can a 4 inch toilet vent line be downsized to a 2 1/2 inch vent line 4 feet before the line terminates. The house was remodeled and a addition put on and this is in the new attic section. i don't have a picture.
any help is welcome. House 2 Home LLC 503-602-1420 HomePros@House2HomeLLC.ORG Protecting Peace of Mind One House at a Time IAC2 Certified IR Certified A favorite place on Google Maps |
| Find an InterNACHI certified Michigan Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Yes,
P3113.1 Size Of Vents. The minimum required diameter of individual vents,branch vents,circuit vents,vent stacks,and stack vents shall be at least one-halph the required diameter of the drain served. Vents shall not be less than 1.25 inches in diameter. Vents exceeding 40 ft. in developed length shall be increased by one nominal pipe size for the entire developed length of the vent pipe. |
|