Default HWH ?s

This from a one year warranty inspection. What do you think about the TPRV and the condensate line?
Attached Thumbnails
hwh-s-whwh-4-.jpg.jpg
Views:	86
Size:	73.7 KB
ID:	14872   hwh-s-whwh-6-.jpg.jpg
Views:	80
Size:	66.7 KB
ID:	14873  
Reply With Quote
  #2  
Old 10/2/07, 1:09 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: HWH ?s

Discharge of the TPR line isn't exactly visible is it?
Reply With Quote
  #3  
Old 10/3/07, 10:04 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HWH ?s

This must be out in the country.
Reply With Quote
  #4  
Old 10/3/07, 10:47 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HWH ?s

Quote:
Originally Posted by Rick Maday
This from a one year warranty inspection. What do you think about the TPRV and the condensate line?
Looks like there's a TPR drain line, A/C condensate line and HRV condensate line all going to a floor drain. All seems good to me but you folks seem to pay way more attention to the TPR drain/piping than we do up here; at least nothing is draining onto the floor.......
Reply With Quote
  #5  
Old 10/3/07, 10:49 AM
Emmanuel J. Scanlan Emmanuel J. Scanlan is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 1,036
Default Re: HWH ?s

Quote:
Originally Posted by Rick Maday
This from a one year warranty inspection. What do you think about the TPRV and the condensate line?
TPR Discharge piping, 2003 IRC:

Quote:
P2803.6.1 Requirements of discharge pipe.
The outlet of a pressure relief valve, temperature relief valve or combination thereof, shall not be directly connected to the drainage system. The discharge from the relief valve shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building. In areas subject to freezing, the relief valve shall discharge through an air gap into an indirect waste receptor located within a heated space, or by other approved means. The discharge shall be installed in a manner that does not cause personal injury or property damage and that is readily observable by the building occupants. The discharge from a relief valve shall not be trapped. The diameter of the discharge piping shall not be less than the diameter of the relief valve outlet. The discharge pipe shall be installed so as to drain by gravity flow and shall terminate atmospherically not more than 6 inches (152 mm) above the floor. The outlet end of the discharge pipe shall not have a valve installed.
That also appears to be the drain for the HVAC condensation pan ('s). Was there a trap before that or after the point the TPR is inserted into the drain?

No drain pan for the HWH either in an area where leakage can cause damage. 2003 IRC:

Quote:
P2801.5 Required pan.
Where water heaters or hot water storage tanks are installed in locations where leakage of the tanks or connections will cause damage, the tank or water heater shall be installed in a galvanized steel pan having a minimum thickness of 24 gage (0.016 inch) (0.4 mm) or other pans for such use. Listed pans shall comply with CSA LC3.
Obviously the HWH and heater is gas fired. The room appears to be small. Has the area been checked for proper combustion air source?



Knowledge is power, but sharing knowledge brings peace!

http://www.psinspection.com

TREC License# 7593

Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 1:43 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts