Default polybutylene?

I found a little of this hidden in my inspection today. I could not see any data stamped onto the piping although I am thinking it is polybutylene. Can someone confirm please? Thank you.
Attached Thumbnails
polybutylene-dsc06441-medium-.jpg.JPG
Views:	192
Size:	54.9 KB
ID:	25354  
Reply With Quote
  #2  
Old 11/22/08, 3:08 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: polybutylene?

Looks like PB pipe from here
Reply With Quote
  #3  
Old 11/22/08, 6:12 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: polybutylene?

If it is PB, it's not an issue unless you see crimped fittings.
Reply With Quote
  #4  
Old 11/22/08, 6:54 AM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: polybutylene?

Certainly appears to be PB, but you will normally find the PB2110 stamped on the surface.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #5  
Old 11/22/08, 9:25 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: polybutylene?

Quote:
Originally Posted by dvalley View Post
If it is PB, it's not an issue unless you see crimped fittings.

David, can you substantiate that statement? I've never heard that before. Most would say plastic fittings are MORE of an issue than crimped fittings. I simply say this anytime I see PB (the statement below is actually required by the State of NC whenever we see PB...but I modified it slightly to put in a web link and advising them to call a plumber):

"Polybutylene plastic plumbing supply lines (PB) are installed in the house. Polybutylene has been used in this area for many years, but has had a higher than normal failure rate, and is no longer being widely used. Copper and brass fittings used in later years may have reduced the failure rate. For more information about PB, see http://www.pbpipe.com and other Internet resources and/or rely on the evaluation and advice of a licensed plumbing contractor prior to the close of escrow."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 11/22/08, 12:30 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: polybutylene?

Quote:
Originally Posted by dvalley View Post
If it is PB, it's not an issue unless you see crimped fittings.
I would not suggest saying that PB 2110 is acceptable because it does not have crimped fittings.

Our Office recommends that all PB be replaced when found to be present.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 11/22/08, 2:38 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: polybutylene?

The type of fittings used with PB are not the only problem. Chlorine added to public municipal water supplies will cause deterioration of the pipe.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #8  
Old 11/22/08, 8:46 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: polybutylene?

I that a plastic dryer hose in that picture???
Reply With Quote
  #9  
Old 11/23/08, 11:21 AM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: polybutylene?

Quote:
Originally Posted by wsiegel View Post
I that a plastic dryer hose in that picture???
Yes it is venting a bathroom vent to the exterior wall above some ceiling tiles in a basement.
Reply With Quote
  #10  
Old 11/23/08, 7:37 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: polybutylene?

I would recommend they change out the dryer hose for safety reasons. Plus I agree you have PB on your hands. I would recommend a replacement.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
  #11  
Old 11/23/08, 11:12 PM
pabrioux pabrioux is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Peterborough, ON
Posts: 132
Default Re: polybutylene?

Quote:
Originally Posted by bboerner View Post
I would recommend they change out the dryer hose for safety reasons. Plus I agree you have PB on your hands. I would recommend a replacement.
Since that "plastic hose" is just a duct for a bathroom exhasut fan, not a dryer, it should be ok, no? You might recommend that it be the insulated type if it goes directly to the outside wall.

Paul-Marc
Reply With Quote
  #12  
Old 11/24/08, 8:36 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: polybutylene?

Quote:
Originally Posted by pabrioux View Post
Since that "plastic hose" is just a duct for a bathroom exhasut fan, not a dryer, it should be ok, no?
Paul-Marc
Metal is required around here...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #13  
Old 11/24/08, 11:39 AM
pabrioux pabrioux is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Peterborough, ON
Posts: 132
Default Re: polybutylene?

Quote:
Originally Posted by lkage View Post
Metal is required around here...
Ok, I didn't know that. I could see it for a dryer vent, but thought that for a bath exhaust fan a plastic type would be adequate.

Mark, do you know what's required out there on the island?

Paul-Marc
Reply With Quote
  #14  
Old 11/24/08, 12:44 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: polybutylene?

Yea I missed his post that the hose was venting the bathroom exhaust fan how I don't know fell asleep I guess or just assumed it was for the dryer lol regardless I always recommend installing metal over plastic for any type of venting especially those with any type of heat source.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
  #15  
Old 11/24/08, 8:32 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: polybutylene?

Most insurance companies around here are not insuring homes with PB water lines. Replace them. Too many issues either way.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Polybutylene Plumbibg? gbrasseur Plumbing Inspections 29 2/26/07 4:28 PM
polybutylene plumbing pwathen Plumbing Inspections 2 2/23/07 6:09 PM
polybutylene plumbing website kgerhauser Plumbing Inspections 4 2/10/07 8:53 AM


All times are GMT -4. The time now is 2:41 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts