  #1  
Old 8/26/08, 3:00 PM
John Achin John Achin is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Goshen, VA
Posts: 11
Default TPRV extention materials

Will someone please list all the acceptable materials for use for TPRV
extentions.
thankyou.
Reply With Quote
  #2  
Old 8/26/08, 3:58 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,825
Send a message via AIM to sstanczyk
Default Re: TPRV extention materials

Galvanized steel, hard-drawn copper, CPVC




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #3  
Old 8/26/08, 5:05 PM
John Achin John Achin is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Goshen, VA
Posts: 11
Default Re: TPRV extention materials

Thanks Stephen,
My code check book says that you can use the same materials allowed for water distribution, but it doesn't list pex (it lists the same materials that you listed). I have seen pex used frequently and write it up as wrong, but it is accepted for water supply. Do you write up pex when used for TPRV extension?
Reply With Quote
  #4  
Old 8/26/08, 5:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: TPRV extention materials

Pex is fine for the TPR discharge.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 8/26/08, 5:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: TPRV extention materials

It depends on your AHJ, but Mr. Larson is correct - PEX is generally accepted for this use. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 8/26/08, 6:04 PM
John Achin John Achin is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Goshen, VA
Posts: 11
Default Re: TPRV extention materials

thanks guys
Reply With Quote
  #7  
Old 8/26/08, 9:35 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,825
Send a message via AIM to sstanczyk
Default Re: TPRV extention materials

The problems with PEX are minor.

It needs to be secured more than the other materials since it is more flexible.

It is also affected by sunlight so if the water heater is in say a utility room with a window, the PEX should be covered. If the TPRV is routed to the exterior as it should, the termination point in sunlight should be protected or a different material.

For the supply lines, there must be 18" of metallic or approved piping between the water heater and any PEX. It makes sense that it would be for the TPRV also. Just a thought.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #8  
Old 8/26/08, 10:56 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: TPRV extention materials

Quote:
Originally Posted by sstanczyk

For the supply lines, there must be 18" of metallic or approved piping between the water heater and any PEX. It makes sense that it would be for the TPRV also. Just a thought.
Hi Stephen,

Could you provide the source for this requirement, please?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #9  
Old 8/26/08, 11:45 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,825
Send a message via AIM to sstanczyk
Default Re: TPRV extention materials

Uniform Plumbing Code (2003). I know some don't go by the UPC but some of the manufacturers quote this in their installation guidelines. There are parts made specifically for water heater and PEX connections..




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #10  
Old 8/27/08, 12:19 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: TPRV extention materials

Stephen is correct. . .

604.11.2 Water Heater Connections.
PEX tubing shall not be installed within the first eighteen (18 inches (457mm) of piping connected to a water heater.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 8/27/08, 1:36 PM
John Achin John Achin is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Goshen, VA
Posts: 11
Default Re: TPRV extention materials

The TPRV extension should terminate 2 -6 inches from the ground. It must be visible and not be routed to a crawlspace or exterior.
Reply With Quote
  #12  
Old 8/27/08, 1:53 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,825
Send a message via AIM to sstanczyk
Default Re: TPRV extention materials

Quote:
Originally Posted by jachin
The TPRV extension should terminate 2 -6 inches from the ground. It must be visible and not be routed to a crawlspace or exterior.
Sorry to disagree, you are only partially correct. It should not terminate in the crawl space. But the best application is to route to the exterior, to within 6" of the ground.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #13  
Old 8/27/08, 3:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: TPRV extention materials

Actually you are both correct, depending on which code your area follows. The Uniform Code says the termination should be between 6" and 24" from grade or finished floor, and the International Code says not more than 6" from grade or ff.

Also, with manufactured homes, Federal guidelines allow a termination into the crawl space.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 8/27/08 at 3:49 PM..
Reply With Quote
  #14  
Old 8/27/08, 4:59 PM
John Achin John Achin is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Goshen, VA
Posts: 11
Default Re: TPRV extention materials

"2. Discharge through an air gap located in the same
room as the water heater.

7. Discharge to a termination point that is readily
observable by the building occupants."
Reply With Quote
  #15  
Old 8/28/08, 9:06 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: TPRV extention materials

Quote:
Originally Posted by sstanczyk
Uniform Plumbing Code (2003). I know some don't go by the UPC but some of the manufacturers quote this in their installation guidelines. There are parts made specifically for water heater and PEX connections..


Quote:
Originally Posted by jpope
Stephen is correct. . .

604.11.2 Water Heater Connections.

PEX tubing shall not be installed within the first eighteen (18 inches (457mm) of piping connected to a water heater.




Ahh, the UPC...thanks, gentlemen.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Options in selecting materials for basement construction wdevries Canadian Inspectors 2 8/4/08 2:30 PM
IAQ: moderating humidity in homes using absorbent wall materials kshepard Green Building Inspections 0 1/17/08 1:27 PM
IAQ: moderating humidity in homes using absorbent wall materials kshepard Green Building Inspections 0 1/17/08 1:27 PM
IAQ: moderating humidity in homes using absorbent wall materials kshepard Green Building Inspections 0 1/17/08 1:27 PM
TPRV line and condensate line marriage ccarrington Plumbing 3 4/29/06 8:59 AM


All times are GMT -4. The time now is 4:05 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts