#1
|
||||
|
||||
|
Do you find anything wrong with the way the TPRV discharge pipe is installed and routed? Do you find anything wrong how the Gas Water Heater is sitting on the garage? Is the distance from the garage floor to the combuation chamber of the gas w/h correct? Or does the w/h requires to be set on a stand higher that 12" from the floor? |
|
#2
|
||||
|
||||
|
Where's the pictures?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
You can see the pictures. I refresh and open the mesage board and there they are. Here are attached. All comments are welcome.
Thanks! Last edited by jacaron; 10/30/08 at 9:33 AM.. |
|
#4
|
||||
|
||||
|
Quote:
As to the TPR, is the copper pipe going into the wall of the second picture coming from the TPR? If so that's wrong, it should discharge at the floor. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. Last edited by mnahrgang; 10/30/08 at 11:09 AM.. Reason: Corrected by Kenton S. |
|
#5
|
||||
|
||||
|
As Mark says... must be sealed combustion chamber, also known as FVIR to rest on the floor.
If that's a screen in the base, it indicates that the water heater is Flamable Vapor Ignition Resistant (FVIR), which in some jurisdictions are allowed to be installed in a garage without the typically-required 18" height requirement. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
Last edited by kshepard; 10/30/08 at 11:10 AM.. |
|
#6
|
||||
|
||||
|
Nothing wrong with it going through the wall to the exterior of the home, provided it discharges above grade and is conspicuous.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#7
|
||||
|
||||
|
Oops. my bad. Absolutely correct. Forgot about that, as I never see it around here.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#8
|
|||
|
|||
|
Are seismic restraints required in Florida?
|
|
#9
|
||||
|
||||
|
It has to turn down too.
In the world view we are all important and our mere existence effects all life. Jack Gilleland Home Inspection Services Clayton Commercial, Multifamily, and Residential jgilleland1@att.net Ohio_Commercial and_Home_Inspections activerain |
|
#10
|
||||
|
||||
|
Shouldn't it have a downward slope?
HLC Home Inspections Okla. Lic. #776 I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
|
|
#11
|
|||
|
|||
|
Please Note:
jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes, but it's hard to tell from the angle of the pic.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| A.O. Smith water heater recall | Gary Reecher | Inspecting HVAC Systems | 0 | 4/4/08 12:18 AM |
| TPR valve | acox | Plumbing Inspections | 19 | 5/27/07 1:36 PM |
| Water Heater Dip Tube Failure | jacaron | Plumbing Inspections | 2 | 2/25/07 12:28 AM |
| Need Help On Chimney Liners | Nick Scibetta | Exterior Inspections | 10 | 1/11/06 10:53 PM |