Default Gas hot water heater in garage closet

Found a natural gas hot water heater in a garage closet that had been installed at floor level. I've seen gas water heaters in closet in garages before and always, without exception they are 18 inches above the floor level.

I flagged this as a safety concern and recommended that the buyer obtain further information from a qualified technician.

The closet had a self-closing metal door.

Another thing was that in addition to a six-inch fresh air intake pipe there was a vent high up on the wall that connected with the kitchen.

Another safety issue as far as I was concerned.

So I get a call from the owner's father ... he is upset because he made a few phone calls and some plumber told him the tank was perfectly okay, and the vent to the kitchen was okay.

So I told him, you get that in writing and give it to the buyer.

This is one unit in a townhouse complex that is about 12 years old. Apparently all the gas hot water tanks have been installed in this way.
Reply With Quote
  #2  
Old 7/24/08, 2:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gas hot water heater in garage closet

The tank must be permanently isolated from the garage, or be raised to at least 18" off of the floor. The door cannot open into the garage unless the tank is elevated.

There are some heater models that can be at floor level, but they must be listed accordingly.

The vent itself is not an issue - assuming that it is not the exhaust vent.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/24/08, 5:47 PM
wblakey wblakey is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Sechelt, BC
Posts: 431
Default Re: Gas hot water heater in garage closet

I guess they could say that the tank was isolated from the garage, but when I inspected it, the door was wedged open. As for the vent into the kitchen, what would be the purpose of this? And if the exhaust flue was damaged, would the fumes not make their way into the kitchen?
Reply With Quote
  #4  
Old 7/24/08, 6:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gas hot water heater in garage closet

If the door can be opened into the garage, it is not isolated from the garage. A flash-ignition could occur when/if the door is opened. That is why it must be raised within the closet.

"Isolated from the garage" means that there is no direct access from the garage. A closet door is direct access.

Water heaters and other gas-fired appliances are often located with the living spaces of a dwelling. Optimally, combustion-air is supplied through vents from the attic or exterior vent ports, but this is not necessarily required.

A recommendation for a CO detector is always prudent when gas-fired appliances are supplied or vented from the interior of a building.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 7/24/08, 7:44 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Gas hot water heater in garage closet

Quote:
Originally Posted by jpope
Optimally, combustion-air is supplied through vents from the attic or exterior vent ports, but this is not necessarily required.
As we all know "Combustion air ducts and openings shall not connect appliance enclosures with space in which the operation of a fan may adversely affect the flow of combusiton air." (2003 IRC M1701.4) Seems like a Kitchen range vent hood might fit that bill to me. It, of course, goes on to say no combustion air from sleeping rooms, bathrooms & toilet rooms as well.
Reply With Quote
  #6  
Old 7/15/10, 11:23 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Gas hot water heater in garage closet

Quote:
Originally Posted by jpope View Post
If the door can be opened into the garage, it is not isolated from the garage. A flash-ignition could occur when/if the door is opened. That is why it must be raised within the closet.

"Isolated from the garage" means that there is no direct access from the garage. A closet door is direct access.
Does anybody know which year this took affect?
Reply With Quote
  #7  
Old 7/15/10, 11:35 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Gas hot water heater in garage closet

Quote:
Originally Posted by jbraun View Post
Does anybody know which year this took affect?
The year is irrelevant as you are not doing code compliance certification, but the requirement has been around for a long time. If looking for a reference, dig up an installation manual online from the mfr. It will have the requirement in it.

As mentioned, floor level installation of non-FVIR type water heater in a room opening directly into a garage is improper, regardless of when it was done.

OP: I'm curious, where did the 6 inch fresh air intake open to: garage, exterior, attic?



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #8  
Old 7/15/10, 12:09 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Gas hot water heater in garage closet

I just want to know when for the purpose of knowing when.
Reply With Quote
  #9  
Old 7/15/10, 2:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: Gas hot water heater in garage closet

I have references that date this requirement back to the mid 60's, but it may be even earlier than that.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 7/15/10, 9:59 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Gas hot water heater in garage closet

2006 IRC M1307.3 Elevation of ignition source. Appliances having an
ignition source shall be elevated such that the source of ignition
is not less than 18 inches (457 mm) above the floor in garages.
For the purpose of this section, rooms or spaces that are not part
of the living space of a dwelling unit and that communicate
with a private garage through openings shall be considered to
be part of the garage
."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
flammable vapor ignition resistant dbaucum General Inspection Discussion 35 2/19/08 1:42 PM
Water Heater Dip Tube Failure jacaron Plumbing Inspections 2 2/24/07 11:28 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 10:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts