Old 12/29/10, 7:44 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Proper CSST bonding

Here, I found the reason from gastite


Proper bonding and grounding will reduce the risk of damage and fire from a lightning strike. Lightning is a
highly destructive force. Even a nearby lightning strike that does not strike a structure directly can cause all
electrically conductive systems in the structure to become energized. If these systems are not adequately
bonded, the difference in electrical potential between the systems may cause the charge to arc from one
system to another. Arcing can cause damage to CSST. Direct bonding and grounding as set forth above will
reduce the risk of arcing and related damage over a non direct bonded system.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 12/29/10, 8:39 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Proper CSST bonding

BTW gastite has a product called flashshield. They say this tubing does not need to be bonded.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #18  
Old 12/29/10, 10:02 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Proper CSST bonding

Quote:
Originally Posted by jpope View Post
Water piping can be used as the GES, but gas piping cannot be used as the GES, nor can it be used as a primary path from the service equipment to the grounding-electrode.

Metallic piping (gas or water) is not "grounded" (even though it may appear to be so), it is "bonded" to the electrical system. The electrical system is "grounded."
Actually I do not think bonding to a water pipe would be a good idea unless you can confirm that the water pipe is all conductive leading to the electrical ground.
The communication industry stopped allowing conductors to be bonded to water pipes years ago.
Reply With Quote
  #19  
Old 12/29/10, 10:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Proper CSST bonding

It's a terrible idea, that's one of the reasons it is no longer used. Many systems lost their CES as soon as the home was re-piped. Not all plumbers know what that silly clamp is for...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #20  
Old 12/29/10, 10:52 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Proper CSST bonding

Good reminder to check for that water meter jumper wire.
Reply With Quote
  #21  
Old 12/29/10, 11:09 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Proper CSST bonding

Quote:
Originally Posted by sfogarty View Post
BTW gastite has a product called flashshield. They say this tubing does not need to be bonded.
Make sure you know the difference between "bonding" and "additional bonding" when talking about CSST.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #22  
Old 12/30/10, 12:15 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Proper CSST bonding

Quote:
Originally Posted by bking View Post
Make sure you know the difference between "bonding" and "additional bonding" when talking about CSST.
Correct as it simply conducts and dissipates 10 x better.
proper-corrugated-stainless-steel-tubing-bonding-csst-gastite-flashshield.jpg
Reply With Quote
  #23  
Old 12/30/10, 12:33 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Proper CSST bonding

Quote:
Originally Posted by belliott View Post
Correct as it simply conducts and dissipates 10 x better.
Attachment 40925
You are referencing the new design of that csst not bonding vs additional bonding right?

Many home inspectors report "gas pipe not bonded" when it actually is.
The pipe is electrically connected to the furnace cabinet via the furnace valve mounting and the branch circuit ground. This is a very poor high resistance bond to ground and has been improved by what is called "additional bonding".

The new pipe, usually black, may not need "additional bonding" according to the manuf or the code at this time but it is a good idea.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #24  
Old 12/30/10, 1:20 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Proper CSST bonding

Check out the video on their site Bruce.
But yes it all is bonded I hope.
This stuff just conducts better according to them.
Reply With Quote
  #25  
Old 12/30/10, 11:12 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Proper CSST bonding

Quote:
Originally Posted by bking View Post
The pipe is electrically connected to the furnace cabinet via the furnace valve mounting and the branch circuit ground.
Regardless of the material used (CSST, black-steel pipe) this is an inadequate bond, and does not satisfy the NEC bonding requirements.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #26  
Old 1/3/11, 1:54 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Proper CSST bonding

Quote:
Originally Posted by jpope View Post
You're missing the point Sean. The gas lines are not GROUNDED, they are BONDED (to the electrical service). Read Bruce's post.

There is no need to "ground" the piping. Only the electrical system needs to be "grounded."
Some gas co. in some areas do install a ground rod at the meter . That is gas co. decision for , they say safety reasons against outside static .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
CSST bonding reckenroth General Inspection Discussion 6 8/13/10 8:36 PM
CSST bonding poll jfunderburk Electrical Inspections 17 8/12/09 4:28 PM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM