After having a discussion about this, grounding to the electrical system is rarely seen or practiced in our area. The gas meters are grounded and bonded to a grounding rod.
Since the system is connected to the meter, and the meter grounded, would this be a sufficent source of grounding? Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
The gas system must be bonded to the main panel ground bus or to the electrical system grounding electrode. It CANNOT be bonded to a separate electrode.
More info: http://www.nachi.org/forum/f2/good-c...tration-55769/
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#3
|
||||
|
||||
|
Water piping can be used as the GES, but gas piping cannot be used as the GES, nor can it be used as a primary path from the service equipment to the grounding-electrode.
Metallic piping (gas or water) is not "grounded" (even though it may appear to be so), it is "bonded" to the electrical system. The electrical system is "grounded." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Are you saying that a water pipe can be the only grounding electrode?
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#5
|
||||
|
||||
|
What would be the difference when bonding to a grounding electrode that services the panel or bonding to a competely seperate grounding rod next to the meter?
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#6
|
||||
|
||||
|
Please clarify. Normally, there is only one electrode (a driven rod) at the meter or main panel (which should be near the meter).
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#7
|
||||
|
||||
|
Often times it is, in existing construction. Codes are not retroactive so there's no requirement to add a supplemental electrode.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Bonding to a separate electrode does not bond the system to the electrical service.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
8ft rods are actually poor grounds but considered adequate for the intended purpose. True ground is achieved around a depth of 200ft as explained to me by a guy that used to work for a power company in a division related to high power distribution.
The goal of bonding the gas pipe is "equipotential" with the electrical ground and that can not be achieved with two different rods. Lightning induced arcing can jump from "ground to ground" since there are differences in potential. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#10
|
||||
|
||||
|
Quote:
E3608.1.1 Metal underground water pipe. A metal underground water pipe that is in direct contact with the earth for 10 feet (3048 mm) or more, including any well casing effectively bonded to the pipe and that is electrically continuous, or made electrically continuous by bonding around insulating joints or insulating pipe to the points of connection of the grounding electrode conductor and the bonding conductors, shall be considered as a grounding electrode (see Section E3608.1). Interior metal water piping located more than 5 feet (1524 mm) from the entrance to the building shall not be used as part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system. Commentary: Any metal water pipe in contact with the earth for 10 feet (3048 mm) or more is considered a grounding electrode. It is often thought that only the main water service piping fits this description, but any metal water pipe, such as an irrigation pipe or pipe from a water well, if buried in the earth for 10 feet (3048 mm) or more, must be bonded as part of the grounding electrode system. The pipe could be of any material such as copper or steel because the code does not mention the type of metal. In many houses, a water meter, water-pressure reducing valve, or similar equipment is installed in the water supply line. A bonding jumper of the same size as the grounding electrode conductor is installed around such devices because many of these devices are made of nonconductive materials. In many cases, when the device is removed and/or replaced, the grounding electrode is disconnected. A useful practice is to leave enough slack in the bonding jumper around the device that the jumper will not have to be taken off the piping in the event the device is replaced. The code assumes that the first 5 feet (1524 mm) of water piping, measured from the point that the piping penetrates an outside wall or floor slab on grade, will not be disturbed or altered by plumbing work. Any piping beyond 5 feet (1524 mm) into the building is more likely to be altered such that electrical continuity is lost. This alteration could take the form of the installation of plastic piping, nonconductive components (e.g. water filters), dielectric fittings or the removal of grounding clamps. A supplemental grounding electrode is always required when a water pipe electrode is used. The most commonly used supplemental grounding electrode is the ground rod. That is why in so many dwellings a grounding electrode conductor is run from the service equipment to the entry point of the water pipe and another grounding electrode conductor is run to a ground rod. The ground rod is quite often driven into the ground close to the service equipment. A grounding electrode conductor that connects the service equipment to a ground rod, pipe or plate electrode and connects to no other elec- trodes is not required to be larger than size 6 AWG copper or 4 AWG aluminum (see note to Table E3603.1 and Section E3610.2).
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
Quote:
My question is since both systems use the same type of grounding style would the gas meter grounding rod be as satisfactory as the one for the electrical service? If not then why? That seems to be the accepted practice in our area. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#12
|
||||
|
||||
|
When you said meter, I thought you meant the electric meter. My bad.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#13
|
||||
|
||||
|
Quote:
It's up to you to point out the "accepted practice" is incorrect by citing it as a defect and proving it with the code when challenged. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
I answered that in post #9 B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#15
|
||||
|
||||
|
Quote:
There is no need to "ground" the piping. Only the electrical system needs to be "grounded." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| CSST bonding | reckenroth | General Inspection Discussion | 6 | 8/13/10 8:36 PM |
| CSST bonding poll | jfunderburk | Electrical Inspections | 17 | 8/12/09 4:28 PM |
| Neutral bus bar failed inspection | Greg Moritz | Electrical Inspections | 18 | 1/19/08 1:53 PM |