Plumbing is not my strong suit so this drain had me a little stumped. The house is 3 years old. This is an island kitchen sink but it doesn't have an air admittance valve. It is 1-1/2" drain/P-trap that transitions to a 2" drain into the slab. Is it permissable to have an island drain with no air admittance valve? See photo.
|
|
#2
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
i believe the horizontal leg after the trap has a minimum length requirement.
otherwise it's considered an S-trap. someone should chime in on the length. in this application, i can't see how you'de do it without an AAV. |
|
#3
|
||||
|
||||
|
Quote:
http://www.theplumber.com/vent.html Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#4
|
|||
|
|||
|
Please Note:
bandag is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marcel, that's a neat website, I went to their homepage and looked at some of the topics under "the history of plumbing". glad I didn' grow up in that era!
www.theplumber.com |
|
#5
|
|||
|
|||
|
I checked the site. However I still can't determine if this is allowable or not. I don't think it is, but it is such new construction I'm hesitant to call it incorrect. I was wondering if somehow switching from the 1-1/2" to the 2" drain pipe might somehow make this situation allowable.
I have to get this report out tonight so I would sure would appreciate any help. |
|
#6
|
||||
|
||||
|
Quote:
Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#7
|
||||
|
||||
|
Quote:
Section P3111.3 IRC Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#8
|
|||
|
|||
|
So here is what I can figure:
P3111.1 "...A combination waste and vent system shall not receive the discharge of a food waste grinder." Since this drain DOES receive the waste from a food waste grinder, it should not be allowed. I don't even need to look at sizes I think. Does this sound right? |
|
#9
|
|||
|
|||
|
OK, I think I found the answer in P3105 and figure P3105.3. Looks like as long as it is within 6 feet of the vent (which is presumably in the closest wall) then it is OK.
|
|
#10
|
|||
|
|||
|
Please Note:
twasion is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would think that the vent is probably inside the wall tieing in with other vents.
|
|
#11
|
|||
|
|||
|
Please Note:
sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
If that is supposed to be a vent, it's on the wrong side of the trap.
It should come off the top of the 90. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Basement Bathroom Venting Question | Sean M. Jeric | Plumbing Inspections | 4 | 3/21/07 12:56 AM |
| Question about a gas fireplace vent | jvogan | Inspecting HVAC Systems | 10 | 3/20/07 9:46 PM |
| No plumbing vent...No problem | cceccarelli | Plumbing Inspections | 7 | 6/6/06 3:22 AM |