Default New Construction Plumbing.....

Hi Inspectors,

What do you guys make of this plumbing in this new house? I am not sure of this "double P trap"? Also I can't figure what the cord with the plug (not plugged in) is for? Any Help? Comments?

Thanks,
Attached Thumbnails
new-construction-plumbing-100_3818-large-small-.jpg (Small).JPG
Views:	170
Size:	44.0 KB
ID:	9007   new-construction-plumbing-100_3819-large-small-.jpg (Small).JPG
Views:	139
Size:	29.0 KB
ID:	9008   new-construction-plumbing-100_3820-large-small-.jpg (Small).JPG
Views:	156
Size:	36.4 KB
ID:	9009   new-construction-plumbing-100_3823-large-small-.jpg (Small).JPG
Views:	204
Size:	44.9 KB
ID:	9010  

Last edited by gbrasseur; 2/8/07 at 3:34 PM..
Reply With Quote
  #2  
Old 2/8/07, 3:49 PM
arook arook is offline
Active Poster
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 256
Please Note: arook is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

Quote:
Originally Posted by gbrasseur
Hi Inspectors,

What do you guys make of this plumbing in this new house? I am not sure of this "double P trap"? Also I can't figure what the cord with the plug (not plugged in) is for? Any Help? Comments?

Thanks,
Cord looks like it may go to the dishwasher. Did they have a dishwasher to the left of the sink? Looks they there was based on the drain line.

Trap looks ok, although I'm not sure why they didn't route everything to one trap.

Last edited by arook; 2/8/07 at 3:53 PM..
Reply With Quote
  #3  
Old 2/8/07, 11:59 PM
twasion twasion is offline
Active Poster
 
Join Date: Jun 2006
Location: Whitefish, MT
Posts: 106
Please Note: twasion is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

The cord is probably for the dishwasher. The p-trap is OK and are often plumbed this way. I would have a triple stack of directional tee's for every thing. For example: one trap for each sink bay (two total) and one for the garbage disposer.
Reply With Quote
  #4  
Old 2/9/07, 10:10 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

Couple problems.

If the red hot pipe is PEX, it is coiled in a manner inconsistent with its approved use....In other words, it is looped too tightly and appears kinked. This is a plumbing code violation.

The drain from the dishwasher is not connected at the highest point under the counter. This could cause backsiphonage of waste water back into the DW.

The second trap is completely unnecesary and the DW drain could have been simply installed to a diswasher "T" as part of the extension of the baseket strainer.

Looks like there is an air admittance valve for ventilation.

AAVs usually need to be installed above the flood level rim of the sink. This installation would normally be flagged as illegal.
Reply With Quote
  #5  
Old 2/10/07, 9:40 AM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: New Construction Plumbing.....

That doesn't look like PEX coiled. It looks like PEX before the valve. It looks like sloppy work.
Reply With Quote
  #6  
Old 2/10/07, 10:57 AM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

One GFCI next to the sink, but not the other. Nice try, although it could be on the same circuit. Good use of plumbers putty to stop the weeping. I am shocked. As I DIYer I could do better! And I know how much you guys hate DIYers!

Last edited by Ian Gills; 2/10/07 at 11:00 AM..
Reply With Quote
  #7  
Old 2/10/07, 11:46 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: New Construction Plumbing.....

http://www.homeinspections-usa.com/hitips.php3



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #8  
Old 2/10/07, 11:55 AM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

The red line appears to be reinforced poly supply line to dishwasher.
Reply With Quote
  #9  
Old 2/10/07, 12:01 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

Quote:
Originally Posted by staylor5
That doesn't look like PEX coiled. It looks like PEX before the valve. It looks like sloppy work.
Regardless if it is some type of PEX or other material, it appears kinked in photo 4 which is a plumbing code violation.
Reply With Quote
  #10  
Old 2/10/07, 1:27 PM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

"Regardless if it is some type of PEX or other material, it appears kinked in photo 4 which is a plumbing code violation."


By definition- it's a flexible water connector. Not to say that I'm all for kinks, but please cite the code that the kink violates.
Reply With Quote
  #11  
Old 2/11/07, 11:07 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

Quote:
Originally Posted by jcundiff
"Regardless if it is some type of PEX or other material, it appears kinked in photo 4 which is a plumbing code violation."


By definition- it's a flexible water connector. Not to say that I'm all for kinks, but please cite the code that the kink violates.
2003-2006 International Residential Code plumbing requirements for example:

Quote:
P2608.2 Installation of Materials. "All materials shall be installed in strict accordance with the standards under which the materials are accepted and approved. In the absence of such installation procedures, the manufacturer's installation instructions shall be followed. Where requirements of referenced standards or manufacturer's installation instructions do not conform to the minimum provisions of this code, the provisions of this code shall apply.
To make this long story short, flexible pipes are not permitted to be 'bent' beyond a certain radius as described by their testing and listing or according to their manufacturers installation instructions.

No manufacturer allows for their flexible pipe to be 'kinked'. It simply weakens or damages the pipe.

A common formula is to not allow a flexible pipe, like PEX, to be bent in a radius that exceed 6X it's pipe diameter.

What this means, is that if one is using 1/2" PEX pipe, it cannot be bent in an arc of radius that is produced by a circle with a radia of 3".

A 'kink' is not an 'arc'.

A 'kink' is a 'bend', and flexible pipe is not designed nor intended to be 'bent'.

I won't pretend to know just what kind of pipe material we are dealing with connecting the dishwasher supply in the original photos....Nor should anyone else. But presuming it is PEX, it is 'kinked' and 'bent' beyond it's design and therefore a plumbing code violation...and least under IPC/IRC.

Here is a link illustrating maximum bending radius for some types of PEX tubing:

http://www.pexsupply.com/bending_radius.asp

Hope this helped.

Last edited by homebild; 2/11/07 at 11:12 PM..
Reply With Quote
  #12  
Old 2/11/07, 11:14 PM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

Its a stretch- but left to the ahj's interpretation, it might not fly under this rule. A flexible water connector cannot be grouped with Pex, PB, or any other flexible tubing.
Reply With Quote
  #13  
Old 2/11/07, 11:30 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

No stretch...And sorry to disagree.

What I have stated is properly applied and basic plumbing code.

"Code" is what manufacturer and testing agencies determine to be the proper installation procedures for that given material.

A 'fexible water connector' IS grouped in the same way as PEX, PB, or any other flexible tubing by the limits and listing of its material testing agency and manufacturer's installation instructions.

Generally speaking, a 'kinked' pipe violates its listing and installation instructions.

If you want specific answers, have the OP supply us with the type of flexible pipe being run to the dishwasher, so we can look up its listing and installation instructions to be 100% sure.

Otherwise this 'catch all' Code section is designed to do just that:
Make all installations conform to the listing and manufacturer's instructions, and make 'Code' what the listing and installations instruction for the material demand.

Ohio Plumbing Code is based on the 2003 IPC, the plumbing code I cited.
You can see your own state's plumbing code online and its similar requirements here:
http://ecodes.iccsafe.org/iccf/gatew...0$vid=icc%3Aoh

Sorry.

Last edited by homebild; 2/11/07 at 11:41 PM..
Reply With Quote
  #14  
Old 2/12/07, 6:34 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: New Construction Plumbing.....

Homebild,
Now that john is done with you, were did you get your info for the AAV?



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #15  
Old 2/14/07, 11:31 AM
Mark Hopewell Mark Hopewell is offline
New User
 
Join Date: Feb 2007
Posts: 1
Please Note: Mark Hopewell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Construction Plumbing.....

AAV only needs to be 4" above the weir of the trap.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM