Default Gas unions

Is a gas union allowed inside the furnace cabinet?
Attached Thumbnails
gas-unions-104607-028-small-.jpg.jpg
Views:	120
Size:	62.7 KB
ID:	14215  
Reply With Quote
  #2  
Old 8/31/07, 4:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas unions

I know of nothing that would prohibit it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/31/07, 4:30 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Gas unions

The union was leaking and I just wanted to make sure that it is allowed in the cabinet.

Another question pertaining to unions. There was no union on the water heater line. (Or none that I could see) There is supposed to be one correct?
Attached Thumbnails
gas-unions-104607-037-small-.jpg.jpg
Views:	113
Size:	55.7 KB
ID:	14216  
Reply With Quote
  #4  
Old 8/31/07, 5:17 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas unions

With a flex line there would be no purpose for a union.

By the way. I do not see a dirt leg or a shut off valve for the DHW. I see a valve for the stub out only.

Last edited by phinsperger; 8/31/07 at 5:23 PM..
Reply With Quote
  #5  
Old 8/31/07, 5:56 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas unions

What the general consensus with drip "dirt" legs? Do you recommend them on any furnace/water heater where they are not present regardless of age? Do you recommend them on newer ones in which they should have one based on current code but do not? Basically, do you recommend retrofits?
Reply With Quote
  #6  
Old 8/31/07, 7:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas unions

I don't recommend them at all, because our utility company does not require them. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 8/31/07, 8:37 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas unions

maybe not due to moisture in the gas but what about the sediment that can develop in the line over time? Also, what if you have a unit that has the "install drip leg" label and one is not installed?
Reply With Quote
  #8  
Old 8/31/07, 9:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas unions

If I saw such a label, I would certainly recommend installing one. I have never seen such a label. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 8/31/07, 9:41 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Gas unions

Don't know about you guys, but I prefer hard pipe.

to use the right techniques for flare fittings.
Flared fitting with flex hose might be alright, but when it is kinked like in the picture, it make me wonder if it is right.

Marcel
Reply With Quote
  #10  
Old 8/31/07, 10:13 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Gas unions

Hi to all,

David, nothing to do with the piping issue, but I would suspect a heat exchanger problem based on the corrosion just to the left of that burner bar

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #11  
Old 8/31/07, 11:11 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Gas unions

Unions or bushings in concealed locations are prohibited according to my Code Check. Personally, I wouldn't get too bend out of shape over it if it's tight. However, unions tend to leak more often than threaded couplings.
Reply With Quote
  #12  
Old 9/1/07, 3:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Gas unions

Quote:
Unions or bushings in concealed locations are prohibited
That is correct but the furnace cabinet with excess door is not considered as a concealed area.

Quote:
However, unions tend to leak more often than threaded couplings.
This very true I find more leaks on unions than most anyother fittings but try to change a gas valve with a coupling in place of a union and you will be using a sawsall. I have observed that to many fitters will use a union to compensate for a misaligned pipe and just pull the two ends together with the union which most useally leads to a leak.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 9/1/07, 3:53 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: Gas unions

I could stand corrected but I think the drip leg is left over from whem they used to manufacture gas from coal ,hence the name coal gas.
http://www.zetatalk.com/energy/tengy112.htm
They used to cooke the coal and coal gas had a lot of moisture in it the left over from the manufacture was coke and this was sold to people to heat their homes,
We used it when I was a kid last century and it was alot cheaper then coal not as much heat.
......... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #14  
Old 9/1/07, 5:02 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Gas unions

Drip legs are required on all black iron gas supply lines in Massachusetts. I hardly ever find a drip leg on flex piping though. I call them out on black iron piping only.

I agree with Gerry on the furnace. There's signs of flames shooting out of the burner area. This issue may have been corrected already, but it still needs to be noted.

Usually when I find these signs, I shut the unit down and watch it fire up. Then write up my results.
Reply With Quote
  #15  
Old 9/1/07, 5:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas unions

Quote:
Originally Posted by mcyr
Don't know about you guys, but I prefer hard pipe.
Flexible appliance connectors are the preferred method in this state. When I see a complete "hard-pipe," I will always recommend upgrading. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Grounding at meter nbhi Electrical Inspections 5 7/23/07 11:55 PM


All times are GMT -4. The time now is 5:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts