Default Relief valve

Is this a relief valve on the cold water line? Can you install on cold water line? No other relief valve on heater casing. Any help would be appreciated. This was an "older" water heater.

Thanks in advance.
Attached Thumbnails
relief-valve-13171-rd.-126-paulding-076.jpg   relief-valve-13171-rd.-126-paulding-077.jpg  
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/14/10, 3:08 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Relief valve

Quote:
Originally Posted by jfrederick View Post
Is this a relief valve on the cold water line? Can you install on cold water line? No other relief valve on heater casing. Any help would be appreciated. This was an "older" water heater.

Thanks in advance.
Yes and it is OK on the cold line as the pressure is the same.

However it is not a temperature sensing device so a TPR is still required.

http://media.wattswater.com/1910868.pdf



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 5/14/10, 3:17 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Relief valve

Exactly what I was looking for, you da man. Thank you. Have a great weekend!

BTW, this is the oldest one I've seen still in operation
Attached Thumbnails
relief-valve-13171-rd.-126-paulding-080.jpg  
Reply With Quote
  #4  
Old 5/14/10, 4:06 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,569
Default Re: Relief valve

i see the warranty has expired...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 5/17/10, 3:58 PM
rmchenry rmchenry is offline
InterNACHI Member
 
Join Date: May 2010
Posts: 2
Default Re: Relief valve

no you dont put a relief valve on the cold water side it goes on the hot side because of the heated pressure
Reply With Quote
  #6  
Old 5/17/10, 4:07 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Relief valve

Quote:
Originally Posted by rmchenry View Post
no you dont put a relief valve on the cold water side it goes on the hot side because of the heated pressure
The pressure is the same on both sides.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #7  
Old 5/17/10, 5:43 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Relief valve

Quote:
Originally Posted by mlarson View Post
The pressure is the same on both sides.
Riddle me this then.
Why are expansion tanks only installed on the cold side ?

No because it is code or manufacturer instructions as an answer ,please.
Reply With Quote
  #8  
Old 5/17/10, 7:05 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Relief valve

Quote:
Originally Posted by rmchenry View Post
no you dont put a relief valve on the cold water side it goes on the hot side because of the heated pressure

If you have a watt-210 valve the pressure relif valve goes on the COLD side on the exterior hose bib. Pressure is pressure equal on both hot and cold.

When water is heated it expands. On a 'closed' system the expansion tank, on the cold side, absorbs that extra expansion . If you did not have an expansion tank the pressure relief valve would open

Chuck
Reply With Quote
  #9  
Old 5/17/10, 7:35 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Relief valve

Quote:
Originally Posted by belliott View Post
Riddle me this then.
Why are expansion tanks only installed on the cold side ?

No because it is code or manufacturer instructions as an answer ,please.
The bladder will last longer on the cold side.

Installation
1. Install the THERM-X-TROL® on the city supply line to the water heater at a point
between the water heater and backflow preventer, check valve or pressure
reducing valve (see Figure 1).
Attached Thumbnails
relief-valve-ext.jpg  



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #10  
Old 5/17/10, 8:02 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Relief valve

Yeah ,that was all I could find on it..
Reply With Quote
  #11  
Old 5/18/10, 12:13 AM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Relief valve

Quote:
Originally Posted by belliott View Post
Riddle me this then.
Why are expansion tanks only installed on the cold side ?

No because it is code or manufacturer instructions as an answer ,please.

When water is heated it expands. On a 'closed' system the expansion tank, on the cold side, absorbs that extra expansion . If you did not have an expansion tank the pressure relief valve would open.

The expansion goes to the cold side.

Chuck
Reply With Quote
  #12  
Old 5/18/10, 1:19 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Relief valve

relief-valve-plumbing-hot-water-heater-expansion-tank.jpg

Chuck, by looking at the picture above you will see that water is represented by the red color.
As far as I know the tank itself does not have a check valve though you see one on the cold water side of the piping in this illustration.

In Chicago expansion tanks are required if there is a check valve by the way.

Please explain using this illustration as a guide or reference how only the cold side would expand.

Interesting that it is the hot water doing the expanding.
Another interesting fact is that cold water when cold enough turns to ice on the opposite end of the spectrum and also expands.
Yet an expansion tank would do no good in that case.
Reply With Quote
  #13  
Old 5/18/10, 1:44 AM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Relief valve

Bob,

The expansion tank is just that an expansion tank it has a bladder in it, water pressure on one side and air pressure on the other, has the air valve on it to set pressure. When the water heats it expands and we all know you cannot compress a liquid (water). On the hot side (closed system) of the system there is nowhere for the expansion to go. If there is a check valve on the cold side, again (closed system) again there is no where for the expansion to go. This would cause the Pressure relief valve to open with no expansion tank installed. With an expansion tank installed the expansion goes back through the cold side and puts pressure on the bladder, thus expanding into the tank. If the expansion tank was installed on the hot side the same results would occur as the expansion could not go through the cold side due to the check valve.

As for the freezing and the expansion. Freezing on a system with a check valve would most likely occur on the supply side, not water heater/expansion tank side of the check valve thus causing damage to the water lines and components.

Chuck
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/18/10, 7:16 PM
rmchenry rmchenry is offline
InterNACHI Member
 
Join Date: May 2010
Posts: 2
Default Re: Relief valve

what i was trying to say is that the pressure relief valve should be installed on the tank TPR valve means temperature pressure relief valve the hotter the water gets the more pressure the tank builds up inside and if there is no relief valve the tank could explode thats what i meant
Reply With Quote
  #15  
Old 5/18/10, 8:41 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Relief valve

Quote:
Originally Posted by Chuck Lambert View Post
Bob,

The expansion tank is just that an expansion tank it has a bladder in it, water pressure on one side and air pressure on the other, has the air valve on it to set pressure. When the water heats it expands and we all know you cannot compress a liquid (water). On the hot side (closed system) of the system there is nowhere for the expansion to go. If there is a check valve on the cold side, again (closed system) again there is no where for the expansion to go. This would cause the Pressure relief valve to open with no expansion tank installed. With an expansion tank installed the expansion goes back through the cold side and puts pressure on the bladder, thus expanding into the tank. If the expansion tank was installed on the hot side the same results would occur as the expansion could not go through the cold side due to the check valve.

As for the freezing and the expansion. Freezing on a system with a check valve would most likely occur on the supply side, not water heater/expansion tank side of the check valve thus causing damage to the water lines and components.

Chuck
OK ,better explanation as you are correct in that it expands toward the cold side when there is no check valve.

(Reason I assume is ,that a typical city water pressure is weaker than the piping or tank construction)(of course a TPR is set in between the two).

Of course with a check valve the pressure would all be equal and have no where to go but out the TPR or if that malfunctioned would choose the weakest point.

Last edited by belliott; 5/18/10 at 8:44 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater relief valve question acassady Plumbing Inspections 14 9/18/09 9:21 AM
Tankless water heater and pressure relief valve Chris Tan Plumbing Inspections 13 6/27/08 1:13 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Hot Water Tank - missing Pressure relief valve? Jan Lombard Plumbing Inspections 31 4/12/07 3:32 PM


All times are GMT -4. The time now is 2:45 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts