  #1  
Old 8/31/06, 6:26 PM
mmorgan mmorgan is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Brownwood, TX
Posts: 196
Default Septic tank inside home

I've never seen this before. It doesn't seem right, but I cannot find anything that specifically disallows a septic tank in the home.

The house had been added onto and, therefore, the septic tank ended up in the added-on room. In the room, there is a cleanout sticking out of the slab about 6 to 8 inches. Just under the cap, there is a 2-inch vent pipe that comes out horizontally then turns up, goes up along the wall and out through the roof.

Can anyone tell me if there is anything in the code that specifically disallows this?

(My picture of this did not work out for some reason.)
Reply With Quote
  #2  
Old 8/31/06, 7:00 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,613
Default Re: Septic tank inside home

Quote:
Originally Posted by mmorgan
I've never seen this before. It doesn't seem right, but I cannot find anything that specifically disallows a septic tank in the home.

The house had been added onto and, therefore, the septic tank ended up in the added-on room. In the room, there is a cleanout sticking out of the slab about 6 to 8 inches. Just under the cap, there is a 2-inch vent pipe that comes out horizontally then turns up, goes up along the wall and out through the roof.

Can anyone tell me if there is anything in the code that specifically disallows this?

(My picture of this did not work out for some reason.)
Not allowed any where I know of ,can you more then likely no permit for this addition . Methane Gas is not healthy
Roy Cooke
Reply With Quote
  #3  
Old 8/31/06, 8:15 PM
wforsyth's Avatar
wforsyth wforsyth is offline
Active Poster
 
Join Date: Feb 2006
Location: Brinnon, Wa
Posts: 7,860
Please Note: wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Septic tank inside home

vents out through the roof. I think I remember having a house as a kid like this. But I wouldn't want one.
Reply With Quote
  #4  
Old 8/31/06, 8:18 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,613
Default Re: Septic tank inside home

Quote:
Originally Posted by wforsyth
vents out through the roof. I think I remember having a house as a kid like this. But I wouldn't want one.
Yes and bring the hose into the living room to pump out the tank sure will never happen in my home . Roy Cooke
Reply With Quote
  #5  
Old 8/31/06, 8:24 PM
wforsyth's Avatar
wforsyth wforsyth is offline
Active Poster
 
Join Date: Feb 2006
Location: Brinnon, Wa
Posts: 7,860
Please Note: wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Septic tank inside home

Very disgusting. I think it was a multi level house and we also had a "garden" level that had a root cellar. It was back in Virginia.
Reply With Quote
  #6  
Old 8/31/06, 9:52 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Septic tank inside home

Hi to all,

I have to agree with Roy, there is no way that is allowed anywhere in the developed world.

Off the to of my head I believe the absolute minimum clearance between the structure and the tank is 5 feet, but most jurisdictions require 10 feet. (I know Massachusetts Title 5 calls for a minimum of 8ft.)

That home has to have been added to without the benefit of permiting or inspection.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 8/31/06, 10:17 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Septic tank inside home

Quote:
Originally Posted by mmorgan
I've never seen this before. It doesn't seem right, but I cannot find anything that specifically disallows a septic tank in the home.
I would note it in the report and suggest that they replace it with a litter box.
Reply With Quote
  #8  
Old 8/31/06, 10:19 PM
dbush's Avatar
dbush dbush is offline
Active Poster
 
Join Date: Dec 2002
Location: Joplin, MO
Posts: 243
Send a message via MSN to dbush Send a message via Yahoo to dbush
Please Note: dbush is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Septic tank inside home

Missouri you must have a minimum of 5' from the house to the tank. Question is, how are they going to remove it?
Reply With Quote
  #9  
Old 8/31/06, 10:27 PM
Emmanuel J. Scanlan Emmanuel J. Scanlan is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 1,036
Default Re: Septic tank inside home

Mike,

On Site Sewage Facilities are controlled by the Texas Commission On Environmental Quality. The required separation distance from a structure is 5'. Also don't forget the 10' separation to water lines.

http://info.sos.state.tx.us/pls/pub/...1&ch=285&rl=31

T
exas Administrative Code
TITLE 30 ENVIRONMENTAL QUALITY
PART 1 TEXAS COMMISSION ON ENVIRONMENTAL QUALITY
CHAPTER 285 ON-SITE SEWAGE FACILITIES
SUBCHAPTER D PLANNING, CONSTRUCTION, AND INSTALLATION STANDARDS FOR OSSFS

RULE §285.31 Selection Criteria for Treatment and Disposal Systems
(d) Separation requirements. OSSFs shall be separated from features, in the area where the OSSF is to be installed, that could be contaminated by the OSSF or could prevent the proper operation of the system. The separation requirements are in §285.91(10) of this title.

REQUIRED SEPARATIONS

http://info.sos.state.tx.us/pls/pub/...1&ch=285&rl=91

(10) Table X. Minimum Required Separation Distances for On-Site Sewage Facilities.

http://info.sos.state.tx.us/fids/30_0285_0091-23.html



Knowledge is power, but sharing knowledge brings peace!

http://www.psinspection.com

TREC License# 7593

Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!

Last edited by escanlan; 8/31/06 at 11:54 PM..
Reply With Quote
  #10  
Old 8/31/06, 11:19 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,892
Default Re: Septic tank inside home

You're also supposed to have clear access to leeching fields, drain tiles, tank, etc. I can't put drive, patio, etc over one - do you think a house gets special consideration for being over the tank.
Reply With Quote
  #11  
Old 9/1/06, 12:11 AM
wforsyth's Avatar
wforsyth wforsyth is offline
Active Poster
 
Join Date: Feb 2006
Location: Brinnon, Wa
Posts: 7,860
Please Note: wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Septic tank inside home

Quote:
Originally Posted by gbeaumont
Hi to all,

I have to agree with Roy, there is no way that is allowed anywhere in the developed world.

Off the to of my head I believe the absolute minimum clearance between the structure and the tank is 5 feet, but most jurisdictions require 10 feet. (I know Massachusetts Title 5 calls for a minimum of 8ft.)

That home has to have been added to without the benefit of permiting or inspection.

Regards

Gerry
Two words.

Galax Virginia
Reply With Quote
  #12  
Old 9/1/06, 9:09 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Septic tank inside home

Quote:
Originally Posted by wforsyth
Two words.

Galax Virginia
Wendy, I did say the developed world

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #13  
Old 9/1/06, 5:50 PM
dhelm's Avatar
dhelm dhelm is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Bellingham, Wa
Posts: 704
Smile Re: Septic tank inside home

Quote:
Originally Posted by gbeaumont
Wendy, I did say the developed world

Regards

Gerry
Yeah, but if you're into Bluegrass music, Galax is the center of the universe!



Helm Home Inspection
David Helm, Owner/Inspector
http//www.helmhomeinspections.com
Reply With Quote
  #14  
Old 9/1/06, 5:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Septic tank inside home

Quote:
Originally Posted by dhelm
Yeah, but if you're into Bluegrass music, Galax is the center of the universe!
I Love bluegrass. I play bluegrass. I belong to Minnestoa Bluegrass and Oldtime Music Association.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #15  
Old 9/1/06, 9:22 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Septic tank inside home

Quote:
Originally Posted by dbush
Missouri you must have a minimum of 5' from the house to the tank. Question is, how are they going to remove it?
...and some folks think people in MO/KS are backwards.
At least we don't sh#t where we sleep.

Last edited by ckratzer; 9/4/06 at 7:24 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Coeur d'Alene, ID Home Inspectors rspriggs Miscellaneous Discussion for Inspectors 12 1/8/09 5:16 PM
Scumbag NAHI hits new low at ASTM meeting yesterd cmccann General Inspection Discussion 27 2/22/07 3:31 PM
Buckeye Home Inspections Service Area sboyd2 Miscellaneous Discussion for Inspectors 3 9/4/06 7:21 PM