Default PVC for cold water?

The other day I saw a first (for me). The home had been a rehab (sort of). The guy replaced all the plumbing. For the hot water he used CPVC which was fine. But for the cold he used PVC. I didn't make an issue out of it, but what is the official word on PVC being used for the cold water supply?

For what its worth, this is what I put in the report...

1.Observed the cold water pipes in the home are plumbed with PVC piping. In most cases, CPVC is used on all clean water pipes, and PVC is reserved for waste pipes. While this will likely not cause any serious concerns as this is only used on the cold water side, any future plumbing work should be done in consideration of this. It would be very easy for someone to accidentally connect a waste pipe to this supply piping in ignorance.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 6/26/09, 6:04 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: PVC for cold water?

I would say probably 90% of the homes here have PVC for their main supply line coming in off the meter / street. I see PVC for cold water supply a lot particularly in rehabs. It is cheap, easy to install and will last virtually forever as long as it isn't exposed to UV. Same for sprinklers and Pool equipment; pumps, filters, etc. ALL PVC.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #3  
Old 6/26/09, 6:25 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: PVC for cold water?

I found this...

Quote:

Because PVC piping system components can be manufactured in a variety of colors, identification of application is easy. A common color scheme (although not universal) is:
  • White for DWV and some low pressure applications.
  • White, blue, and dark gray for cold water piping.
  • Green for sewer service.
  • Dark gray for industrial pressure applications.
This color scheme has an exception in that much of the white PVC pipe is dual rated for DWV and pressure applications.

PVC piping systems should not be used to store and/or convey compressed air or other gases. PVC piping systems should not be tested with compressed air or other gases either. CODE STATUS
PVC piping is recognized as acceptable material for DWV, sewers, and potable water services and distribution in all model plumbing codes. These Codes normally identify acceptable products for specific uses based on the ASTM Standard designation.
Here...
http://www.ppfahome.org/pvc/index.html
Reply With Quote
  #4  
Old 6/26/09, 6:29 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: PVC for cold water?

Quote:
Originally Posted by rmaday View Post
Thanks Rick



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 6/26/09, 6:29 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: PVC for cold water?

Quote:
Originally Posted by dedwards View Post
I would say probably 90% of the homes here have PVC for their main supply line coming in off the meter / street. I see PVC for cold water supply a lot particularly in rehabs. It is cheap, easy to install and will last virtually forever as long as it isn't exposed to UV. Same for sprinklers and Pool equipment; pumps, filters, etc. ALL PVC.
Thanks Doug.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #6  
Old 6/26/09, 9:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: PVC for cold water?

PVC is not allowed for interior distribution.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 6/26/09, 9:03 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: PVC for cold water?

Quote:
Originally Posted by jpope View Post
PVC is not allowed for interior distribution.
Is there a reason for that?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 6/26/09, 9:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: PVC for cold water?

Other than the "codes don't allow it?" I'm not sure. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 6/26/09, 9:30 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: PVC for cold water?

2006 IRC P2904.5 says (like Jeff says, PVC not to be seen):
pvc-cold-water-2904.5.jpg pvc-cold-water-2904.5t.jpg
Reply With Quote
  #10  
Old 6/26/09, 9:33 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: PVC for cold water?

Quote:
Originally Posted by mboyett View Post
2006 IRC P2904.5 says (like Jeff says, PVC not to be seen):
Attachment 29610 Attachment 29611
Ok, "code" says it's not suitable. Anyone know what the problem is with it?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #11  
Old 6/26/09, 9:52 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: PVC for cold water?

This might help;

http://www.nsf.org/consumer/plumbing/index.asp

PVC, CPVC, PEX, and Other Plastic Plumbing Materials

Plastic plumbing has been used for potable and non-potable water applications since the 1950s. Initially, there were many concerns about these products potentially leaching harmful chemicals into the water. To ensure that the public's health was protected, independent standards were quickly developed which established strict guidelines for these products.

Today, plastic plumbing products designed for potable water applications are usually designated with either "NSF-PW" or "NSF-61" to indicate that the product complies with the health effects requirements of NSF/ANSI Standard 61 for materials designed for contact with potable water. \

This standard also establishes similar guidelines for other plumbing materials, including copper tubing.
If your pipe is not coded with one of these designations or if it is designated with an alternative code such "NSF-DWV," it is probably not meant for potable water applications and should not be used for such purposes.
Reply With Quote
  #12  
Old 6/27/09, 12:08 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: PVC for cold water?

OK per IL plumbing code...

http://www.ilga.gov/commission/jcar/...ZZ9996aaR.html

About 1/3 of the way down .
Reply With Quote
  #13  
Old 6/27/09, 1:20 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: PVC for cold water?

It's always advisable to check your local codes. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #14  
Old 6/27/09, 7:04 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,228
Default Re: PVC for cold water?

Someone should tell People here they are not allowed to use PVC here . It is every where
Reply With Quote
  #15  
Old 6/27/09, 3:18 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: PVC for cold water?

Copper supply is the norm here.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Refrigerator Water Dispenser Works Only Intermittently Matt Ablemarle Plumbing Inspections 3 2/28/12 3:27 PM
Hot water first then cold out of cold side of fixture jberthiaume Plumbing Inspections 19 3/12/08 1:32 AM
smelly well water afrost Ancillary Inspection Services & Additional Topics 26 11/21/07 7:30 PM
More water, different windows Brenda Exterior Inspections 12 9/22/06 2:55 AM


All times are GMT -4. The time now is 10:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts