Ran across this situation today on a Warranty Inspection.
The picture show a plumbing vent in the attic. The vent runs horizontal for 20 - -25 feet across the attic to the vertical pipe that goes through the roof. Appeared to be plumbed to 4 incoming pipes. First question: is this horizontal run allowed. Second Question: The horizontal pipe appears to go downhill after the 'tee' fitting. So that in my opinion it would/could form a trap if rain water entered the vent from outside. I think you can see this in the first picture. This would be in need of repair, correct? Third Question: If this setup caused the vent pipe to fill with water and form a trap, would that cause the attached fixture drains to drain slowly? The homeowner had showed me the last sink on the line and complained that it often seems to have a slow drain and backs up at the beginning of the inspection. It did not do it when I was there. It seems that intermittant blockage from rain water could explain this type of intermittant problem. Reasonable? Any input or advice would be appreciated. Thanks in advance. Kevin Weiss Professional Inspector Infrared Imaging Specialist www.AbsoluteInspections.net Absolute Inspections, LLC 972-463-0887 |
|
#2
|
||||
|
||||
|
Horz run is allowed. It should slope to the drain at 1/4" per foot (just as a drainline is required to slope).
After that, nothing else really matters. It needs correction and could potentially cause drainage issues with the drain lines it serves. I wouldn't speculate as to rain water or anything else for that matter. Just recommend appropriate repairs. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Thanks for confirming for me, Jeff.
I was speculating more for my information than to include specific speculation in the report. Kevin Weiss Professional Inspector Infrared Imaging Specialist www.AbsoluteInspections.net Absolute Inspections, LLC 972-463-0887 |
|
#4
|
||||
|
||||
|
Please Note:
tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
|||
|
|||
|
Vent
Kevin Weiss Professional Inspector Infrared Imaging Specialist www.AbsoluteInspections.net Absolute Inspections, LLC 972-463-0887 |
|
#6
|
||||
|
||||
|
Here's the specific reference and commentary. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
|||
|
|||
|
Last picture shows what appears to be an air conditioning duct. It does not appear to be installed properly. Maximum sag should be nor more than 1/2 foot per meter. That sag looks greater than that.
Bill Siegel Florida Home Inspection Team Inc. |
|
#8
|
|||
|
|||
|
That is not a sag it is travelling down to the ceiling vent. Though sagging is not that uncommon around here with the soddy way the flex duct is installed.
Kevin Weiss Professional Inspector Infrared Imaging Specialist www.AbsoluteInspections.net Absolute Inspections, LLC 972-463-0887 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Plumbing vent next to exhaust vent | mpettitt | Plumbing | 4 | 10/12/07 6:38 PM |
| Question about a gas fireplace vent | jvogan | HVAC | 10 | 3/20/07 9:46 PM |
| Plumbing Vent...why so tall? | jvogan | Plumbing | 16 | 8/17/06 12:02 AM |
| Plumbing vent help | lclark | Plumbing | 3 | 7/21/06 4:31 PM |
| A few useful posts - I forget from whom | jmichalski | Plumbing | 12 | 3/30/06 10:06 PM |