  #1  
Old 12/9/07, 1:39 PM
sbenson sbenson is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Suffolk, Va
Posts: 31
Default Saddle Valves

Noted a saddle valve installed in a hot water heater copper flex connector at the shank portion of the flex connector where it transitions to the PEX hot water distribution system. Valve was corroded and leaking causing damage to hot water heater . Valve feeds a hole house humidifier system. Granted valve is bad, HVAC company who installed it says it needs replaced, Question is it permissible install a saddle valve in a copper flex line in the first place. Cannot find and reference data on it.
Attached Thumbnails
saddle-valves-valve.jpg  
Reply With Quote
  #2  
Old 12/9/07, 2:01 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Saddle Valves

I suspect it's one of these things the valve manufacturer does not bother to prohibit because "No one would be stupid enough to do it".
Reply With Quote
  #3  
Old 12/9/07, 3:39 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Saddle Valves

Even the handyman says not to install on the hot water line, even less one that is corrugated.

http://www.naturalhandyman.com/iip/infxtra/infsad.html

Marcel
Reply With Quote
  #4  
Old 12/9/07, 5:12 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Saddle Valves

Quote:
Originally Posted by mcyr
Even the handyman says not to install on the hot water line, even less one that is corrugated.

http://www.naturalhandyman.com/iip/infxtra/infsad.html

Marcel
Also in the common sense code book first sentence of first paragraph
</IMG></IMG></IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 12/9/07, 5:18 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Saddle Valves

Quote:
Originally Posted by cbottger
Also in the common sense code book first sentence of first paragraph
</IMG></IMG></IMG>
Hi. Charley;

Is there any of that left in today's residential Builders. ??? or most likely this was a DIY entrepreneur.

Marcel
</IMG></IMG></IMG></IMG>
Reply With Quote
  #6  
Old 12/9/07, 6:10 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Saddle Valves

Saddle valves are not allowed in Illinois.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #7  
Old 12/11/07, 9:25 AM
sbenson sbenson is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Suffolk, Va
Posts: 31
Default Re: Saddle Valves

Thanks all. "Common sense" was same term I used with home owner.
Reply With Quote
  #8  
Old 12/11/07, 10:41 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Saddle Valves

Some of the humidifiers from the "Big Orange" used to come with saddle valves in the box!

They are not allowed here.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #9  
Old 12/11/07, 10:45 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Saddle Valves

Saddle valves are common here in Wisconsin.

They are used for:

icemakers
whole house humidifiers
Reverse Osmosis drinking water units

Last edited by mlarson; 12/11/07 at 10:49 AM..
Reply With Quote
  #10  
Old 12/11/07, 1:13 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Saddle Valves

saddle valves may not be allowed in Illinois but are incorperated all the time.
The bad thing about most saddle valves is that I can guarantee they will eventualy leak.
When used with copper they have a tendency to crush the copper pipe they are being used on.
When working with Sears we were instructed to use them.
Another problem they have is a tendency for the cutting tube to break off before it digs a good hole which also can cause leaks.
There is another type which is made for galvanised pipe which was better in that we would actualy drill a hole in the side of the pipe and screw it in.
In general however , the other problem with this item is the rubber gasket which does eventualt deteriorate.
These are my personal opinions , but I find them to be accurate from a practical standpoint which is what really matters.
P.S yes I know the galvinized will clog up, but can be repoked.
Reply With Quote
  #11  
Old 12/11/07, 2:16 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Talking Re: Saddle Valves

Quote:
Originally Posted by relliott
saddle valves may not be allowed in Illinois but are incorperated all the time.
The bad thing about most saddle valves is that I can guarantee they will eventualy leak.
When used with copper they have a tendency to crush the copper pipe they are being used on.
When working with Sears we were instructed to use them.
Another problem they have is a tendency for the cutting tube to break off before it digs a good hole which also can cause leaks.
There is another type which is made for galvanised pipe which was better in that we would actualy drill a hole in the side of the pipe and screw it in.
In general however , the other problem with this item is the rubber gasket which does eventualt deteriorate.
These are my personal opinions , but I find them to be accurate from a practical standpoint which is what really matters.
P.S yes I know the galvinized will clog up, but can be repoked.

He said Repoked...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #12  
Old 12/11/07, 9:01 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Saddle Valves

Soon as I typed it I thought thought , hmmm, naw it's just my dirty mind.
Reply With Quote
  #13  
Old 12/11/07, 9:18 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Saddle Valves

The point is, Rob, they are not allowed, per the state plumbing code (which, in this instance, is the same as the Chicago code. NOTE: In Illinois, there are only two plumbing codes. Chicago (and some surrounding suburbs) and the State code)).

In any case, they are wrong and should be called out.

If Sears tells their installers to use them, then Sears (as a corporate entity, open to suit) is in violation of the law.


Anyone want to join me in sueing Sears!



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #14  
Old 12/11/07, 9:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Saddle Valves

CA Rules. . .

Saddle fittings are not allowed for use in DWV systems. They can be used on PVC piping, but only in exterior locations. In other piping systems, they can be used according to their listing when that listing does not conflict CPC requirements.

I'll bet you a dollar that the listing doesn't allow the fitting to be used on flex pipe.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 12/11/07, 9:52 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Saddle Valves

New to me:

77 ILLINOIS ADMINISTRATIVE CODE, PART 890, (NEW) ILLINOIS PLUMBING CODE (02/04)

SUBPART I: WATER SUPPLY AND DISTRIBUTION

Section 890.1130 Protection of Potable Water… 5. No pipe or fitting of the water supply system shall be drilled or tapped nor shall any band or saddle be used except at the water main in the street. Exception: See Section 890.320(h) for potable water use only.

http://www.firesprinklerassoc.org/Ba...ive%20code.pdf

Section 890.320(h) Brazed Joints. Brazed joints shall be made by first cleaning the surface to be joined down to the base metal, applying flux approved for such joints and for the filler metal to be used, and making the joints by heating to a temperature sufficient to melt the approved brazing filler metal on contact. (See Section 890.330(b).) An extracted mechanical joint may be made in copper tube types K or L only for water distribution. The joint shall be made with a mechanical extraction tool and joined by brazing. To prevent the branch tube from being inserted beyond the depth of the extracted joint, depth stops shall be provided. This joint shall be for above ground use only.

http://www.ilga.gov/commission/jcar/admincode/077/077008900C03200R.html



But... does that apply in "Home Rule" municipalities?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need Title 24 (CA) reference for TPR valves jhugenroth Plumbing Inspections 12 8/31/09 2:12 PM
Does anyone know anything about corrugated stainless steel tubing (CSST)? gromicko Structural Inspections 5 9/28/07 6:24 PM
Bathroom Shut-off Valves - Mineral deposits - Do you note them as leaking in reports? jwatts1 Plumbing Inspections 8 7/29/06 11:50 AM
Shutoff Valves?? tpriddy Plumbing Inspections 9 2/23/06 4:57 PM


All times are GMT -4. The time now is 2:47 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts