Local AHJ wants 8'+ copper or other material at hot water discharge side of tankless water heater; no CPVC. Anyone know a reason for this? Seems to me there would be no more "shock" fro 120 degree water from a tankless than a regular tank heater....
Thanks. |
|
#2
|
|||
|
|||
|
Quote:
|
|
#3
|
||||
|
||||
|
Its a safety backup in the event of multiple failures in the tankless unit. Flow sensing and overtemp sensing would both have to fail to melt a plastic pipe but it "could occur".
Same idea for the one inch gap for B-vent's, paper will not ignite when left touching a b-vent even for years. Its a safety requirement for unusual events somewhat like thermal runaway. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#4
|
|||
|
|||
|
Please Note:
George Szontagh is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank you Mr. King. That makes sense. I must say the controls I've seen on tankless units look like they were made by NASA engineers though, and I haven't heard of runaway failures. Interestingly Noritz doesn't want a T&P valve on the discharge, only a pressure safety valve.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| CPVC Water Filtration System | dhubler | Electrical | 5 | 11/15/08 5:34 PM |
| CPVC wall connection | rbrady | Plumbing | 5 | 5/1/08 12:30 PM |
| Tankless & BRAINLESS | sfigert | General Inspection Discussion | 9 | 8/2/07 11:56 AM |
| Cpvc & Pvc | waksell | Plumbing | 28 | 5/8/07 3:49 PM |