Old 10/6/06, 8:18 AM
thejnicki's Avatar
thejnicki thejnicki is offline
Default No Sleeve
Main drain line was buried by concrete at the perimeter foundation wall.
How would you correct this situation?
Old 10/6/06, 8:52 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
Default Re: No Sleeve
Perhaps a better questions is WHY would you correct this situation unless the drain pipe was damaged or stopped up.
Old 10/6/06, 8:56 AM
thejnicki's Avatar
There was no sleeve protecting the waste line, you would not note this condition in your report?
Old 10/6/06, 10:02 AM
phinsperger's Avatar
I don't see the problem either.
Old 10/6/06, 10:20 AM
Does your local area require a sleeve?
Old 10/6/06, 1:09 PM
thejnicki's Avatar
As far as I know this jurisdiction does require a protective sleeve..
Thanks for the input.
Old 10/6/06, 1:16 PM
Jeffrey R. Pope's Avatar
It's too late for "correction," short of removing the concrete or replacing the pipe with a smaller diameter and running through the existing.
CPC 313.10.1 Sleeves shall be provided to protect all piping through concrete and masonry walls.
The IRC requires sleeves as well. . .
P2603.5 Pipes through footings or foundation walls.
Any pipe that passes under a footing or through a foundation wall shall be provided with a relieving arch; or there shall be built into the masonry wall a pipe sleeve two pipe sizes greater than the pipe passing through.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net