Default Sediment trap location w/ gas flex line

Here is a pic w/ my comment at a recent new home move in inspection where I called out that the sediment trap / drip leg should be before flex line (low side), of water heater.
Thoughts on this, please.
I had a debate w/ builders superintendent, who insisted that it should be right by unit, which as seen is in pic is on the high side of flex- not making sense to me since sediment, condensation, etc would settle better on low side of flex.
Attached Thumbnails
sediment-trap-location-w-gas-flex-line-tjones-113.jpg  



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/1/11, 8:44 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Sediment trap location w/ gas flex line

What is pictured is correct.

The sediment trap
should be as close as possible to the appliance.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #3  
Old 7/1/11, 8:57 PM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 356
Default Re: Sediment trap location w/ gas flex line

Thanx Joe, here are a couple of images showing it should be the other way.
Attached Thumbnails
sediment-trap-location-w-gas-flex-line-wh-drip-leg.jpg   sediment-trap-location-w-gas-flex-line-wh-gas-line-drip-leg.jpg  



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com
Reply With Quote
  #4  
Old 7/2/11, 1:00 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Sediment trap location w/ gas flex line

Joe, I agree with Joe!

Pic in 1st post is correct.

2nd Pic... there is a difference in the setup, thus the difference in the sediment trap location.

Pic 3 looks like it may have 2 traps, but you blocked a portion of the 2nd one with your text box.
Reply With Quote
  #5  
Old 7/2/11, 3:58 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Sediment trap location w/ gas flex line

Quote:
Originally Posted by jkeresztury View Post
Thanx Joe, here are a couple of images showing it should be the other way.
Here's how Bradford White says to do it. If in doubt (and you think it really matters which side of the appliance connector it's on) research the specific water heater you are working with or check with your AHJ for local requirements.

Quote:
Connect this water heater only to the type of gas (Natural or Propane gas) as shown on the rating plate. Use clean black iron pipe or equivalent material approved by local codes and ordinances. (Dirt and scale from the pipe can enter the gas valve and cause it to malfunction). The inlet gas line must have a minimum length of three (3) inches (7.6 cm) drip leg (sediment trap) installed as close to the water heater’s gas valve as possible. A ground joint union must be installed as close to the water heater as possible in the gas supply line feeding the water heater to permit servicing of the water heater. Compounds used on the threaded joints of the gas piping must be resistant to the action of liquefied petroleum gases/propane gas. DO NOT apply pipe dope to the gas valve inlet and make certain that no pipe dope has become lodged in the inlet screen of the gas valve. Extreme care must be taken to ensure no pipe dope enters the gas valve. Avoid excessive torque
when tightening the gas supply line to the gas valve. Excessive torque may result in cracking of the gas valve housing and could create a gas leak. The suggested maximum torque is 31.5 ft. lbs. (4.4 kg-m).



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #6  
Old 7/2/11, 11:10 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Sediment trap location w/ gas flex line

Sediment traps and drip legs are actually two different things.

Sediment traps (also called dirt legs) are primarily to catch debris that may be inside the piping, and needs to be installed as close as practical to the equipment after the supply shut off valve (IRC G2419.4 Sediment Trap). All the pictures appear to show the required sediment traps.

Drip legs are installed to catch moisture that may be in the gas if the local authority consideres the gas to be "wet", and must be installed at the lowest point in the gas piping where condensate could collect (IRC G2419.2 Drips).


Many times the sediment trap and drip leg are the same thing (and the terms interchangeable) because it is both the lowest point in the piping and just before the equipment ... as in this picture ...





In the following picture it appears that both a drip leg (on the left just as the pipe comes thru the wall) and a sediment trap (right at the equipment) are installed.





Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 7/4/11 at 9:36 AM..
Reply With Quote
  #7  
Old 7/12/11, 11:24 PM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 356
Default Re: Sediment trap location w/ gas flex line

Here is an email image sent to me by a member, showing the drip leg/sediment trap before flex line as required by IRC. Everyone here agrees the drip leg/sediment trap should be as close to the WH gas valve as possible, which is true. But taking in consideration of the loop of the gas flex line, my opinion is that it should be before the flex line, changing the requirements and opinions of the drip leg/ sediment trap on a stiff (non flex) gas line that should be right before the gas valve of the Water Heater. Does this make sense?
Attached Thumbnails
sediment-trap-location-w-gas-flex-line-sediment-trap.gif  



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com

Last edited by jkeresztury; 7/12/11 at 11:41 PM..
Reply With Quote
  #8  
Old 7/13/11, 11:42 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Sediment trap location w/ gas flex line

Quote:
Originally Posted by jkeresztury View Post
But taking in consideration of the loop of the gas flex line, my opinion is that it should be before the flex line ...
Sediment build-up from the flexible connector between the hard pipe and the gas valve isn't a significant concern, so what is shown in the diagram is adequate.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #9  
Old 7/13/11, 12:08 PM
David Hays David Hays is online now
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Sediment trap location w/ gas flex line

Here is one that is incorrect.

sediment-trap-location-w-gas-flex-line-p7095364.jpg



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #10  
Old 7/13/11, 12:34 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Sediment trap location w/ gas flex line

Quote:
Originally Posted by dhays View Post
Here is one that is incorrect.

Attachment 46401
Hate to be standing next to that TPRV when she blows!
Reply With Quote
  #11  
Old 7/13/11, 2:50 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sediment trap location w/ gas flex line

Another illustration

sediment-trap-location-w-gas-flex-line-1572.jpg
Reply With Quote
  #12  
Old 7/13/11, 3:17 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Sediment trap location w/ gas flex line

This Joe agrees with Joe also.

Either way is fine. Pick another battle. The direction of the leg (will sediment blow into it or blow past it) and the fact that it is after the shut-off valve are of primary importance. Whether it's before or after the connector is of little consequence.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas flex line in crawl space Richard Seay Plumbing Inspections 19 8/12/08 8:12 PM
Dishwasher line to trap hspinnler Plumbing Inspections 6 9/19/06 10:37 PM
A/C location of expansion device vs line temps. bking Inspecting HVAC Systems 9 5/29/06 4:16 PM
Exposed Flex Gas Line jfunderburk Plumbing Inspections 20 5/11/06 1:44 AM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 2:47 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts