Something to remember when you run into a home that has replaced their old gas water heater with a new tankless model. There could be an issue with the amount of gas delivered to the home.

Tank water heaters use an average of 36k btu on a standard 50 gallon model up to 88k btu on a standard 100 gallon model. They are supplied with a 1/2" gas line to the valve. Not a problem.

Now the owner comes in and replaces this with a tankless gas water heater. These units operate at 199k btu, quite a bit higher, and needs to be supplied by a 3/4" gas line.

There are numerous things you need to check when this change is done. Gas is delivered to a normal home through a meter that normally supplies 250 cfh, or 250k btu. The meter must deliver enough gas to supply all appliances operating at the same time. So let's take a look at an all gas house.

New tankless water heater = 199,000 btu
Standard Furnace = 48,000 btu and up
Oven / Stove = 48,000 btu
Fireplace = 39,000 btu

Total 334,000 btu.

By exchanging the old tank style water heater with the new tankless, you have exceeded the standard gas meter output and also the capacity of the initial 3/4" gas line into the home.

The only way to take care of this issue is to upgrade the gas meter to a higher capacity model that can also operate at a higher pressure. But that means a pressure reducer is needed at each appliance. These are not inexpensive upgrades from the gas company. They can be pretty spendy.

So if you see a tankless water heater, start by checking the capacity of the gas meter and how many appliances use gas. This could be an issue for your client.

There is also the issue of the b-vent, which could be undersized for the additional btu output, especially if it is combined with the furnace.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/24/10, 11:41 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Tankless water heater issue

Quote:
Originally Posted by sstanczyk View Post
Something to remember when you run into a home that has replaced their old gas water heater with a new tankless model. There could be an issue with the amount of gas delivered to the home.

Tank water heaters use an average of 36k btu on a standard 50 gallon model up to 88k btu on a standard 100 gallon model. They are supplied with a 1/2" gas line to the valve. Not a problem.

Now the owner comes in and replaces this with a tankless gas water heater. These units operate at 199k btu, quite a bit higher, and needs to be supplied by a 3/4" gas line.

There are numerous things you need to check when this change is done. Gas is delivered to a normal home through a meter that normally supplies 250 cfh, or 250k btu. The meter must deliver enough gas to supply all appliances operating at the same time. So let's take a look at an all gas house.

New tankless water heater = 199,000 btu
Standard Furnace = 48,000 btu and up
Oven / Stove = 48,000 btu
Fireplace = 39,000 btu

Total 334,000 btu.

By exchanging the old tank style water heater with the new tankless, you have exceeded the standard gas meter output and also the capacity of the initial 3/4" gas line into the home.

The only way to take care of this issue is to upgrade the gas meter to a higher capacity model that can also operate at a higher pressure. But that means a pressure reducer is needed at each appliance. These are not inexpensive upgrades from the gas company. They can be pretty spendy.

So if you see a tankless water heater, start by checking the capacity of the gas meter and how many appliances use gas. This could be an issue for your client.

There is also the issue of the b-vent, which could be undersized for the additional btu output, especially if it is combined with the furnace.
Good one Steve....!
Reply With Quote
  #3  
Old 11/24/10, 11:55 PM
Jarrod M. Northage's Avatar
Jarrod M. Northage Jarrod M. Northage is offline
InterNACHI Member
 
Join Date: Nov 2010
Location: Winnipeg, Manitoba, Canada
Posts: 44
Default Re: Tankless water heater issue

Thanks for the info!
Reply With Quote
  #4  
Old 11/25/10, 12:07 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Tankless water heater issue

Thanks Stephen, I'll definitely keep that in mind.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 11/25/10, 1:03 AM
Mary Ann Chiquete Mary Ann Chiquete is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Buckeye, Arizona
Posts: 101
Default Re: Tankless water heater issue

Thanks for the education! I think we will see more tankless in the future and this info will come in handy.



Mary Ann Chiquete
Benchmark Home Inspection
Serving the greater Phoenix Metro area
623-399-7962
Reply With Quote
  #6  
Old 11/25/10, 1:16 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Tankless water heater issue

Good info.

Most tankless type water heaters will require a stainless steel vent kit designed specifically for that unit. I don't know of any (although there may be some) that are compatible with galvanized "B" vents. Most of the current crop of higher efficiency units produce condensate in the vent which is corrosive and must be drained off similar to a HE furnace.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #7  
Old 11/25/10, 3:11 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tankless water heater issue

The switch over to instantaneous may not save that much energy and can be bit of a nuisance each time you draw water (it takes longer to heat up from cold). There are actually some storage type hot water heaters that are more efficient than instantaneous!!

http://www.americanwaterheaternews.c...ts/polaris.htm


Here's a website with independently tested efficiencies. For example, Bosch has a range of Energy Factors (EF.......equates to efficiency) of from .69 to .93 with only one being over .90 and most being in the low .8's!!

ps: It was a bit late (4:11 AM) when I posted....here's the address for the energy efficiency directory for appliances:
http://www.ahridirectory.org/ahridir...ages/home.aspx

Last edited by Brian A. MacNeish; 11/25/10 at 8:50 PM..
Reply With Quote
  #8  
Old 11/25/10, 3:36 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Tankless water heater issue

Good info Brian. There is also another issue with tankless units. There is a minimum flow required before the unit turns on. If you are washing your hands using a newer low flow faucet, there may not be enough flow to start the heater. Same thing can happen with the new ultra low flow showerheads. They do not draw enough water to activate the system.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #9  
Old 11/25/10, 3:04 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Tankless water heater issue

Thanks!!! Good information.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #10  
Old 11/28/10, 5:24 PM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Tankless water heater issue

very nice




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #11  
Old 11/29/10, 4:01 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Tankless water heater issue

http://www.tanklesswaterheaterguide.com/


Here is one I put on my web site for tank-less systems. It has charts and math problems to consider when switching systems. Basically, if you have three or more bathrooms in the home, you may need two tank-less systems. This requires perhaps two gas meters and lines. Pricing would then be out of sight.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #12  
Old 12/1/10, 6:01 PM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: Tankless water heater issue

Now THATS a good thread, Thanks for all of that info.....



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #13  
Old 12/1/10, 8:12 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tankless water heater issue

Quote:
Originally Posted by gfarnsworth View Post
http://www.tanklesswaterheaterguide.com/


Here is one I put on my web site for tank-less systems. It has charts and math problems to consider when switching systems. Basically, if you have three or more bathrooms in the home, you may need two tank-less systems. This requires perhaps two gas meters and lines. Pricing would then be out of sight.

Most if not all that info is for electric tankless. Gas units are more efficient and produce higher temps and higher GPM flow rates. Noritz has a 98% efficient unit but the cost is through the roof.

Chuck
Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/2/10, 8:51 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Tankless water heater issue

I would want to compare a tankless to one of these. Put it in your garage and heat your garage at the same time!



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 12/2/10, 10:06 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Tankless water heater issue

Quote:
Originally Posted by jfunderburk View Post
I would want to compare a tankless to one of these. Put it in your garage and heat your garage at the same time!

It takes heat from the garage and transfers it to the water.
Garage will be cooler.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sulphur smell bsmith Plumbing Inspections 2 6/6/08 8:32 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 1:57 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts