Default S-Trap?

Would this be considered an S-Trap? The vertical pipe to the right is the washer's drain and the one on the left goes up a few feet and terminates with an air admittance valve. The whole thing is in the garage (and that wall separates the garage from the house, so not the best fire rated wall)

s-trap-dsc03692b.jpg s-trap-dsc03690b.jpg



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections
www.redfishinspections.com
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/23/11, 10:18 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,569
Default Re: S-Trap?

not really an S just a poor choice of fittings imo



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 11/23/11, 11:22 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: S-Trap?

Yeah pass it over unless you need more comment in the report.
Reply With Quote
  #4  
Old 11/23/11, 11:37 PM
William T. Misegades William T. Misegades is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 734
Default Re: S-Trap?

Thanks guys! Yeah, I decided to pass it over. That drain pipe isn't connected to the rest of the house except at the very end before the main line, so I won't worry about it.



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections
www.redfishinspections.com
Reply With Quote
  #5  
Old 11/24/11, 1:26 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: S-Trap?

Quote:
Originally Posted by wmisegades View Post
Thanks guys! Yeah, I decided to pass it over. That drain pipe isn't connected to the rest of the house except at the very end before the main line, so I won't worry about it.
Back in now.
Defiantly call out the lack of a firewall.

Standing trap water in a frozen garage eh? Just looked and see you are in Texas.Never mind the last comment.

(edit here) I just looked up info on traps and perhaps the trap violates what I have below from an older powerpoint.


The vertical between the fixture outlet and the trap weir shall be as short as practical, but in no case shall the tail piece, from any fixture, exceed 24 inches in length

Perhaps someone can explain the reason behind that rule.

Last edited by belliott; 11/24/11 at 1:42 AM..
Reply With Quote
  #6  
Old 11/24/11, 7:43 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: S-Trap?

A few comments I found Bob on your question;

I think (and I may be wrong) that the reason it limits it to 24" is becasuse if it gets longer, the water from the fixture will have extra momentum on the vertical drop which transfers directly to the trap-seal water. This of course can cause the water in the trap to be "pushed out" or drain (partially) thereby eliminating or reducing the water seal (although some water will probably still remain in the trap).

But the 24" maximum is to reduce odor and the growth of bacteria upstream of the trap. Buildup on the wall of the fixture outlet pipe will breed bacteria and cause odors to develop.

I understand the purpose of the maximum length such that a plugged trap would only hold a static head of only so much.

Take your pick.
Reply With Quote
  #7  
Old 11/24/11, 9:36 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: S-Trap?

Quote:
Originally Posted by belliott View Post

The vertical between the fixture outlet and the trap weir shall be as short as practical, but in no case shall the tail piece, from any fixture, exceed 24 inches in length
Bob - That's for a trap on a fixture. The tailpiece here is a standpipe for a washer drain. That's usually 18" - 30".



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #8  
Old 11/24/11, 9:56 AM
William T. Misegades William T. Misegades is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 734
Default Re: S-Trap?

Quote:
Originally Posted by belliott View Post
Back in now.
Defiantly call out the lack of a firewall.
Sure did thanks! There were many other fire hazards like knob and tube degraded wires in the attic insulation. I also called out as a safety and fire hardware the fact that the dryer was right under the main panel which had openings in it. The entire area around the panel was covered with lent. It was a more interesting house to inspect



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections
www.redfishinspections.com
Reply With Quote
  #9  
Old 11/24/11, 10:08 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: S-Trap?

1002.3 Prohibited traps. The following types of traps are prohibited:

1. Traps that depend on moving parts to maintain the seal.
2. Bell traps.
3. Crown-vented traps.
4. Traps not integral with a fixture and that depend on interior partitions for the seal, except those traps constructed of an approved material that is resistant to corrosion and degradation.
5. "S" traps.
6. Drum traps.

Exception: Drum traps used as solids interceptors and drum traps serving chemical waste systems shall not be prohibited.

That fitting is a Y and it should be a T....I would call that an "S" trap in my humble opinion.



Paul W. Abernathy
Reply With Quote
  #10  
Old 11/24/11, 10:24 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: S-Trap?

A S-trap has the ability to siphon the trap. The trap in the pic does not as it will maintain a seal that is the only concern



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 11/24/11, 11:13 AM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 196
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: S-Trap?

Quote:
Originally Posted by pabernathy View Post
1002.3 Prohibited traps. The following types of traps are prohibited:

1. Traps that depend on moving parts to maintain the seal.
2. Bell traps.
3. Crown-vented traps.
4. Traps not integral with a fixture and that depend on interior partitions for the seal, except those traps constructed of an approved material that is resistant to corrosion and degradation.
5. "S" traps.
6. Drum traps.

Exception: Drum traps used as solids interceptors and drum traps serving chemical waste systems shall not be prohibited.

That fitting is a Y and it should be a T....I would call that an "S" trap in my humble opinion.
The fitting I believe you are refering to is called a "sanitary tee" and is the proper fitting for that application. I have seen it called a "TY" though.
Reply With Quote
  #12  
Old 11/24/11, 2:47 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: S-Trap?

Quote:
Originally Posted by bsmith View Post
Bob - That's for a trap on a fixture. The tailpiece here is a standpipe for a washer drain. That's usually 18" - 30".
OK.
Would you call out a trap in an unheated garage in NY?
Reply With Quote
  #13  
Old 11/24/11, 11:38 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: S-Trap?

Probably not. My garage is unheated and never gets below freezing, but I guess it would depend on the conditions at the inspection.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/25/11, 6:33 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: S-Trap?

What ever you call it....Im an Electrician Dude...lol

The fitting where it connects to the vent should not change the direction down again. This is no different in that the gas from the sewer line could come up without the seal present in the trap. Since the connector slops down and not straight in like it would with a T fitting ( short for Sanitary Tee ) I would call this an S trap configuration and so would my municipal inspector....agree or not they would have to change that connector fitting in my opinion.



Paul W. Abernathy
Reply With Quote
  #15  
Old 11/25/11, 6:54 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: S-Trap?

Quote:
Originally Posted by belliott View Post
OK.
Would you call out a trap in an unheated garage in NY?
I wood call it frozen lolol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Condensation Drain line question acassady Inspecting HVAC Systems 25 2/26/12 11:40 AM
Trap weird and crown weir dpant Plumbing Inspections 22 1/24/11 11:41 PM
Negative angle trap arm issue rlind Plumbing Inspections 4 4/14/06 11:00 PM
Grease Trap / Drum Trap David White Plumbing Inspections 1 2/7/06 5:41 PM


All times are GMT -4. The time now is 2:46 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts