Default gas water heater vent

Is ok for a gas water air vent to terminate in the attic.

Thanks





gas-water-heater-vent-img_5711-small-.jpg.JPG
Views:	235
Size:	26.5 KB
ID:	11586

gas-water-heater-vent-img_5721-small-.jpg.JPG
Views:	198
Size:	50.2 KB
ID:	11587



www.wisemovehomeinspection.com
Carl Pennick
Lighthouse Point, FL
954-946 2737
407-928 8489

Florida Licensed Home Inspector #65
NACHI #04072098
ICC #5294144
Certified Master Inspector
Reply With Quote
  #2  
Old 5/15/07, 8:17 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: gas water heater vent

No .. No



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #3  
Old 5/15/07, 9:31 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: gas water heater vent

Looks to me like WH is vented via the B-Vent going through the roof (which has its own issues), and the rectangular duct is admitting in combustion air from the attic via the grills at the top and bottom of the wall behind the WH.
Reply With Quote
  #4  
Old 5/15/07, 10:20 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: gas water heater vent

Quote:
Originally Posted by cpennick
Is ok for a gas water air vent to terminate in the attic.

Thanks





Attachment 11586

Attachment 11587
Joe, I believe the question was "can the combustion make up air source come from the attic?" and the question is yes. However the exhaust flue does have to discharge to the exterior.
Reply With Quote
  #5  
Old 5/19/07, 11:55 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: gas water heater vent

Are those broken decking boards in the second pic?
Reply With Quote
  #6  
Old 5/20/07, 12:14 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: gas water heater vent

Also, make sure those joints have screws in them to secure them.....not just tape.
Reply With Quote
  #7  
Old 5/20/07, 1:06 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: gas water heater vent

Modern B-vents are self-locking and should not have any screws. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 5/20/07, 1:24 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: gas water heater vent

that bottom connection in the second pic looked a little suspect. Just threw it out there just in case.
Reply With Quote
  #9  
Old 5/20/07, 5:50 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: gas water heater vent

Only place you should have screws is at the draft hood to flue pipe connection. There should be 3 screws installed at this connection.
Reply With Quote
  #10  
Old 5/20/07, 5:54 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: gas water heater vent

How do you guys feel about combustion air being drawn from attic with water heater located in closet and ceiling covering (sheetrock ceiling) above missing. Just hole in the ceiling above the water heater. I know the ceiling should be fireblocked, but I see this set up often in older construction.
Didnt mean to change the subject.
Reply With Quote
  #11  
Old 5/20/07, 6:34 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: gas water heater vent

Quote:
Originally Posted by Scott Schultz
Also, make sure those joints have screws in them to secure them.....not just tape.
Duct Tape or Duck Tape, is not designed to be used on Ductwork. It is general use tap. In the 2nd photo the lower section looks like General Purpose Duct Tape... The upper connection looks like the proper type of foil tape.


Off subject, what does everyone think about the use of the flex-lines used on the Hot & Cold water lines? I personally have not ever used them. I always add a 6" to 8" nipple to the top of the WH with a Di-elect union to CU. That way I have the available height for different size replacement WH. I also like to install valves on both hot & cold sides, that way I don't have to deal with waiting for the pipes to drain.

My family has owned a lot of rental homes, I worked on the construction of 90% of them.




Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #12  
Old 5/20/07, 6:52 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: gas water heater vent

Quote:
Originally Posted by jsieg
. . .what does everyone think about the use of the flex-lines used on the Hot & Cold water lines?
Standard operating proceedure in CA. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 5/20/07, 7:09 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: gas water heater vent

Quote:
Originally Posted by jpope
Standard operating proceedure in CA. . .
Jeff, I had a feeling someone from CA would be the first to reply. Standard due to Earth Quakes???

Would it be normal (or a good idea) to replace them each time the WH is replaced? (Flexable things tend to crack or break without notice). I know that they are made more durable but, would you replace them when replacing a WH?



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #14  
Old 5/20/07, 7:13 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: gas water heater vent

Is that a dryer vent being used as a flue?

tom
Reply With Quote
  #15  
Old 5/20/07, 7:55 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: gas water heater vent

Quote:
Originally Posted by tdietrich1
Is that a dryer vent being used as a flue?

tom
Looks like flexible B vent to me.

Single wall and double wall, 1" clearance.

http://www.hartandcooley.com/vent/all_vent.htm



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 5/20/07 at 8:01 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater vent & corrosion to tank. dmacy Plumbing Inspections 2 1/4/07 11:01 AM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
Return air and water heater vent jorbeck Inspecting HVAC Systems 5 10/9/06 7:42 AM
TPR & Combusiton Air thejnicki Plumbing Inspections 16 9/18/06 8:55 PM