Default Pressure relief valve extension

The pressure relief valve extension is plastic and has a couple of elbows leading it to a drain. I always advise the client that the pipe should be copper and should terminate about 6" inches from the floor. I explain that it was routed to a drain to prevent a mess if it discharges but that you would want to see water on the floor if it was dripping or pressure had blown off so that you know there is a problem. I come across this A LOT around here and always write it up that it is not a preferred installation but want to ask what others thought. Thanks!
Attached Thumbnails
pressure-relief-valve-extension-img_5449.jpg  



Patrick Coulter
Cross County Inspection Services, LLC
(443) 266-7544
Reply With Quote
  #2  
Old 1/21/09, 2:35 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Pressure relief valve extension

When I find a PTR valve extension piped improperly, I simply note it and leave it at that.

504.6 Requirements for discharge piping

The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall:

1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room as the water heater.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area.
6. Discharge in a manner that does not cause personal injury or structural damage.
7. Discharge to a termination point that is readily observable by the building occupants.
8. Not be trapped.
9. Be installed so as to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.
11. Not have a threaded connection at the end of such piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section 605.4 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.
Reply With Quote
  #3  
Old 1/21/09, 2:37 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Pressure relief valve extension

What's up with the water heater roller coaster vent? I'd be writing up that vent installation.

All the Plumber had to do was install a WYE insert (at the main) and install the vent tubing into that.
Reply With Quote
  #4  
Old 1/21/09, 2:42 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Pressure relief valve extension

Lousy install on the gas line fittings also. I wouldn't write it up but they didn't need two elbows and a TEE. It could have been done with one elbow with a twist of the TEE.
Reply With Quote
  #5  
Old 1/21/09, 2:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Pressure relief valve extension

From the 2006 IRC.
- P2803.6.1 Requirements for discharge pipe. The discharge piping serving a pressure-relief valve, temperature-relief valve or combination valve shall:
- - 13. Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.

TABLE P2904.5
WATER DISTRIBUTION PIPE
MATERIAL ------------------------------------------------ STANDARD
Brass pipe ------------------------------------------------ ASTM B 43
Chlorinated polyvinyl chloride (CPVC) plastic pipe and tubing - ASTM D 2846; ASTM F 441; ASTM F 442; CSA B137.6
Copper or copper-alloy pipe -------------------------------- ASTM B 42; ASTM B 302
Copper or copper-alloy tubing (Type K, WK, L, WL, M or WM) -- ASTM B 75; ASTM B 88; ASTM B 251; ASTM B 447
Cross-linked polyethylene (PEX) plastic tubing ---------------- ASTM F 877; CSA B137.5
Cross-linked polyethylene/aluminum/cross-linked polyethylene (PEX-AL-PEX) pipe - ASTM F 1281; CSACAN/CSA-B137.10
Cross-linked polyethylene/aluminum/high-density polyethylene (PEX-AL-HDPE) - ASTM F 1986
Galvanized steel pipe ---------------------------------------- ASTM A 53
Polybutylene (PB) plastic pipe and tubing --------------------- ASTM D 3309; CSA CAN3-B137.8
Polyethylene/aluminum/polyethylene (PE-AL-PE) composite pipe - ASTM F 1282
Polypropylene (PP) plastic pipe or tubing ----------------------- ASTM F 2389; CSA B137.11
Stainless steel (Type 304/304L) pipe -------------------------- ASTM A 312; ASTM A 778
Stainless steel (Type 316/316L) pipe -------------------------- ASTM A 312; ASTM A 778



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #6  
Old 1/21/09, 2:54 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Pressure relief valve extension

Quote:
Originally Posted by mlarson View Post
From the 2006 IRC.
- P2803.6.1 Requirements for discharge pipe. The discharge piping serving a pressure-relief valve, temperature-relief valve or combination valve shall:
- - 13. Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.

TABLE P2904.5
WATER DISTRIBUTION PIPE
MATERIAL ------------------------------------------------ STANDARD
Brass pipe ------------------------------------------------ ASTM B 43
Chlorinated polyvinyl chloride (CPVC) plastic pipe and tubing - ASTM D 2846; ASTM F 441; ASTM F 442; CSA B137.6
Copper or copper-alloy pipe -------------------------------- ASTM B 42; ASTM B 302
Copper or copper-alloy tubing (Type K, WK, L, WL, M or WM) -- ASTM B 75; ASTM B 88; ASTM B 251; ASTM B 447
Cross-linked polyethylene (PEX) plastic tubing ---------------- ASTM F 877; CSA B137.5
Cross-linked polyethylene/aluminum/cross-linked polyethylene (PEX-AL-PEX) pipe - ASTM F 1281; CSACAN/CSA-B137.10
Cross-linked polyethylene/aluminum/high-density polyethylene (PEX-AL-HDPE) - ASTM F 1986
Galvanized steel pipe ---------------------------------------- ASTM A 53
Polybutylene (PB) plastic pipe and tubing --------------------- ASTM D 3309; CSA CAN3-B137.8
Polyethylene/aluminum/polyethylene (PE-AL-PE) composite pipe - ASTM F 1282
Polypropylene (PP) plastic pipe or tubing ----------------------- ASTM F 2389; CSA B137.11
Stainless steel (Type 304/304L) pipe -------------------------- ASTM A 312; ASTM A 778
Stainless steel (Type 316/316L) pipe -------------------------- ASTM A 312; ASTM A 778

Code is nice...but remember....it is the lowest possible standard. For instance, look at the temperature that the TPR valve releases at....then look at the 180 degree tolerance of the CPVC tube.

The author of this thread advises his clients to use copper. Personally, I consider that good advice. While the lowest possible standard might allow something else...he is probably setting his and his client's standards for safety a tad or so higher.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #7  
Old 1/21/09, 4:04 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Pressure relief valve extension

Quote:
Originally Posted by jbushart View Post
Code is nice...but remember....it is the lowest possible standard. For instance, look at the temperature that the TPR valve releases at....then look at the 180 degree tolerance of the CPVC tube.

The author of this thread advises his clients to use copper. Personally, I consider that good advice. While the lowest possible standard might allow something else...he is probably setting his and his client's standards for safety a tad or so higher.
James,

I would agree with you if the CPVC was under pressure but it is not in this case.

Copper if fine, CPVC is fine unless the manufacturer states otherwise.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 1/21/09, 6:40 PM
Patrick Coulter Patrick Coulter is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 186
Default Re: Pressure relief valve extension

Quote:
Originally Posted by dvalley View Post
What's up with the water heater roller coaster vent? I'd be writing up that vent installation.

All the Plumber had to do was install a WYE insert (at the main) and install the vent tubing into that.
I agree David and it's already written up. Thanks again!



Patrick Coulter
Cross County Inspection Services, LLC
(443) 266-7544
Reply With Quote
  #9  
Old 1/21/09, 6:42 PM
Patrick Coulter Patrick Coulter is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 186
Default Re: Pressure relief valve extension

Quote:
Originally Posted by dvalley View Post
When I find a PTR valve extension piped improperly, I simply note it and leave it at that.

504.6 Requirements for discharge piping

The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall:

1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room as the water heater.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area.
6. Discharge in a manner that does not cause personal injury or structural damage.
7. Discharge to a termination point that is readily observable by the building occupants.
8. Not be trapped.
9. Be installed so as to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.
11. Not have a threaded connection at the end of such piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section 605.4 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.
Thanks for taking the time to list the requirements. It's certainly a help and a good reminder!



Patrick Coulter
Cross County Inspection Services, LLC
(443) 266-7544
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tankless water heater and pressure relief valve Chris Tan Plumbing Inspections 13 6/27/08 1:13 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Hot Water Tank - missing Pressure relief valve? Jan Lombard Plumbing Inspections 31 4/12/07 3:32 PM
Tankless and TRP valve jtroth Plumbing Inspections 14 8/8/06 12:09 PM


All times are GMT -4. The time now is 2:42 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts