Question Main supply "T's" off to 2nd floor

This may be area specific.

As a new Inspector in Toronto, I'm trying to be fair and reasonable with the New Home Builder I'm purchasing from.

During one of my site visits I checked through the basement and noticed the main water supply's connection at the beginning of the distribution system (at the front of the home), tee's up to the second floor bathroom giving those fixtures a direct cold water feed. The other half of the T is of course feeding the gas water heater ( at the rear).
I don't really see this as a problem except that I will install a water softening system, and this bathroom's cold water will not have been processed by the softener, unless I make changes to this arrangement. The pressure should be great, but the water around here is very hard.

Seems an odd/lazy way.
Is this common practice?

Any comments are appreciated.

Best,

Mark Ellison
Toronto,
Reply With Quote
  #2  
Old 4/24/06, 2:10 PM
dsmith1 dsmith1 is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: St. Lazare, QC
Posts: 79
Default Re: Main supply "T's" off to 2nd floor

You should have coordinated with your builder and let them know of any special requirements for the plumbing system. If the walls have not been closed in it should not be a be a big deal to rearrange the piping to accommodate your needs.
Reply With Quote
  #3  
Old 4/25/06, 5:23 PM
Mark Ellison Mark Ellison is offline
New User
 
Join Date: Mar 2005
Posts: 12
Please Note: Mark Ellison is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main supply "T's" off to 2nd floor

Thanks David,

I never realized branch service would start before the main supply reaches the "service area" (ie water heater area) of the home.

No biggie to route the pipes for the softener, just another task on the "HoneyDo" list.

More than anything, this was new to me, and I thought the builder was cutting corners.

Thanks for your input.
Reply With Quote
  #4  
Old 4/25/06, 8:00 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Main supply "T's" off to 2nd floor

Mark,
I agree with you, the main water supply valve at the house should turn off all water to the home. I don't see that as a special requirement of any kind. The 2003 International Residential Code (which your area may or may not adhere to) says in section P2903.9.1 Each dwelling unit shall be provided with an accessible main shutoff valve near the entrance of the water service. ..... Additionally, the water service shall be valved at the curb or property line in accordance with local requirements. Seems pretty clear to me, the builder screwed up. I'd push back on him to prove it's OK to plumb it the way he has.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 7:53 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 1:49 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts