International Association of Certified Home Inspectors
|
|||||||
| Plumbing Inspections Contains discussions about plumbing. |
![]() |
|
|
LinkBack | Thread Tools |
|
#1
|
||||
|
||||
|
I've never seen this plumbing configuration. Supply lines on the left side supply water to the right side. Unfortunately the water was turned off at the time of the inspection but I wonder how adequate the flow would be with both sinks in operation. Any of you seen this before?
Vince Santos
StepByStep Home Services LC (734) 748-9584 Providing Home Inspection Services to Southeast Michigan ITA Trained and Certified |
|
#2
|
||||
|
||||
|
1/2' Copper at 40 p.s.i. and 40 ft. of pipe can supply 12 G.P.M.
Shouldn't be a problem. He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father |
|
#3
|
|||
|
|||
|
I agree with Mike on this one.
Frank Carey Inspection Solutions, LLC Wilkes-Barre/ Scranton PA Nachi ID -> 08022204 Frank@careyinspectpa.com www.careyinspectpa.com www.frankcareyconstruction.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Configuration | nbhi | Plumbing Inspections | 9 | 11/19/08 1:38 PM |
| Interesting Question? | jmckenna1 | Miscellaneous Discussion for Inspectors | 9 | 11/25/07 2:13 PM |
| Interesting Development at Inspectionnews | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 7 | 4/18/07 1:48 AM |