My morning inspection had me scratching my head.

Slab on grade.

I opened up the tight utility closet to find the gas-fired furnace and the gas-fired water heater in this closet with plenty of combustion air to the closet.

One problem...The main gas meter was installed about 12" above the top of the water heater. It was situated away from the exhaust pipe approximately 6". I didn't like this set-up at all.

Does someone have codes referencing this sort of gas meter installation?
Reply With Quote
  #2  
Old 4/8/06, 12:43 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,765
Default Re: Gas Meter location

I'm finding this, but no code references...

Meters installed inside a building must be located in a ventilated place. A meter must be more than 3 feet from any source of ignition or any source of heat that might damage the meter.
Reply With Quote
  #3  
Old 4/8/06, 2:19 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,890
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Meter location

Quote:
Originally Posted by dvalley
I'm finding this, but no code references...

Meters installed inside a building must be located in a ventilated place. A meter must be more than 3 feet from any source of ignition or any source of heat that might damage the meter.
NFPA 54

5.7.2 Location.

5.7.2.1 Gas meters shall be located in ventilated spaces readily accessible for examination, reading, replacement, or necessary maintenance.

5.7.2.2 Gas meters shall not be placed where they will be subjected to damage, such as adjacent to a driveway, under a fire escape, in public passages, halls, or coal bins, or where they will be subject to excessive corrosion or vibration.

5.7.2.3 Gas meters shall be located at least 3 ft (0.9 m) from sources of ignition.

5.7.2.4 Gas meters shall not be located where they will be subjected to extreme temperatures or sudden extreme changes in temperature. Meters shall not be located in areas where they are subjected to temperatures beyond those recommended by the manufacturer.

5.7.3 Supports. Gas meters shall be supported or connected to rigid piping so as not to exert a strain on the meters. Where flexible connectors are used to connect a gas meter to downstream piping at mobile homes in mobile home parks, the meter shall be supported by a post or bracket placed in a firm footing or by other means providing equivalent support.

5.7.4 Meter Protection. Meters shall be protected against overpressure, back pressure, and vacuum, where such conditions are anticipated.
Reply With Quote
  #4  
Old 4/8/06, 2:30 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,765
Default Re: Gas Meter location

Thank you, Joe.

I already told my client to get this meter evaluated and possibly moved to a safer location.

I just needed the code back-up you supplied.

Appreciate it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
City electrical inspector says move the meter and panel cbottger Electrical Inspections 9 4/4/07 8:59 PM
Outlet location psmothers Electrical Inspections 2 7/6/06 9:52 AM
Panel and Meter jwilliams7 Electrical Inspections 10 6/21/06 5:49 PM

All times are GMT -4. The time now is 4:30 AM.
no new posts