Default Natural Gas Dryer in Bathroom

I know its not permitted, but why?
Reply With Quote
  #2  
Old 2/27/07, 10:52 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,439
Default Re: Natural Gas Dryer in Bathroom

Quote:
Originally Posted by pbennett1
I know its not permitted, but why?
It's quite common in condos and apartments. What makes you think it's not permitted?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 2/28/07, 12:16 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,376
Default Re: Natural Gas Dryer in Bathroom

It's quite common in mid-size homes, as well, particularly those of about 2,500 SF down in Chula Vista, which is still booming. They tend to have 2½ baths, but that ½ bath is overly large since it is also the laundry room.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #4  
Old 2/28/07, 12:19 AM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 447
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Natural Gas Dryer in Bathroom

There's a joke in here somewhere....
Reply With Quote
  #5  
Old 2/28/07, 1:39 AM
pdoane's Avatar
pdoane pdoane is offline
Active Poster
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,041
Please Note: pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Natural Gas Dryer in Bathroom

Quote:
Originally Posted by pbennett1
I know its not permitted, but why?
You mean gas fired water heaters?
Reply With Quote
  #6  
Old 2/28/07, 2:46 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 392
Default Re: Natural Gas Dryer in Bathroom

Here's the copy from the 2000 IRC:
G2406.2 (303.3) Prohibited locations. Fuel-fired appliances
shall not be located in, or obtain combustion air from, any of the
following rooms or spaces:
1. Sleeping rooms.
2. Bathrooms.
3. Toilet rooms.
4. Storage closets.
Exceptions:
1. Direct-vent appliances that obtain all combustion air
directly from the outdoors.
2. Vented room heaters, wall furnaces, vented decorative
appliances and decorative appliances for installation
in vented solid fuel-burning fireplaces, provided that
the room is not a confined space and the building is not
of unusually tight construction.
3. A single listed wall-mounted unvented room heater
equipped with an oxygen depletion safety shutoff
system and installed in a bathroom provided that the
input rating does not exceed 6,000 Btu per hour
(1760W/hr) and the bathroom is not a confined space.
4. A single listed wall-mounted unvented room heater
equipped with an oxygen depletion safety shutoff system
and installed in a bedroom provided that the input
rating does not exceed 10,000Btu per hour (2930W/hr)
and the bedroom is not a confined space.
5. Appliances installed in a dedicated enclosure in which
all combustion air is taken directly from the outdoors,
in accordance with Section G2407.11. Access to such
an enclosure shall be through a weather-stripped solid
door equipped with an approved self-closing device.
Reply With Quote
  #7  
Old 2/28/07, 4:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,439
Default Re: Natural Gas Dryer in Bathroom

Well, most model codes do not address clothes-dryer locations specifically. They are generally held to manufacturers installation instructions. Although their exhaust/vent systems are covered by codes.

You'll notice dryer hook-ups in garages without any means to raise the dryer as required for furnaces and water heaters.

Here's what the IRC says. . .

G2438.1 (613.1) General. Clothes dryers shall be tested in accordance with ANSI Z21.5.1 and shall be installed in accordance with the manufacturer’s installation instructions.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 3/6/07, 8:29 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 392
Default Re: Natural Gas Dryer in Bathroom

Quote:
Originally Posted by jpope
Well, most model codes do not address clothes-dryer locations specifically. They are generally held to manufacturers installation instructions. Although their exhaust/vent systems are covered by codes.

You'll notice dryer hook-ups in garages without any means to raise the dryer as required for furnaces and water heaters.

Here's what the IRC says. . .

G2438.1 (613.1) General. Clothes dryers shall be tested in accordance with ANSI Z21.5.1 and shall be installed in accordance with the manufacturer’s installation instructions.
Jeff, dryers, both ng and electric, are required to have ignition source 18 inches above the floor.
Reply With Quote
  #9  
Old 3/6/07, 8:33 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,376
Default Re: Natural Gas Dryer in Bathroom

Quote:
Originally Posted by pbennett1
Jeff, dryers, both ng and electric, are required to have ignition source 18 inches above the floor.
Dryers are not required to be raised when located in the garage here in my territory because they are considered "attended" appliances. Consequently, as Jeff said, other than the venting system, they fall under the manufacturer's installation instructions.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 3/6/07, 9:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,439
Default Re: Natural Gas Dryer in Bathroom

Quote:
Originally Posted by pbennett1
Jeff, dryers, both ng and electric, are required to have ignition source 18 inches above the floor.
I agree that they should be, but they are not required to be by the model codes. Russell is on the right track here.

Appliances, addressed by model codes, are those that are part of the necessary equipment of a home - water heaters and furnaces are examples of necessary equipment.

Clothes washers/dryers, microwave ovens, ranges and such are not considered necessary and therefore, they are held to manufacturers installation instructions.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 9/10/07, 11:30 AM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 190
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Natural Gas Dryer in Bathroom

Quote:
Originally Posted by jpope
I agree that they should be, but they are not required to be by the model codes. Russell is on the right track here.

Appliances, addressed by model codes, are those that are part of the necessary equipment of a home - water heaters and furnaces are examples of necessary equipment.

Clothes washers/dryers, microwave ovens, ranges and such are not considered necessary and therefore, they are held to manufacturers installation instructions.
What does "Model Codes" Mean?

In the IRC 2003 the definition of Appliance is "A device or apparatus that is manufactured and designed to utilize energy and for which this code provides specific requirements."

Apparatus is defined as: equipment designed to serve a specific function

I'm not sure how a gas dryer installed in a bathroom or a closet directly connected to a bathroom does not fall under G2406.2 (303.3) Prohibited locations in the IRC book.

Quote:
G2438.1 (613.1) General. Clothes dryers shall be tested in accordance with ANSI Z21.5.1 and shall be installed in accordance with the manufacturer’s installation instructions.


I would think that going to by the stricter code would be wiser.

rrayQuote:


Dryers are not required to be raised when located in the garage here in my territory because they are considered "attended" appliances. Consequently, as Jeff said, other than the venting system, they fall under the manufacturer's installation instructions.

Attended appliance? Turn the dryer on and the burner comes on and turns off as needed. It doesn't sound any different than a furnace except the burner on a furance is normally easier for a home owner to see.

I'm still not sure how G2406.2 (303.0) does not apply.


Any help to get a better understanding would be great.


Reply With Quote
  #12  
Old 9/10/07, 12:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,439
Default Re: Natural Gas Dryer in Bathroom

Kevin,

"Model Codes" is simply a reference to the most recognized codes (such as the IRC or UBC), which are used as "models" for jurisdictions throughout the country. Many localities use these codes to "model" their own requirements for building standards.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 9/10/07, 12:41 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,376
Default Re: Natural Gas Dryer in Bathroom

Quote:
Originally Posted by Kevin Luce
What does "Model Codes" Mean?

In the IRC 2003 the definition of Appliance is "A device or apparatus that is manufactured and designed to utilize energy and for which this code provides specific requirements."

Apparatus is defined as: equipment designed to serve a specific function

I'm not sure how a gas dryer installed in a bathroom or a closet directly connected to a bathroom does not fall under G2406.2 (303.3) Prohibited locations in the IRC book.



I would think that going to by the stricter code would be wiser.

rrayQuote:


Dryers are not required to be raised when located in the garage here in my territory because they are considered "attended" appliances. Consequently, as Jeff said, other than the venting system, they fall under the manufacturer's installation instructions.

Attended appliance? Turn the dryer on and the burner comes on and turns off as needed. It doesn't sound any different than a furnace except the burner on a furance is normally easier for a home owner to see.

I'm still not sure how G2406.2 (303.0) does not apply.


Any help to get a better understanding would be great.
Once the furnace has turned off, one doesn't go to see. Once the dryer turns off, one goes to see if the clothes are dry. Hence, "attended."



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 9/15/08, 3:41 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 392
Default Re: Natural Gas Dryer in Bathroom

So, what about a bathroom with a fan only. The potential for dimished combustion air supply could create conditions conducive to carbon monoxide. Hence, no gas dryer in a bathroom.
You opinion now is...
Reply With Quote
  #15  
Old 9/15/08, 8:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,439
Default Re: Natural Gas Dryer in Bathroom

no different. . .

In fact, my wife and I just purchased an investment condo with this exact setup.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dryer sheets potential hazard badair Misc. Discussion 8 11/26/07 10:19 AM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 8 9/9/07 7:02 PM
dryer and bathroom vents aweston Misc. Discussion 4 10/22/06 11:12 AM
Dryer lint filter senomoto Misc. Discussion 6 5/14/06 10:01 AM
Bad Dryer and Bath Fan Venting Jkrt00 HVAC 3 3/13/06 11:07 PM


All times are GMT -4. The time now is 3:39 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts