I've never seen this plumbing configuration. Supply lines on the left side supply water to the right side. Unfortunately the water was turned off at the time of the inspection but I wonder how adequate the flow would be with both sinks in operation. Any of you seen this before?
Vince Santos
Owner / Certified Home Inspector StepByStep Home Services LC (734) 748-9584 http://www.stepbystepinspections.com Providing Home Inspection Services to Southeast Michigan Active Rain blog http://activerain.com/sbsinspections ITA Trained and Certified Reg104669Cc |
|
#2
|
||||
|
||||
|
1/2' Copper at 40 p.s.i. and 40 ft. of pipe can supply 12 G.P.M.
Shouldn't be a problem. "Never underestimate the difficulty of changing false beliefs by facts." |
|
#3
|
|||
|
|||
|
I agree with Mike on this one.
Frank Carey Inspection Solutions, LLC Wilkes-Barre/ Scranton PA Nachi ID -> 08022204 Frank@careyinspectpa.com www.careyinspectpa.com www.frankcareyconstruction.com |
![]() |