Default Soldered pipe supports causing corrosion

The plumber decided it was a good idea to solder the pipes to the pipe supports. Each one had corrosion. I'm thinking that the solder increases the amount of galvanic corrosion between the dissimilar metals by providing a better electrical connection.

"Supply pipes in the main crawlspace had visible corrosion where they are soldered to supporting hardware. Corrosion appears to be the result of dissimilar metals electrically connected by solder resulting in galvanic corrosion. This condition may result in eventual leaking and these connections should be corrected or monitored for future leakage."

Last edited by kshepard; 10/2/08 at 1:40 AM..
Reply With Quote
  #2  
Old 12/1/06, 3:39 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Soldered pipe supports causing corrosion

You are not supposed to Solder copper to steel.

The problem is the steel pipe "hangers". It looks like bent pieces of allthread to me Kenton.

Copper pipes need copper hangers or hangers that are coated with plastic/rubber.

Reccomend hiring a real plumber to repair.
Reply With Quote
  #3  
Old 12/1/06, 3:57 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Soldered pipe supports causing corrosion

Quote:
Originally Posted by bkelly2
You are not supposed to Solder copper to steel.

The problem is the steel pipe "hangers". It looks like bent pieces of allthread to me Kenton.

Copper pipes need copper hangers or hangers that are coated with plastic/rubber.

Reccomend hiring a real plumber to repair.
They were actually the steel "U" hangers with the prongs you just hammer in. Very common here, but never soldered. Crazy plumbers!
Reply With Quote
  #4  
Old 12/1/06, 6:30 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Soldered pipe supports causing corrosion

Quote:
Originally Posted by kshepard
They were actually the steel "U" hangers with the prongs you just hammer in. Very common here, but never soldered. Crazy plumbers!
That is the problem. Need to keep the steel away from the copper. Even tape or insulation would work.
Reply With Quote
  #5  
Old 12/1/06, 6:34 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Soldered pipe supports causing corrosion

They're probably manufactured for use with black steel gas pipe.

The other fastener they use here are the pound-in hooks with vinyl protection, but they lock the pipe against the joist and I think a fair amount of home noise comes from long uninsulated hot pipe runs throgh a poorly insulated crawlspace. Thermal expansion causes creaking.
Reply With Quote
  #6  
Old 12/1/06, 6:46 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Soldered pipe supports causing corrosion

It looks like the make Copper hangers like that also.
Reply With Quote
  #7  
Old 12/2/06, 1:07 PM
twasion twasion is offline
Active Poster
 
Join Date: Jun 2006
Location: Whitefish, MT
Posts: 106
Please Note: twasion is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Soldered pipe supports causing corrosion

If dissimilar metals are used a barrier such as black tape should be used for the separation. It almost looks like a leak that repaired itself.
Reply With Quote
  #8  
Old 12/3/06, 2:30 PM
egarcia1's Avatar
egarcia1 egarcia1 is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Pueblo, CO
Posts: 52
Default Re: Soldered pipe supports causing corrosion

Mickey Mouse ears would be best for this installation.



Ernie Garcia
(719)821-6211
Builders Eye Home Inspections LLC.
builderseyehomeinspections.com
email me
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 6:39 PM
Water Pipe Corrosion inspector@carolina.rr.com Plumbing Inspections 6 6/12/06 5:37 PM
flex pipe supports. Jay Moge Inspecting HVAC Systems 6 1/23/06 11:34 PM


All times are GMT -4. The time now is 8:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts