawl space in under house dnasser Structural Inspections 15 2/27/07 8:12 PM
Main sewer line vented in the crawl space jfunderburk Plumbing Inspections 3 1/15/07 7:15 PM
Strange Duct in Crawl Space jfunderburk Structural Inspections 3 1/11/06 1:02 AM


All times are GMT -4. The time now is 8:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts