Default Manabloc manifold with PEX piping

This is a plumbing management system installed in a house in 1995. I submit that the red and plue color coded piping is NOT PB, but amd looking for verification or rebuttal. Any help would be appreciated. Thanks!
Attached Thumbnails
manabloc-manifold-cross-linked-polyethylene-piping-manifold-pex.jpg  
Reply With Quote
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
  #2  
Old 11/9/09, 4:16 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Manabloc manifold with PEX piping

The "red and blue" simply indicates hot and cold. Looks like PB to me. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/9/09, 6:23 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Manabloc manifold with PEX piping

I agree with Jeff. Were you able to see any identification on the lines themselves?




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #4  
Old 11/9/09, 6:32 PM
Richard Murphy Richard Murphy is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tampa, FL
Posts: 260
Default Re: Manabloc manifold with PEX piping

The only identification on the PEX themselves was "Manabloc Tubing". I have seen PB used in various locations but never with this type of writing nor with the hold/cold color coding on the tubing. Current site applications show red and blue tubes, but I wonder what they were using in 1995
Reply With Quote
  #5  
Old 11/9/09, 6:33 PM
Richard Murphy Richard Murphy is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tampa, FL
Posts: 260
Default Re: Manabloc manifold with PEX piping

By the way, we did disclaim it as not verified, but could be PB and recommended further review by a licensed professional.
Reply With Quote
  #6  
Old 11/9/09, 7:14 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Manabloc manifold with PEX piping

95 does seem like a ways back. I had heard that it began being used out in CA back in 01 or 02. Started seeing it in TX in 03.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #7  
Old 11/9/09, 7:51 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: Manabloc manifold with PEX piping

Quote:
Originally Posted by rmurphy1 View Post
The only identification on the PEX themselves was "Manabloc Tubing". I have seen PB used in various locations but never with this type of writing nor with the hold/cold color coding on the tubing. Current site applications show red and blue tubes, but I wonder what they were using in 1995
PEX and PB are 2 different animals.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 11/9/09, 11:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Manabloc manifold with PEX piping

I've never seen gray PEX tubing, and I've never seen a gray PEX manifold.

http://www.pexsupply.com/



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 11/10/09, 12:29 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Manabloc manifold with PEX piping

Doesn't look like PB to me. Some of our first generation stuff down here (i.e., before California approved it and people were bringing it in from Canada and Europe) was gray. The oldest I've found it here in San Diego was 1997.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 11/10/09, 1:47 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Manabloc manifold with PEX piping

Quote:
Originally Posted by jpope View Post
I've never seen gray PEX tubing, and I've never seen a gray PEX manifold.

http://www.pexsupply.com/
I haven't either, and I'd bet anything it's PB Pipe as well.
Reply With Quote
  #11  
Old 11/10/09, 8:29 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Manabloc manifold with PEX piping

Quote:
Originally Posted by dduffy View Post
I haven't either, and I'd bet anything it's PB Pipe as well.
Ditto, Shell Oil didn't stop supplying PB resins for plumbing tubing applications until 1996. I have seen PB installed down here as late as the late 90's

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #12  
Old 11/10/09, 8:48 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Manabloc manifold with PEX piping

Its PB, may not be 2110 but its PB. No one in their right mind would ever manufacture pipe the same color as PB.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #13  
Old 11/10/09, 9:09 AM
Richard Murphy Richard Murphy is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tampa, FL
Posts: 260
Default Re: Manabloc manifold with PEX piping

Thanks all!
Reply With Quote
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
  #14  
Old 11/10/09, 10:59 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Manabloc manifold with PEX piping

"California" still hasn't approved it, although many cities/municipalities within the state have approved it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Bonding both hot and hold supply pipes kshepard Plumbing Inspections 22 5/4/08 8:00 AM
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM
PEX Manifold & Piping lfoster Plumbing Inspections 11 4/24/06 10:04 AM


All times are GMT -4. The time now is 9:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts