Received a call from a Realtor I work with on intermittent sewer gases in parts of their building but not the third floor of three floor structure. Here is the dilemma:
What could be the cause? Any and all help is appreciated. Priority One Building Inspection Services d/b/a Home Check America Office: 866-245-4663 Cell: 815-715-6237 Full member InterNACHI: 06010792 IL license: 450.003154
|
|
#2
|
||||
|
||||
|
I have had similar occurrences in commercial buildings with restroom floor drain traps that have dried out allowing sewer gases to enter. Try pouring 3-4 cups of water in all restroom floor drains, wait a day and see if that helps. If so, teach the cleaning crews to do this once a week or so.
|
|
#3
|
||||
|
||||
|
I did some work in a commercial building and saw the plumber attach a AAV for a bathroom vent and it got buried in the wall behind the Sheetrock.
I asked him what happens if the valve fails and he just shrugged his shoulders and said he'd be long gone by then. I'm wondering if a thermal scan would locate any pipes that may be in the wall?? |
|
#4
|
|||
|
|||
|
Please Note:
sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Need to do a smoke test to locate the sewer gas source unless something obvious such as a dried out trap can be found.
I've found a variety of sources using smoke, including nails driven though pipes, ABS joints never glued, corroded out or rusted through pipes, you name it. One time a house had been converted to an office and they just sheet rocked over the bath tub, leaving the faucet and drain untouched. Never had a plugged vent cause an odor. |
|
#5
|
|||
|
|||
|
One of the vent stacks may be cracked inside the wall. I had this problem about 20 years ago in a resturaunt i owned. We found it by pouring cinamon extract down the stacks up on the roof. Pour some down, if you can smell it, you have a cracked pipe somewhere.
|
|
#6
|
|||
|
|||
|
Please Note:
afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
||||
|
||||
|
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
The problem is now intermittent due to pressure changes in the building due to wind, mechanical ventilation and stack effect all changing the pressure regimes constantly. The smell may ocur when a negative pressure occurs in the area where the problem plumbing is located.
Use a blower door to depressurize the area of the buildig where the smell is and you should be able to locate the source pretty quickly if its from an open/cracked DWV pipe. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Stupid ASHI legislatin in Washington DEAD. | gromicko | Legislation, Licensing & Legal Issues | 20 | 1/29/08 10:05 AM |
| Article on Commercial and Residential Inspections and Assessment | mcyr | Commercial | 2 | 8/6/07 2:26 AM |
| No "H" clips? | jbreazeale | Structural | 7 | 5/17/07 3:28 PM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Misc. Discussion | 53 | 8/30/06 6:58 PM |