Question Gas water heater TPRV discharge tube??





Do you find anything wrong with the way the TPRV discharge pipe is installed and routed? Do you find anything wrong how the Gas Water Heater is sitting on the garage? Is the distance from the garage floor to the combuation chamber of the gas w/h correct? Or does the w/h requires to be set on a stand higher that 12" from the floor?
Reply With Quote
  #2  
Old 10/29/08, 10:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Gas water heater TPRV discharge tube??

Where's the pictures?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/29/08, 11:36 PM
John M. Acaron's Avatar
John M. Acaron John M. Acaron is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Panama City Beach, FL
Posts: 559
Default Re: Gas water heater TPRV discharge tube??

You can see the pictures. I refresh and open the mesage board and there they are. Here are attached. All comments are welcome.

Thanks!
Attached Thumbnails
gas-water-heater-temperature-pressure-relief-valve-discharge-tube-dsc03561.jpg   gas-water-heater-temperature-pressure-relief-valve-discharge-tube-dsc03562.jpg  

Last edited by jacaron; 10/30/08 at 9:33 AM..
Reply With Quote
  #4  
Old 10/30/08, 10:54 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Gas water heater TPRV discharge tube??

Quote:
Originally Posted by jacaron View Post
You can see the pictures. I refresh and open the mesage board and there they are. Here are attached. All comments are welcome.

Thanks!
18" in the garage is what is necessary UNLESS it is a sealed combustion chamber. According to Kenton, this is one.

As to the TPR, is the copper pipe going into the wall of the second picture coming from the TPR? If so that's wrong, it should discharge at the floor.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.

Last edited by mnahrgang; 10/30/08 at 11:09 AM.. Reason: Corrected by Kenton S.
Reply With Quote
  #5  
Old 10/30/08, 11:07 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Gas water heater TPRV discharge tube??

As Mark says... must be sealed combustion chamber, also known as FVIR to rest on the floor.
If that's a screen in the base, it indicates that the water heater is Flamable Vapor Ignition Resistant (FVIR), which in some jurisdictions are allowed to be installed in a garage without the typically-required 18" height requirement.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 10/30/08 at 11:10 AM..
Reply With Quote
  #6  
Old 10/30/08, 1:16 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Gas water heater TPRV discharge tube??

Quote:
Originally Posted by mnahrgang View Post
...As to the TPR, is the copper pipe going into the wall of the second picture coming from the TPR? If so that's wrong, it should discharge at the floor.
Nothing wrong with it going through the wall to the exterior of the home, provided it discharges above grade and is conspicuous.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 10/30/08, 2:08 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Gas water heater TPRV discharge tube??

Quote:
Originally Posted by jfunderburk View Post
Nothing wrong with it going through the wall to the exterior of the home, provided it discharges above grade and is conspicuous.
Oops. my bad. Absolutely correct. Forgot about that, as I never see it around here.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 11/2/08, 1:29 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Gas water heater TPRV discharge tube??

Are seismic restraints required in Florida?
Reply With Quote
  #9  
Old 11/4/08, 2:57 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Gas water heater TPRV discharge tube??

It has to turn down too.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #10  
Old 11/21/08, 11:38 AM
John A. Sopher's Avatar
John A. Sopher John A. Sopher is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Oklahoma City, OK
Posts: 240
Default Re: Gas water heater TPRV discharge tube??

Shouldn't it have a downward slope?



HLC Home Inspections



Okla. Lic. #776


I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
Reply With Quote
  #11  
Old 11/21/08, 10:35 PM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas water heater TPRV discharge tube??

Quote:
Originally Posted by jsopher View Post
Shouldn't it have a downward slope?
Yes, but it's hard to tell from the angle of the pic.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A.O. Smith water heater recall Gary Reecher Inspecting HVAC Systems 0 4/4/08 12:18 AM
TPR valve acox Plumbing Inspections 19 5/27/07 1:36 PM
Water Heater Dip Tube Failure jacaron Plumbing Inspections 2 2/25/07 12:28 AM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 10 1/11/06 10:53 PM


All times are GMT -4. The time now is 1:38 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts