Default Insulation shield

Since fiberglass is non-combustible, is an insulation shield required or recommended in an attic when a water heater double wall flue pipe is going through fiberglass loose fill insulation?

Thanks.
Reply With Quote
  #2  
Old 10/28/08, 3:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: Insulation shield

Yes, it is.

The vent manufacturer requires clearances from "building materials," not just combustible materials. The vents won't draft as effectively when there's a hot-spot created by insulation or other building materials.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #3  
Old 10/28/08, 5:45 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation shield

Quote:
Originally Posted by jpope View Post
Yes, it is.

The vent manufacturer requires clearances from "building materials," not just combustible materials. The vents won't draft as effectively when there's a hot-spot created by insulation or other building materials.
The vent should work better as the insulation keeps the heat in the pipe allowing exhaust gases to stay hotter thus creating a lighter, more buoyant gas and better draft.

The fear with creating a hot spot is that if it is:
1) hot enough,
2) and can emit IR radiation to nearby wood products
3) by pyrolysis over a longer period of time
4) the ignition temperature of the dry wood can drop from 800-900 deg F to the 375-400 deg F range

From a paper on pyrolysis:
"However, it is possible for smoldering or glowing to exist prior to flaming ignition if the imposed heating causes the wood surface to reach 200°C (392*F) or higher for the second regime of wood pyrolysis"
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Options in selecting materials for basement construction wdevries Canadian Inspectors 2 8/4/08 2:30 PM
History of Insulation with Masonry mcyr General Inspection Discussion 7 2/27/08 8:53 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM
New Old Insulation rcooke Canadian Inspectors 1 12/13/06 6:25 PM


All times are GMT -4. The time now is 9:32 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics