I had the oddest inspection today of an REO property, the home was built in 2007 2900 sf. with three bathrooms.

The house has PEX Plastic Piping, there was water to two of the bathrooms and none at the Kitchen or one of the baths at the southwest corner of the house, a long distance from the Kitchen.

I looked and looked at every valve under sinks, toilets, the water heater, every possible place there could be a valve turned off, everyone in the house was on.

This made me very curious rather than just saying you needed a plumber, so I looked and looked for a Manabloc for the PEX, generally here they (if installed) are located in the garage, laundry room, or in a closet somewhere.

I could not find a Manabloc any where, and believe me I tried to figure out why there was no water to the Kitchen and that one bathroom for a LONG time, because this is the first time it has happened to me. I have built hundreds of buildings in my days, and this blew my mind.

The only thing I could think of after searching and searching for the problem was maybe there was a Manabloc in the attic, so I even went back up there a couple times looking and looking.

The house was occupied before it was repossesed so they certainly had to have water to the Kitchen and that bathroom, because I could tell they had both been used in the past.

Anybody have any idea what the problem could be?...the water was on when I arrived, so there was no water coming out from under the slab, or leaking from the pipes in the walls-ceiling or I certainly would have seen a MAJOR leak if there was NO water at all to these two areas.

Only thing I could think of, is the past owner may have known where a Manabloc was in the attic and turned a couple valves off in retaliation for the hard times of having the home reposessed.
Reply With Quote
  #2  
Old 10/1/08, 4:08 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,545
Brian E. Kelly .
Default Re: No water?

Buy an IR camera, locate where the water is blocked, then tell the client to CALL A PLUMBER.





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #3  
Old 10/1/08, 4:49 AM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 216
Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted
Default Re: No water?

Dale,
If it's in a sub division with other homes of the same model you could ask one of the neighbors if they know where the valve might be.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #4  
Old 10/1/08, 10:30 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,413
Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful
Default Re: No water?

good one Mark!




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #5  
Old 10/1/08, 10:41 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 3,677
James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute
Default Re: No water?

that is a strange one Dale....Mark's idea sounds like a winner though...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #6  
Old 10/1/08, 12:34 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,823
Dale Duffy .
Default Re: No water?

Quote:
Originally Posted by mjones6 View Post
Dale,
If it's in a sub division with other homes of the same model you could ask one of the neighbors if they know where the valve might be.
Yeah, good idea, (never thought of that), thanks......this really blows my mind..!!

Well, no matter what the question, someone always has a better idea.....!!
Reply With Quote
  #7  
Old 10/1/08, 1:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: No water?

I think you're on the right track. I have found manifolds buried in attic insulation.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #8  
Old 10/1/08, 3:14 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 216
Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted
Default Re: No water?

I might disconnect the hose at the sinks and run a fish tape into the hose see how far it goes. find a location that matches up. IE. 25' from the bathroom 15' from the kitchen sink. I hope you get the idea.

I would not actually do this on a home inspection.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com

Last edited by mjones6; 10/1/08 at 3:21 PM.
Reply With Quote
  #9  
Old 10/1/08, 3:38 PM
Richard A. Maday's Avatar
Richard A. Maday Richard A. Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 2,159
Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute
Default Re: No water?

Quote:
Originally Posted by mjones6 View Post
I might disconnect the hose at the sinks and run a fish tape into the hose see how far it goes. find a location that matches up. IE. 25' from the bathroom 15' from the kitchen sink. I hope you get the idea.

I would not actually do this on a home inspection.
I like your previous idea better!



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #10  
Old 10/1/08, 3:51 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 216
Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted
Default Re: No water?

So do I, but if that doesn't work and you've checked all the obvious places closets, cabinets etc... The second idea might help narrow down the location.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Site grading and drainage wdevries Canadian Inspectors 4 8/2/08 2:27 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM


All times are GMT -4. The time now is 10:06 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics