One might want to mention the 25 foot is code ( But seeing we are not code keepers ) Unless the manufacture states different. Recommend checking your dryer"s guild lines if information is not available contact the manufacture of your dryer.
|
| Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America) |
|
#17
|
||||
|
||||
|
Quote:
Nanci you have the leisure of knowing the appliance installed and the requirements to best satisfy the needs of that appliance to comply with the Manufacturers' installation instructions when recommending repair. We as inspectors rarely see the dryer in the home as they normally do not convey; we are forced to recommend repairing to the lowest common denominator (Code is that minimum) and Marcel just points out that some Dryers will perform adequately and safely with runs which exceed the minimum.... I just don't like 'em!! - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#18
|
||||
|
||||
|
Quote:
To report that a dryer vent does not meet the code requirement, is erroneous and should state that the venting might exceed the limitations of the Manufacturer and should be further evaluated by an appliance technician to assure that it does not become a safety hazard. Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#19
|
|||
|
|||
|
Quote:
The 25 foot rule is the minimum standard. Deviation from that is based upon the recommendations of the manufacturer of a particular appliance and acceptance by a local AHJ. In those cases that we have encountered, the particular (specific) appliance is noted as compliant (and labeled as such). A future replacement requires additional review for compliance at the time of installation. Codes may vary and change. Acceptance of an appliance installation may not be applicable to future replacement. |
|
#20
|
||||
|
||||
|
Quote:
y |
|
#21
|
||||
|
||||
|
Please Note:
ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here's a manufacture table:
Maximum Vent Length with 90° elbows Example: GE (6.0+ capacity electric models) Rigid Metal- Hood Type-A 90 ft. 60 ft. 45 ft. 35 ft. 25 ft. |
|
#22
|
||||
|
||||
|
Quote:
As a builder I simply put the laundry on a exterior wall and run a 8 inch transition duct to a three flap termination... but that's just me... Now if I were to build one like I've encountered on inspections, I would certainly notify the buyer of the need for an appliance which will safely handle the additional run (providing I "got away with it" in the first place) but that doesn't help the subsequent buyers of the home. - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#23
|
|||
|
|||
|
Correct.
A particular installation may exceed IRC requirememt if it is still within the minimum requirement recommended by the appliance manufacturer and accepted as an approved installation by the AHJ. |
|
#24
|
|||
|
|||
|
A Dryer Vent exhaust run that exceeds 25 feet (without a Dryer present) should be noted as an excessive run.
Determination of code compliance can only be made based upon the Dryer to be installed. |
|
#25
|
|||
|
|||
|
Quote:
Good table for different manufacturers... ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Dryer Vent Repair Philadelphia | nhagarty | Ancillary Services & Additional Topics | 0 | 1/12/09 10:22 PM |
| Dryer Vent Cleaning Delaware County PA | nhagarty | Ancillary Services & Additional Topics | 0 | 1/11/09 1:22 PM |
| OAHI Out Of Control - Bylaws Breached - Documented Proof | rwand1 | Canadian Inspectors | 175 | 2/25/08 12:23 PM |
| Dryer vent | kblair1 | HVAC | 21 | 12/6/06 3:13 PM |
| Bad Dryer and Bath Fan Venting | Jkrt00 | HVAC | 3 | 3/14/06 12:07 AM |