Are TPR valves needed on tankless water heaters?



Habitation Investigation LLC
http://www.homeinspectionsinohio.com
Reply With Quote
  #2  
Old 8/4/06, 9:18 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tankless and TRP valve

good question-----I have found several without even though the installation instructions say they are required. Did you find one without?
Reply With Quote
  #3  
Old 8/4/06, 9:26 PM
James M. Troth's Avatar
James M. Troth James M. Troth is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Mechanicsburg, Oh
Posts: 286
Default Re: Tankless and TRP valve

I found one with it. It was located on the supply pipe. Pointed up and without the drain line.
Attached Thumbnails
tankless-and-trp-valve-p1010034.jpg  



Habitation Investigation LLC
http://www.homeinspectionsinohio.com
Reply With Quote
  #4  
Old 8/4/06, 10:24 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: Tankless and TRP valve

Jim

I have seen them with-and without.

Looking at various manufacturer spec's some are not required.
Reply With Quote
  #5  
Old 8/4/06, 10:38 PM
James M. Troth's Avatar
James M. Troth James M. Troth is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Mechanicsburg, Oh
Posts: 286
Default Re: Tankless and TRP valve

I can not think of a reason not to have one, it is one more safety item.

Weither it is required or not probably depends upon the manufacturer and if another safety device is installed.



Habitation Investigation LLC
http://www.homeinspectionsinohio.com
Reply With Quote
  #6  
Old 8/4/06, 10:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Tankless and TRP valve

In (2) states a relief valve is required....but for the most part unless you are in those states...it is not needed....but is a enhancement in safety.

Thanks JEFF....typo.....PR valve is what I was speaking of.........See Mr. Zinsco knows PR valves also...EXCELLENT...



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 8/5/06 at 1:04 AM..
Reply With Quote
  #7  
Old 8/4/06, 11:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Tankless and TRP valve

http://www.nachi.org/forum/showpost....9&postcount=13


Check out the above link, I install about 40 of them a year......most do not require a relief valve..but you can install them if you wish....but in (2) states the valve is required.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 8/5/06, 1:00 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Tankless and TRP valve

PR (pressure relief) valve? Yes (PR valves are required on most residential supply systems).

TPR (temperature & pressure relief) valve? No.

TPR's are required only in tanks (boilers and heaters).

What you have pictured is a PR valve.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 8/5/06, 11:56 AM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tankless and TRP valve

Here is info from the data plate on the side of a Rinnai heater
Attached Thumbnails
tankless-and-trp-valve-tpr-002.jpg  
Reply With Quote
  #10  
Old 8/5/06, 3:10 PM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 348
Default Re: Tankless and TRP valve

Poloma units made by Rheem have them in the carton when purchased.
Also in the installation instructions on the output side of heater.
Reply With Quote
  #11  
Old 8/6/06, 9:48 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,104
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tankless and TRP valve

Jeff is correct. All tankless manufacturers require the use of a pressure only relief valve system meeting all ANSI and or local codes. The systems are equiped with high limit switchs to handle the excessive heat issue. If you find a system installed without a proper pressure relief valve, I'd write it up as being an Unsafe Condition.

Refer to page #12 of the Takagi installation manual:

http://www.takagi.com/web2003/pdf/tk2.pdf
Reply With Quote
  #12  
Old 8/6/06, 9:58 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,104
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tankless and TRP valve

Additional IMC Requirements

SECTION 1006
SAFETY AND PRESSURE RELIEF
VALVES AND CONTROLS
1006.1 Safety valves for steam boilers.
All steam boilers
shall be protected with a safety valve.

1006.2 Safety relief valves for hot water boilers.
Hot water
boilers shall be protected with a safety relief valve.

1006.3 Pressure relief for pressure vessels.
All pressure vessels
shall be protected with a pressure relief valve or pressure-
limiting device as required by the manufacturer’s
installation instructions for the pressure vessel.

1006.4 Approval of safety and safety relief valves.
Safety
and safety relief valves shall be listed and labeled, and shall
have a minimum rated capacity for the equipment or appliances
served. Safety and safety relief valves shall be set at a maximum
of the nameplate pressure rating of the boiler or pressure
vessel.

1006.5 Installation.
Safety or relief valves shall be installed
directly into the safety or relief valve opening on the boiler or
pressure vessel. Valves shall not be located on either side of a
safety or relief valve connection. The relief valve shall discharge
by gravity.

1006.6 Safety and relief valve discharge.
Safety and relief
valve discharge pipes shall be of rigid pipe that is approved for
the temperature of the system. The discharge pipe shall be the
same diameter as the safety or relief valve outlet. Safety and
relief valves shall not discharge so as to be a hazard, a potential
cause of damage or otherwise a nuisance. High-pressure-steam
safety valves shall be vented to the outside of the structure.
Where a low-pressure safety valve or a relief valve discharges
to the drainage system, the installation shall conform to the

Reply With Quote
  #13  
Old 8/7/06, 4:43 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Tankless and TRP valve

Interesting........not a single one I have installed in VA have a "Pressure Valve" on them that WE would install.....to the BEST of my knowledge only (2) states have a Mandatory PRV requirement...but hey...I am a Electrician not a Plumber....

All of ours are inspected and again not a single one has an "External" PRV installed on them and the local AHJ never has a issue with it as we show him the SETS manual which says it is not required except in the listed states.

However...it is important to note that the SETS units we install have Thermal Relays on the front that POP out and have to be depressed in a situation of a thermal temp overload so to speak....but not a pressure valve...



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 8/8/06, 2:26 AM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,104
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tankless and TRP valve

Hey Paul,

I always operate under this general assumption. #1 basic rule of the various model codes are for all installations of code related materials and systems meet OEM installation and or operational specifications. Since I don't do code inspections, and the local building department won't defend me in a lawsuit, I rarely use them as a basis for safe and or unsafe conditions. All of the tankless water heater companies I've encounter mandate the installation and use of an exterior accessible pressure relief valve properly drained by gravity flow down and away from the subject valve.
Reply With Quote
  #15  
Old 8/8/06, 1:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Tankless and TRP valve

Quote:
Originally Posted by whandley
All of the tankless water heater companies I've encounter mandate the installation and use of an exterior accessible pressure relief valve properly drained by gravity flow down and away from the subject valve.
And most model plumbing codes require a PRV to be installed somewhere on the supply systems of residential dwellings where potable water is provided by a public utility.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:04 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts