Default Looking for input on plumbing issue.

I saw this abs plumbing vent in the attic. The through roof portion is 4". Note reducer to 2" abs. This vent serves toilet, and other fixtures. What are the specific issues here.
Attached Thumbnails
looking-input-plumbing-issue-img_0068.jpg  
Reply With Quote
  #2  
Old 4/10/07, 4:21 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Looking for input on plumbing issue.

O.K...I finally found something, I think.

According to an old chart I have a 2" vent pipe can handle 4 DFUs, while a 4" vent can handle 8 DFUs

(What a DFU is--I have no idea. Apparently it's some measurement of drainage venting)

Bathtub = 2 DFU each
Sink = 1 DFU ea
Shower = 2 DFU
Washer = 2 DFU
Diswasher = 2 DFU

So if that is a 2" vent for the house, you can determine it's capabilties using the chart.

BTW, UPC (United Plumbing Code) says the plumbing vent should protrude through the attic 6".



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #3  
Old 4/10/07, 4:23 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Looking for input on plumbing issue.

I just notice the toilet is not listed on my chart, but it should require some consideration in sizing the vent, don't you think? My guess is at least 2 DFU for the toilet.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #4  
Old 4/10/07, 4:41 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Looking for input on plumbing issue.

Quote:
Originally Posted by K Fonoimoana
I saw this abs plumbing vent in the attic. The through roof portion is 4". Note reducer to 2" abs. This vent serves toilet, and other fixtures. What are the specific issues here.
Was there another vent, a 4" main vent? If so, this is probably a secondary vent.

Around here, typically, all vents need to be 4" through the roof.
Attached Thumbnails
looking-input-plumbing-issue-plumbing-small-.jpg.jpg
Views:	132
Size:	65.4 KB
ID:	10702  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 4/10/07, 4:56 PM
dsmith1 dsmith1 is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: St. Lazare, QC
Posts: 79
Default Re: Looking for input on plumbing issue.

In cold climates the vent goes to 4" where it exits the building to help prevent frost forming that could block the vent pipe. Also the vent should not extend more that 12" above the roof for the same reason.
Reply With Quote
  #6  
Old 4/10/07, 5:11 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking for input on plumbing issue.

I believe a water closet is rated at 3 fixture units.
Reply With Quote
  #7  
Old 4/10/07, 5:18 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Looking for input on plumbing issue.

DFU =Drainage Fixture Units???



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #8  
Old 4/10/07, 5:30 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Looking for input on plumbing issue.

Issues at hand...

Looks like the 2"? rizer from wall, tee/elbow runs horiz., then elbows to 2"-4" increaser (not reducer) through the roof. Looks like a cost cutting design to me. But check with a plumber to make sure.

Stains on roof decking (plywood or slatboard?). Active or old?

No visible insulation ?

Probably more, but thats a start.

IMO
Reply With Quote
  #9  
Old 4/10/07, 6:57 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Looking for input on plumbing issue.

Quote:
Originally Posted by jwilliams4
I just notice the toilet is not listed on my chart, but it should require some consideration in sizing the vent, don't you think? My guess is at least 2 DFU for the toilet.
Jae, would it be possible your old chart is so old that toilets as we know where not around yet.???

Marcel
Reply With Quote
  #10  
Old 4/10/07, 7:17 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking for input on plumbing issue.

Quote:
Originally Posted by jwilliams4
DFU =Drainage Fixture Units???
Correct, as oposed to WSFU - water supply fixture units used in sizing supply piping.

If I remember correctly, the 2" vent pipe is good for up to 24 fixture units.

Like someone said, increasing pipe size to 4" where it goes through the roof is to prevent frost from closing up the pipe
Reply With Quote
  #11  
Old 4/12/07, 1:21 AM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
Default Re: Looking for input on plumbing issue.

Thanks to all who've replied. There is one other 2" vent for a total of two penetrations. This is Hawaii. The stains are old. I was wondering about dia. requirements or some quick easy rule of thumb. I think Jae may be on to something.
The vent in the picture is directly above the bathroom plumbing wall. I was wondering if the main soil pipe in the crawlspace (to cess) is 4", shouldn't the vent be the same regardless of wet or dry?

Last edited by kfonoimoana; 4/12/07 at 1:29 AM..
Reply With Quote
  #12  
Old 4/15/07, 4:56 AM
psiposs psiposs is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Liberty Lake, WA
Posts: 243
Send a message via Yahoo to psiposs
Default Re: Looking for input on plumbing issue.

I thought a toilet was always a 4inch vent. Maybe it was a cheat for a final inspection when the house was built. From outside roof view its a 4inch vent all the way. Or is just because thats what the builder/plumber had handy when they ran out of 2 inch.



Peter Siposs
Absolute Home Inspections
Home, Mold, IAQ, Radon, & Lead Based Paint
Liberty Lake, WA
Serving Eastern WA & Northern ID
Nachi# 05100181
peter@absolute-home-inspections.com
Reply With Quote
  #13  
Old 4/15/07, 9:25 AM
sturetsky sturetsky is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 27
Default Re: Looking for input on plumbing issue.

Quote:
Originally Posted by gveal
Looks like a cost cutting design to me.
IMO
I usually see 4" sewer main stacks, but if the vent is only serving minimal fixtures, 4" may not be necessary.

I agree running 2" is a $ savings, but it is also a space saver.
Reply With Quote
  #14  
Old 4/15/07, 7:22 PM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
Default Re: Looking for input on plumbing issue.

Thanks guys- I think I've leaned something here (frost issue, DFU's).
Reply With Quote
  #15  
Old 4/15/07, 10:36 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Looking for input on plumbing issue.

Guess no more
Look at the plumbing sample page

http://www.codecheck.com/images/CC5thEdSample.pdf



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM
Plumbing Code changes mcyr Plumbing Inspections 0 9/8/06 5:47 PM
A few useful posts - I forget from whom jmichalski Plumbing Inspections 12 3/30/06 9:06 PM


All times are GMT -4. The time now is 1:48 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts