I agree with Charles that the trap arm length looks a little too short ... must be at least 2 x Pipe Dia from the trap wier (bottom of elbow going back) to the vent/stack (even if the vent is an AAV).
JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 2/27/06 at 12:32 AM.. |
|
#17
|
||||
|
||||
|
Please Note:
rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
On the trap arm length...
UPC says minimum 2 x diameter, IRC says minimumc 8"...but that is in a section referring to traps with a vertical leg, (P3105.3) and I'm not sure if it really applies to all trap arms. Joe...the AAV prevents siphoning the same as if that upper vertical section extended all the way through the roof. It just doesn't vent the gases back into the cabinet. To my eye it looks like we have that 2 times...albeit barely. I'd say that according to the UPC there is nothing wrong with the set-up. The IRC may require a longer trap arm, but I wouldn't get very excited about it. Last edited by rmoore; 2/27/06 at 4:16 PM.. |
|
#18
|
||||
|
||||
|
Please Note:
rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Going back to the trap arm length as per the IRC...
I'm going by the 2000 version (yes, I know I need to update), but the only place I find the trap arm length mentioned is in the P3105.3 Vertical leg for waste fixture drains section. That's where it says 8". I can't believe you are supposed to read that section to determine trap arm length for normally trapped fixtures. Am I missing something? |
|
#19
|
|||
|
|||
|
Please Note:
John Clayton is a non-member guest and is in no way affiliated with InterNACHI or its members.
Read the next section Richard, It is covered in 3105.4.
When a trap is located within two pipe diameters of the vent it is considered to be crown vented, which is prohibited. |
|
#20
|
||||
|
||||
|
Please Note:
rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks John...right under my nose. Presbyopia can be a *****.
|
|
#21
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#22
|
||||
|
||||
|
Please Note:
rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Stay away from sneezing chickens and you should be OK Jay.
|
|
#23
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Trap | dmacy | Plumbing Inspections | 7 | 11/21/06 8:00 PM |
| Potable Water Line to Trap | jcooper2 | Plumbing Inspections | 9 | 11/1/06 1:17 AM |
| Negative angle trap arm issue | rlind | Plumbing Inspections | 4 | 4/15/06 12:00 AM |
| Grease Trap / Drum Trap | David White | Plumbing Inspections | 1 | 2/7/06 6:41 PM |