Default Piping tee'd off the TPR

Any Plumbers out there?

I thought I post this before, but maybe not.
I never got an explanation to the piping of this hot water tank where the piping is tee'd off the TPR coming out of the tank. I had a plumber with me at the time and he did not know either if this was right or wrong. Plumber was a friend of the client. Good plumber? LOL



piping-teed-off-tpr-gedc0090.jpg

Thanks
Reply With Quote
Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/5/10, 11:38 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,226
Default Re: Piping tee'd off the TPR

I would write it up, TPR shouldn't be installed in a tee, Second question why would they do that anyway. lol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #3  
Old 9/5/10, 11:42 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Piping tee'd off the TPR

Don't know Wayne, this was back in February, and never really found out.
I just stumbled over the picture in my documents.
I know at the time I stated in the report that it needed further evaluation from a licensed plumber, for it did not look like it was proper.
Still curious on the piping configuration.
Reply With Quote
  #4  
Old 9/5/10, 12:55 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,173
Default Re: Piping tee'd off the TPR

Quote:
Piping tee'd off the TPR
What did he do, and did they get in a fist-fight over it???

Seriously though...

No, not allowed. There should be no modification of any kind between the TPR valve and the tank, as well as no tee in the drain line. In the pic you posted, I would think there is a great chance the TPR would not release if it needed to.
Reply With Quote
  #5  
Old 9/5/10, 1:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Piping tee'd off the TPR

That is exactly what I told the Plumber friend of the client when I saw that. I told him, I think there is something wrong with that picture and he said, looks alright to me.
Then I said, look, the tpr should be on its own and if something happens, the pressure would release in the system instead of the exterior.
I still have not figured out the piping purpose on this configuration and what was the intent of the function.

Bugs the hell out of me.
Reply With Quote
  #6  
Old 9/5/10, 1:43 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Piping tee'd off the TPR

Quote:
Originally Posted by mcyr View Post
That is exactly what I told the Plumber friend of the client when I saw that. I told him, I think there is something wrong with that picture and he said, looks alright to me.
Then I said, look, the tpr should be on its own and if something happens, the pressure would release in the system instead of the exterior.
I still have not figured out the piping purpose on this configuration and what was the intent of the function.

Bugs the hell out of me.
Maybe the Plumber was on acid and thinking it was a good way to set up a circulation system.
Reply With Quote
  #7  
Old 9/5/10, 2:39 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,173
Default Re: Piping tee'd off the TPR

Quote:
Originally Posted by mcyr View Post
That is exactly what I told the Plumber friend of the client when I saw that. I told him, I think there is something wrong with that picture and he said, looks alright to me.
Then I said, look, the tpr should be on its own and if something happens, the pressure would release in the system instead of the exterior.
I still have not figured out the piping purpose on this configuration and what was the intent of the function.

Bugs the hell out of me.
Looks like a Tempering Valve peeking out from behind the TPR drain tube.
Reply With Quote
  #8  
Old 9/5/10, 3:07 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Piping tee'd off the TPR

I think it was Jeff, can't remember.
I should pull out the File Disc to see if I have other views.
Reply With Quote
  #9  
Old 9/5/10, 3:41 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,173
Default Re: Piping tee'd off the TPR

If it is, that would explain the piping setup. Hooked into the TPR still a major no-no. Guess they were thinking to not waste the scalding hot water when it gets ready to blow, and the tempering valve will prevent the person taking a shower from getting scalded when it does. Priorities ya know!
Reply With Quote
  #10  
Old 9/5/10, 4:04 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Piping tee'd off the TPR

Marcel, was this tank for storage or was it a water heater with a specific opening for the TPR?

Another thought to consider...

http://www.ashireporter.org/articles/articles.aspx?id=1568

From above article:

"From time to time, I find the TPR valve installed in the hot water piping away from the tank. Though standard storage tank water heaters have an opening specifically for the safety valve, some water storage tanks do not. In this situation and on the rare occasion the valve opening is used for something else, manufacturers recommend that a tee be placed at the hot water outlet and that the TPR valve be screwed directly into the top of the tee. The heat sensor (thermostat) of the TPR valve should pass through the tee and be submerged in the upper 6 inches of the tank water. The side opening of the tee is fitted and piped to deliver hot water to the house."



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 9/5/10, 4:16 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Piping tee'd off the TPR

Larry, I think you are right. It was a holding tank.
Just pulled out another photo from files that shows piping to the furnance.
That may help to explain the configuration.
I know at the time, I was baffaled by the way this was piped.



This help?

And to think the guy with me was a Plumber.
Reply With Quote
  #12  
Old 9/5/10, 5:35 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Piping tee'd off the TPR

The TPR looks like it has a dedicated discharge line pointing down. There are no valves upstream or downstream of the TPR valve itself. Only question I see is whether the sensor probe is actually long enough that it extends into the tank.

I think your plumber is OK here



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #13  
Old 9/5/10, 5:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Piping tee'd off the TPR

If there are no heating elements in that tank, there is no need for a TPR. It's probably just a pressure relief valve, in which case, it's OK.

The whole configuration is a bit extreme, but it appears to simply be a recirculating system or "hot water loop."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/5/10, 5:47 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Piping tee'd off the TPR

Thanks Jeff, that would make sense that only a pressure valve was needed. But the configuration of the piping on the tank sure took me for a loop at the time.
Must be why I kept that photo in my documents as a lone ranger for all this time. Still trying to figure it out.
Reply With Quote
  #15  
Old 9/5/10, 8:43 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Piping tee'd off the TPR

Quote:
Originally Posted by mcyr View Post
Larry, I think you are right. It was a holding tank.
Just pulled out another photo from files that shows piping to the furnance.
That may help to explain the configuration.
I know at the time, I was baffaled by the way this was piped.



This help?

And to think the guy with me was a Plumber.

That's a Canadian Boiler made in New Brunswick...EH! See them a lot in my area.

That Superstor tank is usually used in an indirectly heated DHW situation. The boiler would have its own TPR and the tank would have its own.

Here's from a Superstor installation manual:

DOMESTIC HOT WATER OUTLET CONNECTION
Use both thread tape and pipe dope, and connect an NPT brass tee. In the run of the brass tee, install an NPT brass T & P valve long element, for hot water storage tanks (ANSI Z212B-1984), by a nationally recognized lab that maintains periodic inspection of production listed equipment. Make sure that the relief valve is sized to the BTU/Hour capacity and storage capacity of the water heater. The temperature and pressure relief valve must be plumbed down so discharge can exit only 6” above, or at any distance below the structural floor; and cannot be in contact with any live electrical parts.


So it looks like it's done to manufacturer's instructions.....except it's not a brass T. These instructions are from a newer model though.

Last edited by Brian A. MacNeish; 9/6/10 at 6:54 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Bonding both hot and hold supply pipes kshepard Plumbing Inspections 22 5/4/08 8:00 AM
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM


All times are GMT -4. The time now is 10:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts