Attachment 46192
Is this propane gas tank suppose to be bonded ? There is a bond wire that is next to the tank but not connected to the tank. There are electrical outlets within six feet of the tank. PO BOX 61664 Fort Myers, FL. 33906 239-936-7579 E-Mail: swflhomeinspection@comcast.net HI-278~~~~~CB-C025051 Building Inspections since 1993
Last edited by fsylvester; 9/23/11 at 11:10 AM.. |
| Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
The tank does not require bonding, but the piping within the structure does.
However, the tank does require specific clearance from the structure. I don't know how big that tank is, but it's certainly close to the structure. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Thank you Jeff for your comments, appreciate your help. Happy Inspecting !
PO BOX 61664 Fort Myers, FL. 33906 239-936-7579 E-Mail: swflhomeinspection@comcast.net HI-278~~~~~CB-C025051 Building Inspections since 1993
|
|
#4
|
|||
|
|||
|
Please Note:
dmcmullen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Where would you find the required distance from the structure for the tank? I do not see that many up this way but there are a few, much larger than the one pictured though.
|
|
#5
|
|||
|
|||
|
http://www.idph.state.il.us/envhealt...stallhomes.pdf
Page 44 may be helpful or check with local propane company. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#6
|
||||
|
||||
|
For cylinders and smaller tanks (under 125 gal) there are no clearance requirements to the house, but there are clearances to windows/openings (generally 3' or 5') and ignition sources (generally 5' or 10'). The greater clearances are for tanks filled on-site. Also many consider receptacles a source of ignition.
Attached is an NFPA clearance diagram. You can also view the 2008 NFPA 58 (Referenced in the 2009 IRC) online by going here ... http://www.nfpa.org/aboutthecodes/Ab...&EditionID=226 . Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 7/10/11 at 3:50 PM.. |
|
#7
|
||||
|
||||
|
unknown disconnected bond would get written up
below is the graphic included in report when tanks are on site, so the new owner doesn't think of relocating for aesthetics or other reasons without knowing approved locations, we never know... ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Make $50.00 More Profit per Inspection with Septic Tanks | ebeahm1 | Ancillary Inspection Services & Additional Topics | 6 | 8/20/09 1:38 PM |
| Subject: Safety Flash: Propane Tank Danger | ksitzes | Miscellaneous Discussion for Inspectors | 1 | 6/2/08 12:04 PM |
| Septic System Care | mlarson | Ancillary Inspection Services & Additional Topics | 52 | 8/31/07 10:26 PM |