Default hydronic radiant floor heat on hot water tanks

Most hydronic in floor heating systems I see are on boilers. Your advice regarding this set up would be appreciated. Two hot water tanks providing in floor radiant heat. TPR valve was stamped for 15 PSI (looks like boiler TPR) on the HW tank. The TPR valve was leaking. Thanks.
Attached Thumbnails
hydronic-radiant-floor-heat-hot-water-tanks-pict0789-small-.jpg.JPG
Views:	16809
Size:	56.5 KB
ID:	36441   hydronic-radiant-floor-heat-hot-water-tanks-pict0765-small-.jpg.JPG
Views:	14058
Size:	43.7 KB
ID:	36442   hydronic-radiant-floor-heat-hot-water-tanks-pict0764-small-.jpg.JPG
Views:	3084
Size:	32.5 KB
ID:	36443  
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/14/10, 8:19 AM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 25,241
Default Re: hydronic radiant floor heat on hot water tanks

Here you go Mark.

Open System

The open system uses one heat source, your domestic water heater, to provide both floor heating and domestic hot water. The two systems are basically tied together.
The same water that ends up in your hot shower or dishwasher, for example, has passed through the floor first.

This is a very efficient system because one heat source is doing all the work. As long as the water heater is sized appropriately and matches your heating and domestic needs, the need for a separate heating system is eliminated.

Closed System

This approach utilizes a dedicated heat source for the radiant floor. The fluid in a closed system is re-circulated around and around in a completely closed loop. There is no connection whatsoever to the domestic water supply.
The main advantage to this system lies in the fact that, being closed, anti-freeze instead of water can be used as the heat transfer medium. If freeze protection is an issue, than a closed system with anti-freeze is a good idea.

Now whether or not that is the right kind of TPR, some plumbers might chime in.
Hope this helps.

Reply With Quote
  #3  
Old 4/14/10, 8:46 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 51,721
Default Re: hydronic radiant floor heat on hot water tanks

Mark,

No matter the heat source ,you still have a closed system as long as the water in it is not used for teh potable water system.

The pressure relief at 15-20 psi is right for a dedicated system depending on the elevation of the highest radiator.



As a Professional Home Inspector, I support the privacy of my clients.

For more information click Trustyourinspector.ORG


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me

Reply With Quote
  #4  
Old 4/14/10, 4:03 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 542
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hydronic radiant floor heat on hot water tanks

Update:

I talked to John Wood Canada and they said :

The hot water tanks providing radiant heat have to be an open system providing hot water to atleast one fixture or faucet. The TPR valves are improperly rated for pressure and heat and should be replaced.
Reply With Quote
  #5  
Old 4/14/10, 5:11 PM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 3,262
Default Re: hydronic radiant floor heat on hot water tanks

Electric water heater...not much heat!

Was it heating the whole house or just parts and how large was the house?



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #6  
Old 4/14/10, 5:24 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 51,721
Default Re: hydronic radiant floor heat on hot water tanks

Quote:
Originally Posted by mnicholet View Post
Update:

I talked to John Wood Canada and they said :

The hot water tanks providing radiant heat have to be an open system providing hot water to atleast one fixture or faucet. The TPR valves are improperly rated for pressure and heat and should be replaced.
Does it supply water to any faucet?

If not it's a closed system and the pressure relief is correct.



As a Professional Home Inspector, I support the privacy of my clients.

For more information click Trustyourinspector.ORG


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me

Reply With Quote
  #7  
Old 4/14/10, 5:46 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 25,241
Default Re: hydronic radiant floor heat on hot water tanks

Types of Radiant Heat Systems - Open, Closed and Indirect

A "closed" system is most often refers to a situation where your heat source is dedicated solely to the task of heating water for the radiant heating system. The term "closed" refers to the fact that the water in the radiant heat system re circulates continuously from the heat source through the tubing or radiators and back to the heater again.

The "open" system uses one heat source, your domestic water heater, to provide both floor heating and domestic hot water. The two systems are basically tied together. The same water that ends up in your hot shower or dishwasher, for example, has passed through the floor first. This is a very efficient system because one heat source is doing all the work. As long as the water heater is sized appropriately and matches your heating and domestic needs, the need for a "separate" heating system is eliminated. An open system using a tank type heater such as the "Phoenix" is the most efficient and simplest radiant system you can use and can be ordered with an internal solar coil.

An "open" system refers to a situation where the heat source - typically a water heater - provides hot water both for domestic use and to the radiant heating system.
When there is a call for heat, water is drawn out of the water heat tank, it circulates through the heating system, and then returns back to the water heater. That same water mixes with the water in the tank which is also the direct source of the domestic hot water. So, when a faucet is turned on, water that has been through the heating system is furnished for showers, dishwashers, etc.
While the Universal Plumbing Code does allow for open systems, some local building inspectors do not. Before deciding on or committing to a particular type of system, you should understand what is allowed in you area.

An "indirect " system allows you to separate your domestic/potable water from the water in your heating system and still use a single heat source. By pacing a heat exchanger between the water heater and the radiant heat system, separating the heating system water from the potable water.
Rather than sending water directly into the heating system from the water heater, a pump pushes water from the tank through the heat exchanger which has series of plates inside. At the same time, the water in radiant system is being circulated on the other side of these same plates in the heat exchanger. Heat from the water heater is transferred through the plates to the heating system water. Hence, the heating system water is heated "indirectly" from the water heater. Indirect systems are "closed" systems.

A tank type heater such as the Phoenix combined with a flatplate heat exchanger works best.


CLOSED INDIRECT SYSTEM, SINGLE MANIFOLD



Well if anything, its a good schematic.
Reply With Quote
  #8  
Old 4/14/10, 5:48 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 51,721
Default Re: hydronic radiant floor heat on hot water tanks

I think we can reasonably sure that Mark has encountered a closed system.

A 15 psi pressure relief would not hold on a domestic water system.



As a Professional Home Inspector, I support the privacy of my clients.

For more information click Trustyourinspector.ORG


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Strong sulpher smell and discolored water bbradberry Plumbing Inspections 10 3/16/10 1:05 AM
Water Pressure Problem dcossar Plumbing Inspections 19 11/21/09 8:47 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM

All times are GMT -4. The time now is 6:20 PM.
no new posts