Default Gas Water Heater FUBAR?

Did a new home today. The gas water heater had a single wall vent that went through the ceiling of the garage into the attic. Inside the attic, the single wall vent ran about 8 feet and connected to a B-vent and traveled about 25 feet to exit through the roof. The run of pipe was only supported at the ends. The joints for the vent sections were taped.

Question 1: can a single wall vent pass into the attic at all?

Question 2: can you use tape on the joints?

Question 3: Is there a c-de that specifies the support distances?

Pics attached. Thanks for your help.

P.S. The guy who did this work was the electrician, plumber, and HVAC contractor. All those systems had problems.

gas-water-heater-fubar-082406-088-small-.jpg.jpg
Views:	68
Size:	42.1 KB
ID:	5258 gas-water-heater-fubar-082406-089-small-.jpg.jpg
Views:	65
Size:	43.4 KB
ID:	5259 gas-water-heater-fubar-082406-091-small-.jpg.jpg
Views:	65
Size:	56.8 KB
ID:	5260



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 8/25/06, 1:38 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: Gas Water Heater FUBAR?

I would recommend someone of sound mind try it again....

What was the purpose of running it that direction, back of the house?
Reply With Quote
  #3  
Old 8/25/06, 1:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Gas Water Heater FUBAR?

Water heater was in a side-load garage. They wanted the flue to run out the rear roof.

The same "craftsman" put a 140,000 BTU furnace and a 60,000 BTU A/C in a 2000 sq. ft. house. Return duct and thermostat in separate rooms, of course.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 8/25/06, 1:44 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: Gas Water Heater FUBAR?

Quote:
Originally Posted by jfunderburk
Water heater was in a side-load garage. They wanted the flue to run out the rear roof.

The same "craftsman" put a 140,000 BTU furnace and a 60,000 BTU A/C in a 2000 sq. ft. house. Return duct and thermostat in separate rooms, of course.

...............
Reply With Quote
  #5  
Old 8/25/06, 1:57 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Gas Water Heater FUBAR?

1. No single wall allowed in attics.
2. Taped joints are fine, however, double-walled elbows are not to be used for single wall piping.
3. No code that I am aware of, but that shouldn't stop you from recommending "adequate" support.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 8/25/06, 2:03 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Gas Water Heater FUBAR?

Thanks Jeff.

Oh...the guy also failed to put GFCIs in bathrooms and the garage. Open splices were in the attic. Receptacles had no power. He installed the microwave and it didn't work. He complained about the new Cuttler-Hammer 200 amp service panel and when questioned, said FPE Stab-lok was the best ever made.

I'm thinking they need to remove all the sheetrock and closely examine everything he did.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 8/25/06 at 10:32 PM..
Reply With Quote
  #7  
Old 8/25/06, 7:42 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Gas Water Heater FUBAR?

Quote:
Originally Posted by jpope
1. No single wall allowed in attics.
2. Taped joints are fine, however, double-walled elbows are not to be used for single wall piping.
3. No code that I am aware of, but that shouldn't stop you from recommending "adequate" support.
Oh, no! I'm agreeing with Jeff again.

With one exception. I believe the tape on the joints should be appropriately rated for high temperatures, not King George II's duct tape. The tape in the picture looks like it is HTT (high-temperature tape).



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 8/25/06, 9:06 AM
Andrew Way Andrew Way is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Aledo, TX
Posts: 232
Default Re: Gas Water Heater FUBAR?

Joe,
Support for metal ducts should be made at least every 10' with metal straps wire, or other approved means. Reference 2003 IRC M1601.3.2



Andrew Way
Keystone Residential Inspection Services PLLC
www.keystoneinspections.com
Reply With Quote
  #9  
Old 8/25/06, 10:33 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Gas Water Heater FUBAR?

Quote:
Originally Posted by away
Joe,
Support for metal ducts should be made at least every 10' with metal straps wire, or other approved means. Reference 2003 IRC M1601.3.2
Wonderful help. Thanks.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 8/25/06, 12:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Gas Water Heater FUBAR?

It's a stretch (a long stretch I might add) to say that M1601.3.2 applies here as Chapter 16 covers duct systems for heating and cooling.

M1601.1 Duct design. Duct systems serving heating, cooling and ventilation equipment shall be fabricated in accordance with the provisions of this section and ACCA Manual D or other approved methods.

Personally, I would not consider using that reference in this case. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 8/25/06 at 1:08 PM..
Reply With Quote
  #11  
Old 8/25/06, 2:59 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,607
Default Re: Gas Water Heater FUBAR?

M1801.7 & 1803.3 Manufacture's installation instructions apply. As does, as always, common sense.
Reply With Quote
  #12  
Old 8/25/06, 10:13 PM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Gas Water Heater FUBAR?

Joe, what is your concern about the BTUS on the HVAc system? That should be irrelevant to your inspection right?
Reply With Quote
  #13  
Old 8/25/06, 10:16 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Gas Water Heater FUBAR?

Quote:
Originally Posted by thejnicki
Joe, what is your concern about the BTUS on the HVAc system? That should be irrelevant to your inspection right?
The SC standards of practice mandate that we report BTUs. Even if it weren't for that, I think it's a good idea and a valuable service. I have never done anything other than report the facts--the BTUs. However in this case there was such a blatent question about it that I referred it to a specialist.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #14  
Old 8/25/06, 11:06 PM
cradan cradan is offline
Active Poster
 
Join Date: Aug 2003
Location: Minooka, IL
Posts: 239
Please Note: cradan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Water Heater FUBAR?

High-temp. tape or not, long vent runs like that are often better-secured with mechanical screw-type fasteners (not to mention some hangers). Looks like the last elbow is actually supported by a purlin. If it's B vent and sitting on the framing, you still need minimum 1" clearance to combustibles.

Here's some IRC Fuel Gas:

[2426.6] All portions of vents shall be adequately supported for the design and weight of the materials employed.

[2427.10.10] A vent connector shall be supportd for the design and weight of the material employed to maintain clearances and prevent physical damage and separation of joints.
Reply With Quote
  #15  
Old 8/26/06, 8:44 AM
Andrew Way Andrew Way is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Aledo, TX
Posts: 232
Default Re: Gas Water Heater FUBAR?

Ooops,
Jeff is correct, I thought I was still in the exhaust systems chapter, that and I obviously didn't read it properly. Good thing I don't go around quoting code in my reports.



Andrew Way
Keystone Residential Inspection Services PLLC
www.keystoneinspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Client wants a new water heater adirienzo General Inspection Discussion 46 5/18/09 11:27 PM
Venting an oil-fired water heater mh718 HVAC 3 11/16/06 10:36 AM
TPR & Combusiton Air thejnicki Plumbing 16 9/18/06 9:55 PM


All times are GMT -4. The time now is 8:38 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts