Default Plumbing Vent...why so tall?

Can anyone tell me why they would have extended this plumbing vent so tall? The toilet doesn't flush real well, and this vent is directly above that toilet. It is the only plumbing vent on the house. I was just wondering what the point to extending it 4 feet would be?



Attached Thumbnails
plumbing-vent-why-so-tall-plumbvent.jpg  
Reply With Quote
  #2  
Old 8/13/06, 11:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Plumbing Vent...why so tall?

Minimum heights are specified, but I know of no maximum. However, the height should not affect its function.

Are you sure that's a plumbing vent?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/13/06, 11:45 PM
jvogan's Avatar
jvogan jvogan is offline
Active Poster
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Please Note: jvogan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plumbing Vent...why so tall?

Yes, its a plumbing vent. You can see where they added on the extra pipe. As far as I know, the minimum is 12 inches above the roof. I am just curious as to why they would extend it?
Reply With Quote
  #4  
Old 8/13/06, 11:46 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,613
Default Re: Plumbing Vent...why so tall?

Quote:
Originally Posted by jvogan
Yes, its a plumbing vent. You can see where they added on the extra pipe. As far as I know, the minimum is 12 inches above the roof. I am just curious as to why they would extend it?
does this arae get a lot of snow that would be my thoughts
Roy Cooke
Reply With Quote
  #5  
Old 8/14/06, 12:04 AM
jvogan's Avatar
jvogan jvogan is offline
Active Poster
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Please Note: jvogan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plumbing Vent...why so tall?

Roy,
No, Missouri can get a lot of snow on occasion, but none of the other houses around here have vents this tall. Most are fairly close to the 12 inch mark. Like Mr. Pope said, the height shouldn't effect the operation, it is my own curiousity about why they would extend it. I just can't think of a good reason for doing so.
Reply With Quote
  #6  
Old 8/14/06, 1:26 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Plumbing Vent...why so tall?

I've was told by another inspector that when con artists come through a neighborhood and find a mark and they're doing HVAC work, one of the ways they leave signs for other con artists is by extending vents... like the one shown in the picture.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #7  
Old 8/14/06, 1:31 AM
jvogan's Avatar
jvogan jvogan is offline
Active Poster
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Please Note: jvogan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plumbing Vent...why so tall?

LOL! That is the most logical explaination for this that I have heard! Are you serious? This is not an inspection of mine...it is actually the house my girlfriend rented about a month ago. It has been bugging me ever since I first saw it. The owners of the house live right across the street...I will ask them if they had any work done. Thanks for the info!
Reply With Quote
  #8  
Old 8/14/06, 1:37 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Plumbing Vent...why so tall?

That's just what I was told. If it turns out the owners had work done, find out what they paid.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #9  
Old 8/15/06, 11:49 PM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 2,087
Default Re: Plumbing Vent...why so tall?

Ran across one like that a year ago. When I checked the code it was too high. If memory serves It's not supposed to be more the 3 or 4 inches above the adjacent roof. Do not quote me on this Check it out first.



Vern Mitchinson_CCHI_CMI
Registar
AlbertaNACHI
International Association of Certified Home Inspectors of Canada
Reply With Quote
  #10  
Old 8/16/06, 12:40 AM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Plumbing Vent...why so tall?

One possible issue. I've heard of extension to eliminate sewer gas smell from blanketing the yard, and extending the pipe higher would allow the prevailing winds to take it away, but there is also filters that can be fitted onto the pipe. Or a previous home inspector recommended the 10-foot/ 2-foot rule when the previous owner purchased the home!! HA! Who knows....
Reply With Quote
  #11  
Old 8/16/06, 12:53 AM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,091
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plumbing Vent...why so tall?

SECTION 904





VENT TERMINALS
904.1 Roof extension.






All open vent pipes that extend through
a roof shall be terminated at least
[NUMBER] inches (mm) above
the roof, except that where a roof is to be used for any purpose
other than weather protection, the vent extensions shall be run
at least 7 feet (2134 mm) above the roof.


Looks like ICC goofed when producing the latest CD version. As you can see no inches/mm listed. However I find the 7' comment interesting. Is there a second story deck or bedroom window anywhere near the vent stack?











Last edited by whandley; 8/16/06 at 12:57 AM..
Reply With Quote
  #12  
Old 8/16/06, 12:58 AM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,091
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plumbing Vent...why so tall?

904.5 Location of vent terminal.
An open vent terminal from
a drainage system shall not be located directly beneath any
door, openable window, or other air intake opening of the
building or of an adjacent building, and any such vent terminal
shall not be within 10 feet (3048 mm) horizontally of such an
opening unless it is at least 2 feet (610 mm) above the top of
such opening.

Reply With Quote
  #13  
Old 8/16/06, 12:59 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Plumbing Vent...why so tall?

No worries Will. They've corrected in for '06. The minimum is 6".



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 8/16/06, 7:09 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Plumbing Vent...why so tall?

Quote:
Originally Posted by jpope
The minimum is 6".

There you go...that's what I thought, too.
Reply With Quote
  #15  
Old 8/16/06, 8:29 AM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plumbing Vent...why so tall?

Get the thing up into a good wind and you might get a venturi effect across the top of it and really reduce the effectivness of the vent to draw air.
Larry
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing vent cbono Canadian Inspectors 23 10/13/07 10:58 AM
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 5 10/12/07 5:38 PM


All times are GMT -4. The time now is 10:05 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts