Old 7/31/06, 9:51 AM
David C. Macy's Avatar
Default Gravity vent
I have not seen this type of venting system for a water tank flue. I have seen either the conventional or power vent.
How would you check if the vent is operational?
The tank wouldnt fire when I turned up the thermostat even though there was plenty of hot water.
Thanks
Dave
ID:	4831   gravity-vent-75906-stow-027-small-.jpg.jpg
Old 7/31/06, 10:13 AM
phinsperger's Avatar
Default Re: Gravity vent
Looks like a homemade attempt at a closed combustion system
Old 7/31/06, 12:20 PM
Joseph Hagarty,  CMI's Avatar
Bradford White Direct Vent....
http://www.bradfordwhite.com/images/...eets/103dv.pdf
http://www.bradfordwhite.com/images/...uals/41099.pdf
Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net
Old 7/31/06, 1:02 PM
Roy D. Cooke, Sr's Avatar
Thanks Joe you are a wealth of information and it is appreciated very much.
Roy Cooke Sr
Old 7/31/06, 1:10 PM
Ditto on the thank you.
Dave
Old 8/1/06, 2:47 PM
Robert J. OConnor's Avatar
There are basically three types of equipment venting: gravity venting (or natural draft), direct venting, and power venting (or mechanical draft). For gas fired water heaters I normally just see gravity venting (with the open type draft hood at the top of the water heater), and for boilers/furnaces either gravity venting or power venting. If I came across direct venting I would probably check with the WH manufacturer to make sure thats right for the equipment just because it's something I wouldn't usually see.
Same basic checks as a typical gravity vent WH, except for a few things like checking that there are tight connections on the vent (unlike a gravity vent which is intentionally open at the unit) and that the side-wall vent hood is at least 12" above grade (more for areas with significant snow).
The tank wouldn't fire when I turned up the thermostat even though there was plenty of hot water.
Sounds unusual that the WH wouldn't fire with hot water in the tank when you turned up the temperature. Was it close to the maximum temperature setting already, and did ya wait for a while to make sure it wasn't just a time delay.
Robert O'Connor, PE
LIU CW Post Adjunct Professor
www.reporthost.com/-rjo
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 4 10/12/07 6:38 PM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM