Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by cbottger
What about the dirty leg lets hear it
Sorry to annoy you, but you asked what was wrong and I pointed out what I thought. So so far there are a few problems.

As far as the drip leg goes I would say, yes, it requires one.
Reply With Quote
  #17  
Old 4/13/07, 12:13 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by Jason1
Sorry to annoy you, but you asked what was wrong and I pointed out what I thought. So so far there are a few problems.

As far as the drip leg goes I would say, yes, it requires one.
Not annoyed just playing around went and fed and water the horses in the barn and picked the stalls thought you were reading the IRC

The reason I am picking on the dirty leg in this area we do not install dirty legs in any area that is prone to freezing temps. Attics or on outside package gas heat and cooling units, busted dirty legs far out weight any moisture that may enter the gas valve by a lack of a dirty leg.

This may well just be a local thing have never really taken the time to look in the IRC. Would be curious to know about other areas especially up north where it really gets cold.
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #18  
Old 4/13/07, 12:26 AM
dharris dharris is offline
Active Poster
 
Join Date: Nov 2003
Posts: 1,392
Please Note: dharris is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Horz gas furnace in the attic whats Wrong???

If its a new unit, most mfgs require a drip leg....no flex line installed
Reply With Quote
  #19  
Old 4/13/07, 4:04 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by cbottger
The reason I am picking on the dirty leg in this area we do not install dirty legs in any area that is prone to freezing temps. Attics or on outside package gas heat and cooling units, busted dirty legs far out weight any moisture that may enter the gas valve by a lack of a dirty leg.
Huh? What do "dirty legs" have to do with moisture? I thought they were for sediment in the gas supply. There's moisture everywhere, so what would a "dirty leg" do?

Nonetheless, check with your local gas supply company. Here in San Diego they are not required.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #20  
Old 4/13/07, 8:34 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by rray
Huh? What do "dirty legs" have to do with moisture? I thought they were for sediment in the gas supply. There's moisture everywhere, so what would a "dirty leg" do?

Nonetheless, check with your local gas supply company. Here in San Diego they are not required.
RR There is moisture/condensate that travels with the gas within the gas distribution system and dirty legs are more for trapping the moisture than any solids that might be in the line. Different gas suppliers have different amounts of moisture present. The dirty leg should be a normal part of the maintenance program for for areas that have high levels of moisture. These traps if you would should be checked for moisture and or cleaned every time the furnace is serviced. That is why the manual shut off valve is suppose to be in the line ahead of the dirty leg for easy service.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #21  
Old 4/13/07, 10:46 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by cbottger
RR There is moisture/condensate that travels with the gas within the gas distribution system and dirty legs are more for trapping the moisture than any solids that might be in the line.
That dirty leg must be absolutely huge to trap all that moisture. Can you post a picture of one and/or explain how it works? Thanks.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #22  
Old 4/13/07, 11:28 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by rray
That dirty leg must be absolutely huge to trap all that moisture. Can you post a picture of one and/or explain how it works? Thanks.
RR we are not talking large volumes of water David Valley can probally just throw a PIc right up here. I don't have one readily available but all they are is a Tee in the supply line with the side take off pointing down with a 3 inch nipple installed with a cap on it to allow for any drainage removal. Water being heavier than gas will fall into this nipple thus not carried on into the gas valve.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 4/13/07 at 11:32 AM..
Reply With Quote
  #23  
Old 4/13/07, 11:42 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by cbottger
RR we are not talking large volumes of water David Valley can probally just throw a PIc right up here. I don't have one readily available but all they are is a Tee in the supply line with the side take off pointing down with a 3 inch nipple installed with a cap on it to allow for any drainage removal. Water being heavier than gas will fall into this nipple thus not carried on into the gas valve.
Sounds like you're describing a dirt leg, whose purpose is, indeed, to catch dirt, not moisture. I can't see the little bit of moisture that might be in gas doing much to a gas valve, especially when the relative humidity around that gas valve is usually in the 30% or higher range, except out in the desert, perhaps. Dirt, however, can clog the valve.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #24  
Old 4/13/07, 12:03 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by rray
Sounds like you're describing a dirt leg, whose purpose is, indeed, to catch dirt, not moisture. I can't see the little bit of moisture that might be in gas doing much to a gas valve, especially when the relative humidity around that gas valve is usually in the 30% or higher range, except out in the desert, perhaps. Dirt, however, can clog the valve.
Dirt leg, drip leg all the same and yes RR after working on these system for as long as I have I can tell you that moisture is carried in the lines with the gas more so in the more humid areas yes, and yes if even though a small amount of moisture can and does cause havoc in control valves I have changed to many of them out that have the white powdery scale in the valves from excessive moisture.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #25  
Old 4/13/07, 12:14 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Horz gas furnace in the attic whats Wrong???

I suppose so. Never heard of moisture being the reason for a dirt leg, and I also used to work on the systems from Corpus Christi up to Houston and inward to Bryan/College station, Austin, and San Antonio. Nonetheless, I have a list of 27 WALK inspections I gots to go do, so ciao y'all.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #26  
Old 4/13/07, 12:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by rray
I suppose so. Never heard of moisture being the reason for a dirt leg, and I also used to work on the systems from Corpus Christi up to Houston and inward to Bryan/College station, Austin, and San Antonio. Nonetheless, I have a list of 27 WALK inspections I gots to go do, so ciao y'all.
The term dirt has mis led many folks The real term Dirty leg is implying contamination I also have never observed real dirt in a gas system just rust, scale and other solids not dirt. Today is not a good day for walking anywhere unless you are a Duck here. See my post over on general discussions



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #27  
Old 4/13/07, 12:48 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Horz gas furnace in the attic whats Wrong???

Charlie, just got back to this--you covered it well.

I don't see what's so hard for some to understand that a "drip-leg" or a "dirt-leg" is the same thing, depending on where one might be. Here, they're called drip-legs because we have a high degree of moisture in the system, and they are required by the PUCO.

About the amount of moisture--a drop of water less than the size of a pin head can cause severe problems in the gas valve. Better the moisture falls into the leg than going into the valve.

27 WALK inspections...wow!! I only got 6 "insurance pictures" to do. They go quickly most of the time...and now I have to leave.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #28  
Old 4/13/07, 10:23 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Horz gas furnace in the attic whats Wrong???

Charley

In our area, we can't run any kind of gas line under the appliance, as shown in your pic.
I'd have run the gasline up on the back side of the furnace, high enough to install a dripleg, and then turn it down through the upper knockout.
Also, even if Manuf's allow, local CI's will turn you down for installing furnace in contact with combustible wood platform. They want brick, block, sheetmetal drainpan, etc. insulating unit from wood. Upflow or Horizontal.
Vent looks Ok from here, if it's all B'vent.
Ci's would call us on the hanging Romex running to unit with no disconnect switch.
I think I see Ref.L/S, but I see no Aux.Drain Pan w/drainline or panswitch.
I assume the Plenums are lined since there is no visible insulation, and no Mastic on any joints. Must be a really tight fitting installation?

I don't like the installation though. When that Furnace is running, you know those BTU's will be dripping/falling out of the bottom of that unit.
Reply With Quote
  #29  
Old 4/14/07, 8:40 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Horz gas furnace in the attic whats Wrong???

Quote:
Originally Posted by gveal
Charley

In our area, we can't run any kind of gas line under the appliance, as shown in your pic.
I'd have run the gasline up on the back side of the furnace, high enough to install a dripleg, and then turn it down through the upper knockout.
Also, even if Manuf's allow, local CI's will turn you down for installing furnace in contact with combustible wood platform. They want brick, block, sheetmetal drainpan, etc. insulating unit from wood. Upflow or Horizontal.
Vent looks Ok from here, if it's all B'vent.
Ci's would call us on the hanging Romex running to unit with no disconnect switch.
I think I see Ref.L/S, but I see no Aux.Drain Pan w/drainline or panswitch.
I assume the Plenums are lined since there is no visible insulation, and no Mastic on any joints. Must be a really tight fitting installation?

I don't like the installation though. When that Furnace is running, you know those BTU's will be dripping/falling out of the bottom of that unit.
Greg: We don't put drip legs on furnaces in attic installs here do to freeze potential.

The supply plenum is insulated to the inside and there was a safety pan not really visible in the pic for the A-coil with primary and secondary drains

That was not romax running to the unit a rubberized pigtail to an outlet.

No brick or cement runners for furnace to rest on here use wood runners all the time. C'I's here must not be as picky as yours
</IMG></IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Horizontal Furnace in Attic Anthony Joseph Inspecting HVAC Systems 5 10/12/07 9:08 AM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
Propane gas to attic furnace brepanshek Inspecting HVAC Systems 5 2/21/07 5:06 PM
Furnace in attic (High Efficient) jcordell Inspecting HVAC Systems 14 2/10/07 6:02 PM
Cat 1 Furnace in attic wdecker Inspecting HVAC Systems 2 6/14/06 1:28 AM


All times are GMT -4. The time now is 1:42 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts