Question Polybutylene Okay Anytime?

This system has copper fittings and is only used with well water which has a water softener. It only goes to the exterior hose bibs, shop, and drinking water for kitchen. City water supplies the rest of the home in copper pipes. (No Cross-over) Will the PB tubing survive here or should it "always" be recommended for replacement? The owner and buyers should be made aware of its presence at the least.

Vanguard Thermoguard Potable Tubing PB2110 SDR-11
Attached Thumbnails
polybutylene-okay-anytime-plumbing-pbpipe01a.jpg  
Reply With Quote
  #2  
Old 3/1/06, 7:16 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: West Chester, PA
Posts: 6,941
Default Re: Polybutylene Okay Anytime?

I always recommend replacement of PB 2110 when found.

http://nachi.org/forum/showthread.php?p=10909#post10909



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
PA NACHI Certified Inspector # 01102902
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #3  
Old 3/1/06, 8:13 PM
rbunzel's Avatar
rbunzel rbunzel is offline
Active Poster
 
Join Date: May 2005
Location: Anacortes, Wa
Posts: 143
Please Note: rbunzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Polybutylene Okay Anytime?

It my understanding that chlorine and fluoride are the suspect culprits causing the deterioration of the PB. Since this system is not exposed to that, deterioration should not be a major concern. It is always wise and prudent to disclose that there have been issues and educate the client to the point where they can make a good/bad decision. If you make it for them you assume the liability for that decision.

//Rick
Reply With Quote
  #4  
Old 3/1/06, 8:27 PM
Larry Kage, CMI Larry Kage, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: NW, MI
Posts: 11,641
Default Re: Polybutylene Okay Anytime?

Re: Polybutylene Okay Anytime?

Yes, it is okay until it leaks...then the damage the leaking causes can be substantial.

I agree with Joe in recommending replacement of PB 2110 when found.
Reply With Quote
  #5  
Old 3/1/06, 8:33 PM
Donald W. Johnston Donald W. Johnston is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Springdale, AR
Posts: 6
Default Re: Polybutylene Okay Anytime?

That's why I thought the PB would not deteriorate as quickly too. And in this usage it was not as great a safety concern to me. It is setup as a seasonal system too. I plan to give the clients some background about PB and leave the decision to them.

Thoughts from anyone else?

Donald
Reply With Quote
  #6  
Old 3/1/06, 9:07 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: West Chester, PA
Posts: 6,941
Default Re: Polybutylene Okay Anytime?

Donald:

You can minimize the consequence of PB 2110 all you like.

You can point out the decreased likelihood of failure in Well Water Service.

You can point out the Seasonal factors of use of the property.

Bottom Line. You will be News at 11 when the Pipe Fails.

What will be your defense then?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
PA NACHI Certified Inspector # 01102902
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #7  
Old 3/1/06, 10:03 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 759
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Polybutylene Okay Anytime?

also too many recalls on pb (from what i've read here in the past) for me to say it's ever o.k. well that's wrong, is o.k. to use PB in one area............the dumpster. (ha ha ha. i kill me.)
Reply With Quote
  #8  
Old 3/1/06, 10:04 PM
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 5,118
Default Re: Polybutylene Okay Anytime?

It is only a recomendation or suggestion. It costs you nothing to give it but may save you hundreds maybe thousands of dollars. What they decide to do with your recommendation is immaterial. Once you have given it the onus is on them to make a decision. I had a fella last year that did not take mine on PB and his dog woke him up at 3 AM and the hall bathroom was flooded on an off-grade house. He called me to tell me he wished he had listened to me but figured he had plenty of time to get around to it later. He was wrong. I always tell them, it will usually break on a 3 day week-end and you can't get a plumber until Tuesday. They always laugh but they get the point.
Reply With Quote
  #9  
Old 3/2/06, 3:42 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 17,424
Default Re: Polybutylene Okay Anytime?

There is still disagreement among many people, including plumbers. Here's what I use (note that plumbers are licensed in the State of California, and home inspectors are not, which fact is the underlying cause for my specific recommendation).

Quote:
Active water supply pipes appeared to be polybutylene plastic (hereafter, “PB”). It is believed that chlorine and fluorine react with PB, causing pipes to scale, flake, and become brittle. Micro‑fractures result, and the basic structural integrity of the system is reduced, thereby becoming weak and possibly leaking without warning. A home inspection cannot determine if PB water supply pipes are about to leak simply by looking at the outside of the pipes since they apparently deteriorate from the inside, and they can split or burst under pressure at any time. Insurance companies are known to decline to offer insurance on homes with PB water supply pipes because of associated problems with it. For helpful information about PB pipes and a class-action lawsuit, click here, click here, and click here. Recommend further evaluation by a licensed plumbing professional before close of escrow.

Last edited by rray; 3/2/06 at 3:47 AM..
Reply With Quote
  #10  
Old 3/2/06, 7:37 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: West Chester, PA
Posts: 6,941
Default Re: Polybutylene Okay Anytime?

Quote:
Originally Posted by rray
There is still disagreement among many people, including plumbers. Here's what I use (note that plumbers are licensed in the State of California, and home inspectors are not, which fact is the underlying cause for my specific recommendation).
In PA, Home Inspectors are required to be certified and insured. Contractors (Carpenters, Plumbers, Electricians etc...) are not. The greater burden of responsibility here is on the Home Inspector in making the right call.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
PA NACHI Certified Inspector # 01102902
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #11  
Old 3/2/06, 3:05 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Polybutylene Okay Anytime?

For helpful information about PB pipes and a class-action lawsuit, click here, click here, and click here.

Ah yes, it would be nice to be able to give the client links within the report, but alas, I am using Inspectvue.
Reply With Quote
  #12  
Old 3/2/06, 3:21 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Polybutylene Okay Anytime?

Can't put links in the report w/ inspectvue? I did not know that.
Reply With Quote
  #13  
Old 3/2/06, 5:18 PM
Donald W. Johnston Donald W. Johnston is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Springdale, AR
Posts: 6
Default Re: Polybutylene Okay Anytime?

I used what Russel wrote above and recommended replacement of the tubing as Joseph suggested. I also gave the clients links to 3 websites that discuss this. And I contacted Vanguard, the vendor. They confirmed PB (of course =D>) and gave me the information about the lawsuit. The client will receive that too.

Thank you to everyone for your direction!

Donald
Attached Files
File Type: pdf PB Litigation Fact Sheet.pdf (25.4 KB, 8938 views)




Donald Johnston, Jr.
Qualified Inspections, Inc.
Springdale, Arkansas
http://www.qualifiedinspections.com/
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/28/14, 3:15 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: West Chester, PA
Posts: 6,941
Default Re: Polybutylene Okay Anytime?

Received a recent email and call from an individual.. (not my client)
questioning an Inspection Report....
(from someone in another State / Province...

That Polybutylene Pipe / PB 2110 is somehow "Acceptable" and "Grandfathered" under some sort of perceived Building Code....

Polybutylene PB2110 must always be recommended to be replaced under all circumstances.

I Repeat....

Polybutylene PB2110 must always be recommended to be replaced under all circumstances.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
PA NACHI Certified Inspector # 01102902
Delaware Licensed Home Inspector # H4-071

Last edited by jhagarty; 5/28/14 at 3:34 AM..
Reply With Quote
  #15  
Old 5/28/14, 9:48 AM
Kenneth A. Ramm Kenneth A. Ramm is online now
InterNACHI Member
 
Join Date: Oct 2012
Location: New Glarus, WI
Posts: 507
Default Re: Polybutylene Okay Anytime?

Quote:
Originally Posted by jhagarty View Post
Received a recent email and call from an individual.. (not my client)
questioning an Inspection Report....
(from someone in another State / Province...

That Polybutylene Pipe / PB 2110 is somehow "Acceptable" and "Grandfathered" under some sort of perceived Building Code....

Polybutylene PB2110 must always be recommended to be replaced under all circumstances.

I Repeat....

Polybutylene PB2110 must always be recommended to be replaced under all circumstances.
Obviously someone is writing soft reports.





Kenneth (Kenny) Ramm
608-438-3986
rammhomeinspections@gmail.com
Home Inspections in Madison WI
Home Inspections in South Central WI

Wisconsin License 2516-106
InterNACHI #12101905
Home Inspections in Madison, WI and surrounding communities.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help - Polybutylene Pipes Rick G Plumbing Inspections 45 6/26/13 4:21 PM
Polybutylene Plumbibg? gbrasseur Plumbing Inspections 29 2/26/07 4:28 PM
polybutylene plumbing website kgerhauser Plumbing Inspections 4 2/10/07 8:53 AM
Is this Polybutylene gporter Plumbing Inspections 12 4/24/06 3:51 PM

All times are GMT -4. The time now is 7:47 AM.
no new posts