Default Tprv

Am I missing something with the TPRV venting? Isn't it supposed to to visible to the end, terminating within 6 inches from the floor/drain pan? I've seen in my area the pipe sent through the wall to outside. Maybe I'm missing something--please advise.

Greg
Reply With Quote
  #2  
Old 6/14/08, 12:28 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: Tprv

  1. Be first piped to an indirect waste receptor through an air gap located in a heated area when discharging to the outdoors in areas subject to freezing, since freezing water could block the pipe.
Water Heater Discharge Piping mini-course for inspectors.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 6/14/08, 12:38 AM
Gregory C. Scheer, Jr. Gregory C. Scheer, Jr. is offline
InterNACHI Member
 
Join Date: May 2008
Location: Plumas Lake, CA
Posts: 30
Default Re: Tprv

Exactly, but what I've seen goes against the courses. Hmmmm... New construction too! Crazy!
Reply With Quote
  #4  
Old 6/14/08, 12:43 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: Tprv

Quote:
Originally Posted by gscheer
Exactly, but what I've seen goes against the courses. Hmmmm... New construction too! Crazy!
How high are they set off of the ground? Inside are out, they still fall under the same requirements.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 6/14/08, 12:55 AM
Gregory C. Scheer, Jr. Gregory C. Scheer, Jr. is offline
InterNACHI Member
 
Join Date: May 2008
Location: Plumas Lake, CA
Posts: 30
Default Re: Tprv

Thanks. As suspected; I just don't understand how they're passing code inspections.
Reply With Quote
  #6  
Old 6/14/08, 1:06 AM
mivie's Avatar
mivie mivie is offline
Active Poster
 
Join Date: May 2008
Location: Cornelia, Ga
Posts: 438
Please Note: mivie is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tprv

I see the same thing here in Georgia. Piped right through the wall at a straight angle. Most always in the basement. I call it and take the flack. I also don't know how it passes inspection.
Had one this week but it was also reduced to 1/2 inch and no expansion tank installed.
The expansion tank was still in the box in the corner.
Attached Images
File Type: bmp water heater.bmp (225.1 KB, 46 views)

Last edited by mivie; 6/14/08 at 5:39 PM..
Reply With Quote
  #7  
Old 6/14/08, 4:29 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tprv

Quote:
Originally Posted by ccurrins
  1. Be first piped to an indirect waste receptor through an air gap located in a heated area when discharging to the outdoors in areas subject to freezing, since freezing water could block the pipe.
Water Heater Discharge Piping mini-course for inspectors.
Christopher, is that a Chicago area rule?
I don't see freezing as even a remote possibility in California, even in the Sierras (or in Chicago, either for that matter) as the only water coming down the pipe is a boiling hot splatter, once in a blue moon.
If it's new construction, I would make inquiries about locally accepted practice. Should be recycling that heat.

John Kogel
www.allsafehome.ca
Reply With Quote
  #8  
Old 6/14/08, 5:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Tprv

Based on your very vague description, it doesn't sound improper to me.

First of all, you're in CA. IRC rules don't apply. The termination is required to be between 6" and 24" off the floor - not "within 6".

Secondly, unless your in an are that is subject to freezing temperatures, a "through-wall" termination is perfectly acceptable, so long as the termination (not the entire pipe) is visible.

Rarely will you see a discharge in CA that includes an air-gap or indirect waste connection/receptor.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 6/14/08, 9:36 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: Tprv

Quote:
Originally Posted by jkogel
Christopher, is that a Chicago area rule?
I don't see freezing as even a remote possibility in California, even in the Sierras (or in Chicago, either for that matter) as the only water coming down the pipe is a boiling hot splatter, once in a blue moon.
If it's new construction, I would make inquiries about locally accepted practice. Should be recycling that heat.

John Kogel
www.allsafehome.ca
The "rule" came from...Water Heater Discharge Piping mini-course for inspectors. There are other parts of Illinois besides Chicago.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #10  
Old 6/14/08, 11:20 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tprv

Quote:
Originally Posted by ccurrins
The "rule" came from...Water Heater Discharge Piping mini-course for inspectors. There are other parts of Illinois besides Chicago.
Sorry CC, I see you are closer to St. Louis Mo than Chicago.
Reply With Quote
  #11  
Old 6/15/08, 1:47 PM
Gregory C. Scheer, Jr. Gregory C. Scheer, Jr. is offline
InterNACHI Member
 
Join Date: May 2008
Location: Plumas Lake, CA
Posts: 30
Default Re: Tprv

temperature-pressure-relief-valve-dsc05758.jpg

Here's what the hot water heater looks like. Where do I look to see if this is acceptable? I've already performed a search for CA plumbing code and I don't find it. Thanks for the help.

Greg
Reply With Quote
  #12  
Old 6/15/08, 3:11 PM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tprv

It is very common here for the pipe to be routed through the wall. The pipe is usually ~ 8"-10" above grade and has a 90 degree fitting to direct the discharge towards the ground. I have seen plenty without the 90 degree fitting, which I would report on.
Reply With Quote
  #13  
Old 6/15/08, 3:36 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tprv

Here's mine from yesterday. Not a good picture but the copper line went up and ended about 6-8 inches from the bottom side of the subfloor. Around here about 75% discharge to an exterior point, and almost always uphill.

temperature-pressure-relief-valve-img_7439.jpg
Reply With Quote
  #14  
Old 6/17/08, 8:59 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Tprv

Around here there are a lot of heaters installed in interior closets, under stairs, etc. that discharge into the crawl space below. In some cases the space is so tight that the pipe cannot even be seen.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #15  
Old 6/18/08, 1:46 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,224
Default Re: Tprv

check out http://www.nachi.tv/ppv/8



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plastic TPRV line? rmaday Plumbing Inspections 14 6/5/08 6:50 AM
TPRV questions Rick Maday Plumbing Inspections 1 8/23/07 12:51 AM
TPRV drain piping tsmith5 Plumbing Inspections 4 1/11/07 10:25 PM
TPRV drain cbuell Plumbing Inspections 1 1/5/07 8:22 PM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 8:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts