Default Plumbing Vent Termination

I'm getting ready to submit one of my inspections for review and ran into a question. The plumbing vents in the residence do not penetrate the housing exterior. One ends in the attic and the other ends in the basement. Should I just recommend a professional plumber be called?
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/29/11, 4:09 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Plumbing Vent Termination

Quote:
Originally Posted by jake1 View Post
I'm getting ready to submit one of my inspections for review and ran into a question. The plumbing vents in the residence do not penetrate the housing exterior. One ends in the attic and the other ends in the basement. Should I just recommend a professional plumber be called?
For sure they could have some very serious dificulties .
I think you must have been away from class the day they talked about this .
More education for you could not hurt .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 6/29/11, 4:20 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Plumbing Vent Termination

Studor vents do not require penetration outside the building. However, most AHJ limit the use of such vents to kitchen islands and other such areas where an exterior penetration isn't practical. There should be at least one vent outside. I would write it up.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 6/29/11, 5:20 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Plumbing Vent Termination

Quote:
Originally Posted by jfunderburk View Post
Studor vents do not require penetration outside the building. However, most AHJ limit the use of such vents to kitchen islands and other such areas where an exterior penetration isn't practical. There should be at least one vent outside. I would write it up.
So... Oatey vents (aka... "AAV" Air Admittance Valves) would be acceptable???
Reply With Quote
  #5  
Old 6/30/11, 2:43 PM
Justin R. Ake Justin R. Ake is offline
InterNACHI Member
 
Join Date: Aug 2010
Posts: 14
Default Re: Plumbing Vent Termination

I was there that day for class. I was just curious as to the best way to write it up I guess. You're right though, a little more education could never hurt anybody. I'll look into some additional plumbing courses. Perhaps you should check out Hooked on Phonics.
Reply With Quote
  #6  
Old 6/30/11, 2:45 PM
Justin R. Ake Justin R. Ake is offline
InterNACHI Member
 
Join Date: Aug 2010
Posts: 14
Default Re: Plumbing Vent Termination

Ok thanks. I've seen the studor vents before in kitchen islands but these vents are just the result of laziness I think. They are in areas that shouldn't present much of a problem in regards to penetrating the exterior. I'll write it up just to be safe. Thanks again.
Reply With Quote
  #7  
Old 6/30/11, 2:56 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Plumbing Vent Termination

Quote:
Originally Posted by jjonas View Post
So... Oatey vents (aka... "AAV" Air Admittance Valves) would be acceptable???
If they are acceptable in a kitchen cabinet, why wouldn't they be acceptable in an attic?

But, like I said, most AHJs want to see the plumbing vents penetrate the roof and restrict AAV vents to locations where they are impractical to vent outside.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 6/30/11, 3:02 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Plumbing Vent Termination

Quote:
Originally Posted by jfunderburk View Post
If they are acceptable in a kitchen cabinet, why wouldn't they be acceptable in an attic?

But, like I said, most AHJs want to see the plumbing vents penetrate the roof and restrict AAV vents to locations where they are impractical to vent outside.
So are we discussing this with Joe the HI, or Joe the AHJ?

It would also be prudent to mention that AAV's need to be installed in areas with access. Typical lifespan of an AAV is just a few years. I feel that info should be notated in the report also.
Reply With Quote
  #9  
Old 6/30/11, 3:03 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Plumbing Vent Termination

Quote:
Originally Posted by jjonas View Post
So are we discussing this with Joe the HI, or Joe the AHJ?

It would also be prudent to mention that AAV's need to be installed in areas with access. Typical lifespan of an AAV is just a few years. I feel that info should be notated in the report also.
Does an attic have access?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 6/30/11, 3:04 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Plumbing Vent Termination

Quote:
Originally Posted by jfunderburk View Post
Does an attic have access?
Doesn't mean the AAV does!
Reply With Quote
  #11  
Old 6/30/11, 3:05 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Plumbing Vent Termination

Quote:
Originally Posted by jjonas View Post
So are we discussing this with Joe the HI, or Joe the AHJ?

It would also be prudent to mention that AAV's need to be installed in areas with access. Typical lifespan of an AAV is just a few years. I feel that info should be notated in the report also.
As an AHJ, I would not allow it in an attic. Others would, I suspect, because I can think of nothing off-hand to prohibit it. (Someone may point something out to me...I haven't researched it.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 6/30/11, 4:59 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Plumbing Vent Termination

I have spoken with plumbers about this and they see no issue if it is in an unpractical location.
Reply With Quote
  #13  
Old 7/1/11, 8:53 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Plumbing Vent Termination

The IRC permits individual branch or stack vents to terminate at an AAV, but the waste piping system they are connected to still must have at least one vent up through the roof to the outside ...

http://publicecodes.citation.com/ico..._31_sec002.htm

http://publicecodes.citation.com/ico...014_par002.htm

AAV's have to remain accessible, and if in an attic must be 6" above any insulation.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing vent cbono Canadian Inspectors 23 10/13/07 10:58 AM
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 5 10/12/07 5:38 PM


All times are GMT -4. The time now is 2:41 PM.